JasonPortwood, looking at your panel I see a issue (I think) with your top right 2 breakers. This indicates you have an electric range......if that is true, then you need to replace the top right 2 breakers with one 50/2 breaker. Don't delay any longer than necessary.
JasonPortwood wrote:Honestly I was inspired by you dmpeaceman to post this.I'm using roughly 40 amps spread across 3 15amp circuits - the 40 amp number is high too. That's taking everything as on which it rarely is at full and I know the of the 5 300 watt power supplies I have are not being pushed anywhere near the 80% mark with what's on them. Plus animated display so the usual not everything is on all the time...
I've taken some pics of my panel. I want to run the circuits about 50-60 feet away from the panel. The layout is wide open right now. I have a 4' wide wall that my only limiting factor is about 3' from the floor up is concrete. The wall itself is unfinished drywall on the inside and the outside is vinyl siding. I'd like to put the outlets on the outside wall just to keep things cleaner. I could put them on the inside of the garage by the panel. Just was trying to avoid the extension cables - at least the 40 or so feet I'd save... Probably in the end easier just to have them on the wall in the garage.
How do you determine the capacity left on a panel? I have the slots but I'm wondering on what it can handle load wise. Hopefully what I posted can help...
Sorry for the crappy labeling. Previous owners really weren't good on that front.
You are currently using 40A (max-all-on) for a 45A supply. You are correct about the "not always on" thing, I just tend to not want to re-do my work in a year or two when the numbers grow. It will be much easier to do it all now, and not have to worry about it later...my two cents, but totally your call! 😛
I'm having troubling picturing your issue with the inside vs outside wall. Can you take a picture, and show me what you are trying to decide?
About your question on load - and note I'm NOT an electrician - so don't take this as legal advice, I've just done all the electrical in my house, including a DIY 8.7kW solar system... but honestly, I would not worry about the size of your panel unless you are running everything in your house at once. You are running your christmas light show once a year, and only at night....it's not going to be a big draw on your household, especially with a 200A panel. You are fine to load up your panel - I have probably 500A of breakers in my 200A panel. You're fine!
mrGrumpy wrote:just a little fact checking.....
12/3 or 12/2 with a Ground.Review my design again....if 20A over 15A is 33% more power, than twin 15A'a (30A) is 50% more power than your 20A. And a 100% more power than the 15A
I stand corrected. 12/2 with ground is what I meant, not 12/3. Thanks.
And you aren't really comparing apples to apples with your suggestion. I think the suggestion is that if he's going to put in 3 x 15 amp circuits - why not make 3 x 20 amp circuits instead (33% more power). Sure - if he adds MORE circuits he'll have more power. Not quite sure the argument :-/
Back in 2009, I had to run some extra power and outlets for my LOR boxes so I put in a 100 AMP sub panel and ran conduit out to 3 posts on my front deck. I have 2 - double outlet weatherproof boxes on each deck so I have a total of 12 - 20 amp circuits going out front (I have 2 outlets in each box and a separate 20 amp GFI breaker for each one in the panel box (I wasn't going to have to go outside for a tripped circuit!). I ran 12 AWG stranded THFN wire to each outlet for hot, neutral, and ground to keep things separate for current capability.
Of course, this is way overkill for pixels and such but sure made life much easier. I even had enough circuits that I kept one for the engine heater in my truck! Sorry, I don't have pictures on this computer to show but hopefully, you get the idea and can see my deck on my web page.
dmpeaceman wrote:.....And you aren't really comparing apples to apples with your suggestion. I think the suggestion is that if he's going to put in 3 x 15 amp circuits - why not make 3 x 20 amp circuits instead (33% more power). Sure - if he adds MORE circuits he'll have more power. Not quite sure the argument :-/
Point is....you need to run 12/2+G to get 20A, but if you run 14/3+G (at similar cost) you get 30A. Similar cost, more amps, and still pulling one Romex. So for each 15a circuit you suggest changing to 20A, I suggest changing to twin 15A (30A) Downside; Needs too use 2-15A GFI's at each circuit.....but that could also be an upside, splitting loads to reduce rain effects ground faults.