Crazydave wrote:5v at 15 meters!? 5v cannot travel very far.Check your voltage levels at the beginning and end of strip..... They are probably low.
I hope you also have a ground wire attached to each strip.
Also 10 meters is way too far without null pixels or changing the network resistors on the e682
Sounds like you may have two problems.
1) check voltage at beginning of strip..... Hope you have 5 volts at the beginning. under 3.5 is bad
2) replace network resistors with 56 ohm
It depends which aspect you're looking at. For the data signal, 5V can travel perfectly far, it all depends on the conditions under which it travels. The input current for the WS2811 chip is 1uA. At that current, there's only 0.0000025V drop over 15m of 24AWG wire. The pixel power lines are a totally different story. At the same distance over 18AWG wire, if the system draws 30A (50 full on RGB LEDs), you'll have 1.89V of drop.
If you're seeing substantial voltage drop on the power, that can be an issue. My impression is that's not the case, but if it is, injecting additional power at convenient points down the line will likely help. There's some good info on this in the wiki: http://www.doityourselfchristmas.com/wiki/index.php?title=Power_Injection
Since the use of shielded ethernet cable is stated, the right resistor value is 100 ohms. 56 will underterminate and potentially contribute to any noise issues. Is the cable shielding grounded? In order for the shielding to be effective, it needs to be connected to ground at both ends. Ungrounded shielding can potentially act as an antenna and radiate or collect signals. Additionally, each data wire needs to have a grounded wire as the opposite in its pair (e.g. if solid green is connected to data, striped green should be connected to ground).
Typically with entertainment wiring, you only ground the shield at the source end, not the destination end. There's really nothing to ground to at the pixel end anyhow. This one ended shield grounding is done to prevent ground loops. So make sure the drain wire of the shielding is connected to the ground terminals of the pixel connectors at the 682.
I do this myself out of good practice and old habits. But I doubt this is contributing to your problems. I've seen all sorts of problems with long lead lines on pixels. My rule of thumb now is to use balanced pixel extenders for anything longer than 15' or so. That's solved all of my problems.
--Jon Chuchla--
Sent from my iPhone using Tapatalk
Make sure that you're looking at this in small pieces...I had a situation last night where I added a null pixel...Lights came on and everything went nutz. Checked my wiring, all fine. Cut the pixel out thinking it's bad...same thing. Took the pixel straight to the e682...worked. put it back in line...went nutz. I reached over and bumped the 120v cord...the pixel blinked and worked for a second. Come to find out, the data line would get noise on it when next to my power supply plug in wire....go figure
Seems like the power supply is injecting switching noise back into the power line, when was then coupling into the data line going to the pixel string/strip. There have been FCC regulations in effect for many decades covering what a device is allowed to inject back into the power line, and that power supply would seem to be in flagrant violation.
Where did you get the power supply?