Weird question but I was wondering if this would work.

when i mount pixels on roof line inside a jchannel, id like to have the inject wire follow inside the channel and inject every 50 pixels ( where the supplier has extra red/white for injection. )

if i do this and tap in every 50 would that lower the injection at the end of say 800 pixels or would it not make a difference ?


3 Replies
Posts: 740
(@ezellner)
Prominent Member
Joined: 11 years ago

The voltage will be reduced by the resistance in the wire. However, if you figure out the current required and size the wires (power and ground) properly, you can run a single feed. For 800 pixels, that's about 48 amps full white. You need a BIG wire. Or you could run 3 sets of 12 gauge.


Reply
jhoybs
Posts: 59
(@jhoybs)
Trusted Member
Joined: 11 years ago

I use this calculator to get my voltage drops: http://www.calculator.net/voltage-drop-calculator.html
As Ed states, you need to run these "bus" wires for both ground and +V.


Reply
MartinMueller2003
Posts: 7604
(@martinmueller2003)
Illustrious Member
Joined: 14 years ago

I ran 8 sets of 16 Gauge.