I have 12v pixels x400 of them (50/string 8 strings). They have 22awg wire on them. I am not powering by the controller at all. I have a Meanwell 12v 350 watts power supply. I am going to inject every string straight to the power supply. I am very confused on the wire size I am using. I see a lot of people using 18 AWG, some using 14. Can I use a two (4 string each) daisy chained 18awg wire to inject power or should I have a wire for each string? I have looked at all the charts but a lot of the charts say they are extremely conservative values for amp transmission. I am doing two lines because of voltage drop at 5 feet, 8A on 18 AWG is < 5% drop. This is the last thing I have to figure out is what size wire am i using for power injection.


3 Replies
Posts: 186
(@steve123)
Estimable Member
Joined: 7 years ago

Refer to this wiki page regarding the capacity of wire: https://en.wikipedia.org/wiki/American_wire_gauge

A 22 AWG has a safe capacity of 3A. 50 pixels * 60mA = 3A. So, if you wonder why the wire gauge is 22 AWG, this is why. It is precisely the size required for a 50 pixel string. So, this implies that every string would need power injection since connecting them end to end would increase the current in the upstream strings by 3A for each additional string. So, two strings (100 pixels) means the current in the first string is 6A. 150 pixels = 9A. An so on.

An efficient injection strategy is to inject every 100 pixels. Thus, you inject at pixel 0 (from the controller), 100 (injection), 200 (injection), 300 (injection), etc. The controller supplies power to the first 50 pixels. The current injected at pixel 100 supplies power to the 50 upstream and 50 downstream pixels at that point. This keeps the max current in each string at 3A and within the limits of the 22 AWG wire. The gauge of the injection wire should be adequate to handle 100 pixels, or 6A. This would require nominally about an 18 AWG wire (slightly smaller than 18 AWG, slightly larger than 20 AWG). This is why pigtails are typically advertised as 18 AWG (they are actually closer to 19 or 20 AWG, their cross sectional area is quoted as 0.75mm2 which corresponds to about 19 AWG).

If you use multiple power supplies then you start to have issues with cross connecting them. So, generally try to keep your models grouped to one power supply. You can add additional power supplies per controller but then you need to separate strings so that the power supplies are not in contention with each other.

Another factor you need to consider is the length of the wire. If you have a large distance you many need to increase the wire size to reduce the voltage drop. For 12V strings though, this is generally not a problem so I think you can use the 18 AWG extensions and pigtails for all your power injection needs.

FYI, I have not uncovered a single supplier yet that supplies 18 AWG wire with their strings. Some claim 18 AWG in their advertising but the actual wire gauge is 22 or 24 AWG. So, assume it is all 22 AWG or worse.


Reply
Posts: 98
(@nayrma)
Estimable Member
Joined: 9 years ago

Gauge usually comes into play based on length of wire and how much power is lost going down the wire. Lower the gauge, the further you can go with little loss. I standardized on 16 GA landscaping wire and keep my power supplies close the the pixels. That gauge wire is reasonably priced at the big box stores

http://spikerlights.com/calcpower.aspx

Good site to understand power impact based on different factors like wire gauge, distance, etc.

Sent from my SM-N960U using Tapatalk


Reply
Posts: 186
(@steve123)
Estimable Member
Joined: 7 years ago

For clarity, if you inject every 100 pixels, 18 AWG extensions and pigtails for each injection point running back to the power distribution board or controller. If you want to create a "power bus" and use a single wire to supply injection at multiple points, you would need to increase the wire size. I started out doing the latter using 14 AWG wire for power injection. I quickly realized this is not the best solution since it required me to make my own custom power extensions. I ended up using standard 18 AWG extensions for my power injection since those are easy to buy and less work. So, I recommend you use a separate wire for each injection point and use the power distribution boards as the power distribution point. PixelController.com sells them as "power distro boards".