Posts: 8517
(@angus40)
Illustrious Member
Joined: 15 years ago
11Bravo wrote:Please check my configuration:

The E682 will run the MT which has 16 strings of Ws2811 bullets 50 count per string,
Strings are in series, odd and even are connected for a 100 count string with pwr injection at the end of each odd string.
and setup to zigzag every 50.
The rest of the controller outputs will run pixels on the eves.

The E6804 will hopefully run pixels on the window frames.

on the e682 config you show 400 pixels on each port
Max is 170 per port
You are also in multicast mode rather than unicast .
Also check you universe # designations , you currently show 2 universe 10 and 11 .


Reply
Posts: 1168
(@keith-r)
Noble Member
Joined: 19 years ago

Ken,
Also when in Unicast, make sure that your controllers has a different IP address, and make sure that your output (FPP, Vixen, xLights) is pointed to each of those controllers.


Reply
pmiller
Posts: 2795
(@pmiller)
Famed Member
Joined: 12 years ago

Your start universes are wrong. If one of your outputs start on universe 1 and end on universe 5 then the next output needs to start on universe 5. On your 682, I see the first 4 outputs starting universe 1 and ending universe 10. You have the second set of outputs starting on universe 2 when it should start on universe 11.
On the 6804 output 1 ends on universe 4. Output 3 should start on universe 4.

Sent from my SM-T710 using Tapatalk


Reply
pmiller
Posts: 2795
(@pmiller)
Famed Member
Joined: 12 years ago

I just noticed. Your output 1-1 to 1-4 on the 682 is using 10 universes. That's crazy. You have 400 entered for the number of pixels. With that number you exceeded the output if the controller if you're using multicast. Its been a while since I've used the old firmware but I'm thinking that 400 should be 100. That number designates the number of pixels per your longest string, not the total number of pixels. So let's say you have 4 strings of 100 pixels then you enter 100. But there's a catch. If you have 2 strings of 100 and 4 strings of 50 you still enter 100. That's with the current firmware your 682 is using. If you upgrade the firmware to 5.030 you can control each output separately.

Sent from my SM-T710 using Tapatalk


Reply
Posts: 1592
(@ruppro)
Noble Member
Joined: 11 years ago

For your megatree, output 1 1-4, each string is 100 pixels (not the total 400) and you have Universe 1 Start 1, then just to the right it gives you the ending universe and channel #. Then for Output 2 you again set the Pixels to 100, and enter the ending universe # from the 1st output and the ending channel #+1 as you start channel and so on down the list


Reply
Page 2 / 5
Share: