I just had a 25A "hockey puck" SSR fail in the middle of my show. Luckily I had a spare. I was surprised at this failure though.
It is a 25A 120/240v rated unit. I have max (all white, full brightness) of 20A through it (typically much, much less). I do not have a heat sink in use.
Are these failures common (or not usual)? I wonder if I should go to a 50A rated unit (without heat sink) or add a heat sink to a 25A version. This was not an easy fix (due to enclosure & location) and I would like to prefer a repeat.
heat kills electronics. a little heat kills slowly but still kills. heatsink is a good thing for those units.
This is now clearly not a freak occurrence but rather a design flaw. My spare SSR died yesterday during testing after pixel replacement. I now suspect the culprit is power supply inrush current. I have used these SSRs rated at 25A for a previous design which used 4 Meanwell supplies (inrush spec: 20A each). This year I have a totally different design which uses 8 Meanwell supplies (inrush spec: 60A) - and thus much higher turn-on current. I will try using a different SSR rated at 50A continuous, but even that is well below the 480A max inrush per the specs. BTW, I will be sure to use a zero-cross SSR to reduce the initial current.
Has anyone else used hockey puck SSRs to turn on banks of switching supplies, and if so, what configuration (supplies and SSR rating)?
What brand is the SSR? Many units with false specs out there.
Hi, the link below is a teardown of a 25A SSR, 4:40 looks at the triac.