StickyWicket wrote:I am by no means an electrical guru but in your picture isn't that still only two 15A circuits? Just because there are 4 receptacles doesn't give you more amperage allowed, only more receptacles to plug things into.Last year I had 12 400 watt power supplies in my show and that is going up this year possibly doubling that amount. You start running out of amps real fast that way.
I have no idea the scale/scope of the OP's display but running circuits again because you didn't plan for future growth is a waste of both time and money.
12 - 400W power supplies, ok, but not all at one location, and one circuit.
20A circuits are fine, but if you are adding new cables from the load center, then 14/3 has similar costly, but 33% more power.
Yes that is 2 "full" 15A circuits, but only 3 wire (not the typical 4) And yes, I'm showing a couple receptacles on each circuit. You can have more or less on either circuit.
My intended point was to say; use several 15A circuits, but if you need more than 15A at a single location, go 2-15A circuits and gain the benefits of 10A additional power....even if you are not going to use it now. Plus #12 wire is much harder to deal with than #14
Now the circuitry is a little different than most are familiar, however any electrician would understand. Or I can try to explain.
dmpeaceman wrote:Funny - I just posted about my project for this as well.I agree with SitckyWicket - go 20A, not 15A. You get 33% more power, for a very negligible price difference. Make sure you are using 12/3 wire for all you in-wall/in-attic work which can support 20A.
just a little fact checking.....
12/3 or 12/2 with a Ground.
Review my design again....if 20A over 15A is 33% more power, than twin 15A'a (30A) is 50% more power than your 20A. And a 100% more power than the 15A
mrGrumpy wrote:12 - 400W power supplies, ok, but not all at one location, and one circuit.
20A circuits are fine, but if you are adding new cables from the load center, then 14/3 has similar costly, but 33% more power.Yes that is 2 "full" 15A circuits, but only 3 wire (not the typical 4) And yes, I'm showing a couple receptacles on each circuit. You can have more or less on either circuit.
My intended point was to say; use several 15A circuits, but if you need more than 15A at a single location, go 2-15A circuits and gain the benefits of 10A additional power....even if you are not going to use it now. Plus #12 wire is much harder to deal with than #14
Now the circuitry is a little different than most are familiar, however any electrician would understand. Or I can try to explain.
I've done a bit of research on wiring GFCI's this way and it was my understanding that this wouldn't work because the GFCI wouldn't "sense" the correct current on the shared neutral. (I could be wrong though)
Honestly I was inspired by you dmpeaceman to post this.
I'm using roughly 40 amps spread across 3 15amp circuits - the 40 amp number is high too. That's taking everything as on which it rarely is at full and I know the of the 5 300 watt power supplies I have are not being pushed anywhere near the 80% mark with what's on them. Plus animated display so the usual not everything is on all the time...
I've taken some pics of my panel. I want to run the circuits about 50-60 feet away from the panel. The layout is wide open right now. I have a 4' wide wall that my only limiting factor is about 3' from the floor up is concrete. The wall itself is unfinished drywall on the inside and the outside is vinyl siding. I'd like to put the outlets on the outside wall just to keep things cleaner. I could put them on the inside of the garage by the panel. Just was trying to avoid the extension cables - at least the 40 or so feet I'd save... Probably in the end easier just to have them on the wall in the garage.
How do you determine the capacity left on a panel? I have the slots but I'm wondering on what it can handle load wise. Hopefully what I posted can help...
Sorry for the crappy labeling. Previous owners really weren't good on that front.
StickyWicket wrote:I've done a bit of research on wiring GFCI's this way and it was my understanding that this wouldn't work because the GFCI wouldn't "sense" the correct current on the shared neutral. (I could be wrong though)
Shared neutral is before your GFI's (line side) therefore has no affect. Actual, current may flow L1-L2 and no neutral current at all. GFI only senses the load side.