Schobes wrote:But earlier in this thread it was recommended to run all 32 strings on a single controller by making 16 strings of 100 and connecting the end of the string back around to the same output channel (see this diagram - http://doityourselfchristmas.com/forums/attachment.php?attachmentid=22774 ).
This looks really odd to me. While I suppose you could run the power in a loop from the E682 like this, it certainly is more complex than necessary. Additionally, each output channel is fused for 5 amps - and 110 pixels per output will likely exceed this.
One power supply is 60 amps. 32 strings of 50 (1600 pixels) is 96 amps. So I still need 2 power supplies.
Correct. You couldn't run all 1600 pixels off one 60 amp supply.
How can you connect two 60 amp supplies to a single e682? Aren't the power inputs limited to around 30 amps per side?
Yes, but amperage is actual current flow, not *potential* current flow. The supplies will provide UP TO 60 amps each based on the amount of power being demanded. Simply plugging in two 60 amp supplies to the E682 (one on each side) will cause no problems because there's virtually no power flow/amperage (only that needed to power the E682). But if you then tried plugging in all 1600 lights, then the flow/amperage would exceed the fused amount and you'd have problems.
However, you can decrease power flow/amperage through the E682 by providing power elsewhere via power injection - sharing the load via another source.
There are several ways to wire this. One option is one power supply at the E682 that powers both sides of the controller and the first 50 pixels of each 100 pixel string - one string per E682 output. Then a second power supply powers the last 50 pixels in each string (you could inject power at either pixel 51 or pixel 100, it doesn't matter). Just be sure you disconnect the V+ wire between pixels 50 and 51 (you never want V+ from two separate power supplies to be connected), but ensure that V-/Ground is connected between the supplies.
Another option is to connect both power supplies to the E682 - one on each side. You would still, however, need to do power injection from those power supplies to the ends of each pixel string to keep the amperage through the E682 within limits. You'd run 8 strings off half the E682 and power inject at the end of those same 8 strings using the same power supply. In this case, you don't need to break the V+ because it's coming from the same source, though the flow through the E682 would be roughly half (wire length, gauges, etc. would be factors) that required to power the string (the other half comes from the power injection point).
Hopefully this helps.
apollosmith wrote:
Another option is to connect both power supplies to the E682 - one on each side. You would still, however, need to do power injection from those power supplies to the ends of each pixel string to keep the amperage through the E682 within limits. You'd run 8 strings off half the E682 and power inject at the end of those same 8 strings using the same power supply. In this case, you don't need to break the V+ because it's coming from the same source, though the flow through the E682 would be roughly half (wire length, gauges, etc. would be factors) that required to power the string (the other half comes from the power injection point).Hopefully this helps.
This will not quite work the way you expect. If the fuse on the 682 were to blow due to a short in the string, the string would still overheat because you are injecting power from the other end to the entire string. Also, if the E682 fuse were to blow for some trivial reason, you would get the lights near the E682 end of the string show as dimmer than the lights further from the E682. You really should cut the V+ line at the 50 LED point and you really need to have a fuse in the power injection lines as well.
I believe that the picture above was in reply to someone who wanted to inject power at the top of the megatree.
So would it be a bad idea to run the e682 with one 5v power supply feeding both sides which will allow you to use the onboard fuse for the first 50 pixels then have a separate 5v power supply to inject. Terminate the + and - at the end of 50 ct but continue the data, inject power from a fused wire with a common ground from the power injection supply (not the supply for the e682) and call it a day?
4586shaggy wrote:So would it be a bad idea to run the e682 with one 5v power supply feeding both sides which will allow you to use the onboard fuse for the first 50 pixels then have a separate 5v power supply to inject. Terminate the + and - at the end of 50 ct but continue the data, inject power from a fused wire with a common ground from the power injection supply (not the supply for the e682) and call it a day?
This will work great, EXCEPT that you do not want to terminate the - at the end of the 50 count. You want the - for both supplies to be connected through the pixel strings so that they share a common ground reference.
There's some debate (as you can see above) about whether it's best to terminate the + in the middle if you're using a single power supply. Terminating isolates both strings. If you have a power failure at one end, it will only affect the part of the string that power supply is connected to making it easy to track down the problem.
Not terminating the + provides a better power balance. But if there is a failure (such as a blown fuse) on one supply wire (or in the E682), and the other supply wire can't meet the power demand, you could blow a fuse (or worse) making it difficult to debug what happened. If the string is so long that it shouldn't/can't be powered by the single wire (110 pixels is definitely pushing it), then terminating and isolating the power lines is probably best.
Regardless, you want to properly fuse all V+ lines.