Next year i am looking to do away with running multiple extension cords to various control boxes with power supplies in them. I am looking at dropping 9 PSU's into one box, then run individual cables to each controller. Was looking at using Powercon connectors to run the cables. i know someone has done this, so looking for ideas as well as how should i run the PSU's, should i tie them all together into a a DC breaker bar, or should each PSU, or 2, feed into a single Powercon out plug?


13 Replies
StickyWicket
Posts: 548
(@stickywicket)
Honorable Member
Joined: 14 years ago

When using multiple PSU’s you can’t connect the DC positives together. The only exception to this is load sharing ones which you most likely don’t have. If you did connect them together they fight over voltage regulation.

Keep in mind high voltage AC goes much farther than low voltage DC. With DC your voltage will drop quickly.

Heat is also something to consider.

If you are pulling large amps off your power supplies you need to spread that draw out on all the connection points to each power supply. There is a reason why there is three connection points for each positive and negative.

I would only consider this many PSU’s if they were in one element (maybe two if close together). Other than that I’d keep them closer to each element they run and run extension cords to each.


Reply
Posts: 485
(@jerry-rigs)
Honorable Member
Joined: 11 years ago

Caveat: I am just a hobbyist. I quickly defer to others with more knowledge/experience in this area and there are a lot of them on this forum.

So instead of running multiple AC extension cords to various control boxes with PSU's, you are going to run multiple DC extension cords to various control boxes?

I may not understand what you mean by breaker bar. Do you mean to tie all 9 switching PSU "+" terminals together to a single bus and then tie all 9 switching PSU "-" terminals together to a single bus intending to produce maybe 200+ amps of DC power on a single set of rails? Unless you are knowledgeable electrician (above hobbyist level), I am pretty certain that it is a bad idea on several levels. This would be kinda like power injection in reverse. You would need to isolate each switching PSU because the load will concentrate on one switching PSU and overload/blow it then the load will fail over to the next switching PSU giving a rapid cascade of blown switching PSU's. I think there are load balancers for switching PSU's to share a common output bus but I think they are very expensive. You could also isolate PSU's by not sharing outputs and using 1+ output connectors per switching PSU.


Reply
Posts: 409
Topic starter
(@dim-bulb)
Reputable Member
Joined: 9 years ago
StickyWicket wrote:When using multiple PSU’s you can’t connect the DC positives together. The only exception to this is load sharing ones which you most likely don’t have. If you did connect them together they fight over voltage regulation.

Keep in mind high voltage AC goes much farther than low voltage DC. With DC your voltage will drop quickly.

Heat is also something to consider.

If you are pulling large amps off your power supplies you need to spread that draw out on all the connection points to each power supply. There is a reason why there is three connection points for each positive and negative.

I would only consider this many PSU’s if they were in one element (maybe two if close together). Other than that I’d keep them closer to each element they run and run extension cords to each.

longest run i will have is maybe 25 feet, i am just tired of extension cords, this way i can run custom length cables.


Reply
Posts: 241
(@mrdudeman)
Reputable Member
Joined: 12 years ago

why not make your own custom AC cords to the controllers...
get a spool of it and a bunch of plug ends?


Reply
Posts: 486
(@uncledan)
Honorable Member
Joined: 11 years ago

Most of my display is setup this way. I try to minimize AC in the yard as much as I can. I would advise this way isnt the easiest or cleanest way to set things up. Voltage drop is a pain.... and I have some very large 4 core wire I use from the main box to the props and controllers.


Reply
Posts: 2507
(@mrgrumpy)
Famed Member
Joined: 12 years ago
MrDudeMan wrote:why not make your own custom AC cords to the controllers...
get a spool of it and a bunch of plug ends?

This is what I do. I buy 250 Reels of both 18/2 & 18/3 SJOOW and waterproof power supplies
My power cords run from the transformer to the AC power box with 6-15A GFI receptacles. 12 outlets total.. All are full, and no GF here.

Here are the plugs I use - great price for the quality.
15A 3 Wire: https://www.emisupply.com/catalog/advanced_search_result.php?keywords=lec-515pr&search=&search_in_description=1
15A 2 Wire not indexed: https://www.emisupply.com/catalog/advanced_search_result.php?keywords=lec-115pr&search=&search_in_description=1


Reply
jchuchla
Posts: 8691
(@jchuchla)
Illustrious Member
Joined: 15 years ago

PowerCons are for AC mains, not DC. Never use standard connectors for other than their intended purpose.

There's a reason AC is used for power distribution rather than DC. That battle was fought over 100 years ago and had a clear winner. There's no good reason to reinvent the wheel. There's more good reasons not to distribute low voltage high current DC than there are benefits.

If you don't like the cords you've got, make new ones. Just like you would have in your DC idea.


Reply
rayhjr
Posts: 974
(@rayhjr)
Noble Member
Joined: 12 years ago

I would dig some trenches and burry some pvc in the ground and put AC receptacles in my yard before I would run 30, 60 or more amp DC across my yard.
Or, run the DC in the pvc, but not across my yard. But That's just me.


Reply
Posts: 409
Topic starter
(@dim-bulb)
Reputable Member
Joined: 9 years ago
uncledan wrote:Most of my display is setup this way. I try to minimize AC in the yard as much as I can. I would advise this way isnt the easiest or cleanest way to set things up. Voltage drop is a pain.... and I have some very large 4 core wire I use from the main box to the props and controllers.

That is one hell of a subpanel, way more then i would ever use but nice. I take it that is mounted in your garage?


Reply