deleted , check post 7 and 8
A head scratcher for sure - gotta be something obvious we're missing here... I don't have an E682 at all nor my E681 handy but it doesn't seem right that you get voltage on the left side of the board when you don't have power connected to that side. If you haven't already, you may want to reach out to Jim (jstjohnz) directly and perhaps he can figure this out for you. Still looking at your pix for that light bulb to go off...
edit - - I just realized - - - you are moving your ground lead around with your meter - - the ground is common to both sides always. You are keeping the postive/red lead on the +12v and moving your negative/black lead on right and left sides and measuring 12v which is completely OK. For sure you MUST have a short between + and - voltages on the left side. I'm going to guess that you may have put in too much solder under the terminal block and it shorted across underneath (between the PCB top and the TB itself - or the lead is bent up).
Try this - disconnect the power supply completely and measure the resistance across the +/- leads on the J18 (left) TB - I'm betting you read 0 ohms.
Look very closely at the left-most lead of the pixel connectors when looking at the bottom side of the board - reflow these to ensure they are not touching the surrounding pad as that is ground.
\
also between the tops of the fuse holders to ground. I'd suggest you pull all of the fuses on the left and see if the short goes away if reflowing doesn't change things.
Look at your power supply also, when you connect both sides up and plug in I do not see a power led on the supply like I did when you have only one side connected,
Make sure your connecting to your power supply correctly too
Have you cleaned the bottom of the board?
In your pictures it looks like solder splatter all over. It is difficult to see a good solder joint with excess rosin/flux covering the connection point.
Bob,
Did you try to call or contact Jim St. John? He is very responsive to questions for help.
So I just built 6 of these myself last week. My boards are a different rev )1.3) than yours. (i only have 1 button).
It appears the boards is running a test pattern as the green LED is on. RED LED is on so that means normal operation. Two of the 3 yellow LED are on which means you have the 3.3vdc for logic and pixel power at J19 for 3-4. I would venture to say that if you plug it into a network switch you could pull up the config page. but lets figure out what is going on before you do that, don't want to fry your network.
Your issue to me is the 1-2 side of the board. Power supplies will appear to die as yours does when the device it is powering draws too much current. Try the steps below.
Check for grounds on the board.
1. Disconnect the power supply completely.
2. Using your multimeter on ohms, measure the resistance between the + and - on J18. You should read in the mega ohms range (meaning they are not connected) if you read less than 1 ohm then your + terminal is grounded to your - terminal or somewhere on the board there is a solder bridge between the ground plane and the + some where. Can you post a clearer high res picture of the back of the board?
Only do this after you verified there is no ground between the + and -
Only connect power to J18. Only the Px12 LED will come on. Here is a pic of my board when I did this.
If the above didn't work then try this.
Although this is a long shot, maybe the issue is with the second set of terminals on your power supply. Check for ground between each of the + terminals on the power supply to the - terminals. It is possible something is wrong there. Also, did you try another power supply? The board should only be drawing 250ma to power the board so unless the power supply is defective it shouldn't blink at the power draw of the board alone.
As someone else mentioned, you need to get a 3 wire cord to the power supply to proper ground it. Especially since you are having power issues. I used an old power cord from a PC and cut the end off.
Let me know what you find.
Jay
It's not the power supply since he daisy chained the +DC connection from J19 to J18. For sure he has a dead short on the left side.
This needs to be broken down into manageable bites for troubleshooting.
It appears the on board 3.3 volts is working when half the board is powered. When the other half the board is powered, does the power die? Verify with a meter power stays good. If it dies as in the power supply is shutting down on a short, the short in the 2nd side of the board needs to be found and corrected. The short could be a solder bridge somewhere or a cap could be in backwards, though this usually lets out the magic smoke instead.
If jumping the power does not shut down the power, the power to the pixels output jacks needs verified. If you had a short in a pixel string, you could have lost fuses to some outputs. Verify with a meter that power is good on all outputs.
After power is verified all OK, then and only then should you start to look for driver data issues on the 2nd side of the board.
The board works fine when powering from the main input at J19 and the logic all comes up fine so that means the issue is only wrt to the left side of the board. It's obvious at this point that there is a dead short between + and - on the left side. He actually already proved that because he measured 12v on the *fuses* on the left side when he had the + lead still on the +DC point on J19. This means that the fuses themselves were at ground potential or you wouldn't have measured any voltage. The fuses should NEVER be at ground potential - since they are - it's a short plain and simple.
The power supply shut off because it's being shorted out and it has short-circuit protection. As I've said before, try reflowing the +DC points on the board and nothing there, remove all left side fuses and see if the short goes away. It's only a two-sided board so it must be a solder short somewhere...
2 things I see. The 2 large diodes at the bottom of the boards look like the solder does not go completely through the board. May or may not be the culprit. I would also go back through and hit all solder joints and re-flow the solder.
The power wires you are using looks like some wire I used as SPT-2 and Incans my first year. I had to trash 250 feet of it because it wouldn't carry the proper current. If yours is the same I had, try a different power cord. One other thing, is your power cord a grounded wire and plug. It may not be the problem, but I would think you would want a 3 wire plug for power to the PS
Just a couple of stabs in the dark. Since all of your meter readings look right, it leads me to a cold solder joint. I've soldered about a dozen of these along with a half dozen 6804s. After assembly, before putting power to them, I always hit the solder joints 1 more time, just to satisfy my own mind.