HydroWVU wrote:I am complete newbie when it comes to electricity thanks for your patience in answering my questions.What gauge wire do you run from your controller to you pixel strings. I was thinking 18awg would be a nice balance between cost and voltage performance.
Thanks
John
Sent from my iPad using Tapatalk HD
That all depends on length of the extensions and the number of pixels on the string. The longer the extension the more resistance thus more voltage drop. Also the more pixels the more current thus more voltage drop.
Voltage drop is fairly simple in a DC circuit V=IR, so if you have a 20' #18AWG extension with 200 pixels on it your voltage drop will be substantial so the extension losses might be too much right off the start, But if you have a #12AWG extension it might be just fine running 200 pixels injecting at the start and end.
In my own I try to use at least #16 up to 10', #14 up to 20', over 20' #12. Once over 20' you need to watch things, try to keep pixel loads to a minimum to limit voltage drop.
OK.. now that I have caught up on this thread I would like to chime in if I may.
If you are running short distances the list of wire sizes that Electrified3 put out there should be good for distances he said. But keep in mind that if you are running 200 pixels and you need to inject at every 50, you will most likely have to add wire length. If you are running a matrix, (50 pixels or less per repeating row) which seems to be the jest of most of this thread, you can feed from one proximity location and you should be good. But........
........Not everyone will be doing it this way. As Electrified3 said, "Once over 20' you need to watch things". He is dead on the money. For the Plasma Icicles I had as much as 60 foot power runs. That is why I used the DC-DC converters. The wire size went way down, the voltage is stable at every point along the way, it was less expensive than heavy gauge wire without the drop, and they have protection built in. My point is that if you are exceeding that 20' mark in wire length, and in many cases even closer, you should consider using converters. You can buy them pretty cheap, (cheaper than wire in some cases).
If you are going to play in the pixel arena and you want them to look good, you really need to make sure the power is there to run them correctly. If you don't really care how they look, then as long as they work I guess you can go for it.
Also, keep in mind that once you reach about 75% brightness, you won't notice them getting much brighter ... so, if you want to keep that limit under control on the programming side, you may find your power requirements are easier to fulfill. Just a thought.
Thanks Pythan for the input. I have noticed a few things as well since I started this thread, the best way to validate is running pixels full white to get the true full potential requirements of the pixels. When I did that with a string 200 pixels long with a #16AWG 20' extensions running full white I was seeing it start to drop after about 46 pixels, if I did inject at every 50 full white should work properly. On the strip, 150 pixels on 5M faded out around 100 pixels but stayed white, just reduced intensity, when I added injection to the end went back to full intensity. Now to note on that one I had no extensions on it when running the test.
I took at look at these DC-DC converters you were talking about, looks like a very good option, especially for me since I have all kinds of 24VDC power supplies kicking around. Where do you recommend to buy these DC-DC converters? I would like to try a few of them out but I am also in Canada. Now at 24VDC your voltage drop would be dramatically reduced over long distances compared to 5VDC, only issue I would see is cost for the supplies. Working in the industrial controls field 24VDC is common and easy to get my hands on, but I also know the cost of industrial grade power supplies as well.
The converters I bought worked fine, but the company that made them was just aweful to deal with so I don't advertise them. I had a very high percentage of converters that were bad due to the fact that the +5vdc out was physically shorted to the heatsink and it was not supposed to be. When I clamped them to the conduit they just shorted out because I grounded all my conduits to eliminate noise. The factory would not acknowledge they had a manufacturing issue.. no matter how hard I tried to help them. I even shot video of testing the few replacement for that short before the package was open. The out of the package fail rate was between 15-50% depending on which group I tested. I finally had to arbitrate via PayPal and get some of my money back.
Anyway, I don't recommend them as a company.. but there are lots of converters out there. The ones that were not shorted internally wound up working very well.. except for one that went high voltage on me, but that is a rare occurrence and not something I worried about.
I have about 60 different ones that I bought from Ray for less than $2 each. They are just not waterproof... I also bought a bunch of little heatsinks for them at sub $ price. I was thinking of doing a potting run with those.
BTW, I have about 30 or 40 24vdc 240watt power supplies for sale if you need any. They are new, wet location rated and UL recognized. Made for high power LED fixtures and are made like tanks.
How much are you selling the power supplies for?
I might be interested in the 24 volt power supplies also... I am just starting out with pixels and will have a run at least 50' for probably not even a full sting of 50 but the end will be a long way away from my power source.
I am asking $40 each if you buy less then 5 and $30 each if you buy a case of 5 supplies. FOB Elk Grove Ca. They are a heavy because they are internally potted. Cheaper then getting them from China, but still costs.. I also have the chassis mount mate to the connector and a water proof cable for in between.
Dropbox File (Private or Invalid)
Just a quick question that's related to power injection. I was able to get 500ft of white cat3 cable today for $6. Since I'm building my pixicles with white 2811 12v nodes I thought it would be great to use this for power injection so it'll blend in. My question is, about how many pixels would be the limit to run injection for if I split the 2 pairs up and used 2 wires for + and 2 for -? I'm wanting to run 100 pixels on each 682 output and inject power at the end of it.
dsmjuggalo wrote:Just a quick question that's related to power injection. I was able to get 500ft of white cat3 cable today for $6. Since I'm building my pixicles with white 2811 12v nodes I thought it would be great to use this for power injection so it'll blend in. My question is, about how many pixels would be the limit to run injection for if I split the 2 pairs up and used 2 wires for + and 2 for -? I'm wanting to run 100 pixels on each 682 output and inject power at the end of it.
If I remember correctly, CAT5 cable is only 30 gauge. Not sure I would run any power injection from 30 gauge wire.
It's actually 24, doubled up is about equal to 21 gauge