Beginners Setup Guide Renard Boards with External SSR
This page was created to help out the new users who aren't fully confident that they have built their Renard board correctly. These steps are designed to allow the user to test/verify most components in a manner that should help to eliminate the possibility of damaging any of the components during initial testing.
The following procedures may appear to be tedious and time consuming but they are here for the individuals who are not confident in their soldering skills. By following these steps, the individual will be able to test out individual components and signal paths to verify that everything is working properly with minimal damage to components and rework.
The following procedures require the individual to be familiar with the operation of a digital multimeter (or voltmeter/ohmmeter if you prefer). If you currently do not know how to measure resistance or how to measure voltage, please take some time now an learn these basic skills before attempting these procedures. This website provides some basic information on using multimeters.
| All DC voltages in this document are referenced to GND. So for all measurements, the multimeter negative (-), usually black, lead needs to be connected to a GND point on the PCB. The best location would be TP1 which is the GND Test Point located near J21. The positive lead (+), usually red, gets connected to the location called out in the procedure. |
Renard Basic Setup Steps
- Ensure all power is OFF
- Remove all cables
- If installed, remove all the removable IC chips. For this example, the REN64 will be used. For other boards, the items will be similar but the chip number may be different. The REN64XC chips to be removed are: U3, U4, U5, U7-U14.
- Perform a complete and thorough inspection of the underside of the PCB.
- Check all the solder pads for clean solder joints, no bridging between adjacent pads and that all pads did get soldered.
- Make sure the board surface is clean and free from any debris and flux residue.
- Connect a 6.3VAC power supply to Tab1/Tab2. This requires understanding how to wire up the transformer. If you are using this guide, it is suggested that you install an inline fuse for troubleshooting purposes.
- Turn ON AC power
- Measure DC voltage at U1. This is the lead closest to U4. You can also measure this at the input to R8 next to U5.
- It should be 5.0 (+/- .1) VDC.
- If incorrect , then go to the Renard 64XC Troubleshooting Guide.
- Power LED should be lit.
- If it didn’t , then go to the Renard 64XC Troubleshooting Guide.
- Momentarily connect a jumper (small piece of wire) between U10 IC socket pin 13 and pin 14.
- Channel 2 LED should light-->This is the HB LED. Once again, the chip numbering is specific to the Renard 64XC. Some Renard boards have specific LEDs for the HB or "Heart Beat" Function.
- Momentarily connect a jumper between U10 IC socket pin 10 and pin 14
- Channel 5 LED should light -->This is the ZC or "Zero Crossing" LED.
- Momentarily connect a jumper between U10 IC socket pin 9 and pin 14
- Channel 6 LED should light -->This is the SD or "Data" LED.
- Momentarily connect a jumper between U10 IC socket pin 8 and pin 14
- Channel 7 LED should light -->This is the FE or "Framing Error" LED.
- Momentarily connect a jumper between U10 IC socket pin 7 and pin 14
- Channel 8 LED should light -->This is the OE or "Overun" LED.
- If any of the LEDs in steps 11 thru 15 did not light, then go to the Renard 64XC Troubleshooting Guide.
- Turn OFF AC power.
- Install a SSR like the SSRez into J12 with a known good straight through CAT5 cable. If you are not sure that the cable is good, use the DMM to ring out the cable.
- Attach some test lights to the SSR terminal block for Channel 1.
- Turn ON AC power.
- The power LED on the SSR should be on.
- Test lights should be OFF.
- Momentarily connect a jumper (small piece of wire) between U10 IC socket pin 3 and pin 14.
- Test lights should come ON when the jumper is connected.
- If either step 23 or step 24 failed, then go to the Renard 64XC Troubleshooting Guide.
- Repeat steps 18 thru 25 using the information in the table. Once again, the IC Chip numbering and the Jack numbering are for the Renard 64XC.
Board Channel IC Socket Number Output Jack Test Lights at SSR Channel Connect jumper between Channel 1 U10 J12 Channel 1 Channel 2 U10 J12 Channel 2 Channel 3 U10 J12 Channel 3 Channel 4 U10 J12 Channel 4 Channel 5 U10 J8 Channel 1 Channel 6 U10 J8 Channel 2 Channel 7 U10 J8 Channel 3 Channel 8 U10 J8 Channel 4 Channel 9 U9 J11 Channel 1 Channel 10 U9 J11 Channel 2 Channel 11 U9 J11 Channel 3 Channel 12 U9 J11 Channel 4 Channel 13 U9 J7 Channel 1 Channel 14 U9 J7 Channel 2 Channel 15 U9 J7 Channel 3 Channel 16 U9 J7 Channel 4 Channel 17 U8 J10 Channel 1 Channel 18 U8 J10 Channel 2 Channel 19 U8 J10 Channel 3 Channel 20 U8 J10 Channel 4 Channel 21 U8 J6 Channel 1 Channel 22 U8 J6 Channel 2 Channel 23 U8 J6 Channel 3 Channel 24 U8 J6 Channel 4 Channel 25 U7 J9 Channel 1 Channel 26 U7 J9 Channel 2 Channel 27 U7 J9 Channel 3 Channel 28 U7 J9 Channel 4 Channel 29 U7 J5 Channel 1 Channel 30 U7 J5 Channel 2 Channel 31 U7 J5 Channel 3 Channel 32 U7 J5 Channel 4 Channel 33 U14 J21 Channel 1 Channel 34 U14 J21 Channel 2 Channel 35 U14 J21 Channel 3 Channel 36 U14 J21 Channel 4 Channel 37 U14 J16 Channel 1 Channel 38 U14 J16 Channel 2 Channel 39 U14 J16 Channel 3 Channel 40 U14 J16 Channel 4 Channel 41 U13 J20 Channel 1 Channel 42 U13 J20 Channel 2 Channel 43 U13 J20 Channel 3 Channel 44 U13 J20 Channel 4 Channel 45 U13 J15 Channel 1 Channel 46 U13 J15 Channel 2 Channel 47 U13 J15 Channel 3 Channel 48 U13 J15 Channel 4 Channel 49 U12 J19 Channel 1 Channel 50 U12 J19 Channel 2 Channel 51 U12 J19 Channel 3 Channel 52 U12 J19 Channel 4 Channel 53 U12 J14 Channel 1 Channel 54 U12 J14 Channel 2 Channel 55 U12 J14 Channel 3 Channel 56 U12 J14 Channel 4 Channel 57 U11 J18 Channel 1 Channel 58 U11 J18 Channel 2 Channel 59 U11 J18 Channel 3 Channel 60 U11 J18 Channel 4 Channel 61 U11 J13 Channel 1 Channel 62 U11 J13 Channel 2 Channel 63 U11 J13 Channel 3 Channel 64 U11 J13 Channel 4
- Install optocoupler U2.
- Install two (2) RS232/RS485 Interface ICs U4 and U5.
- If you have a PIC programmed with the Renard Diagnostic Firmware continue with step 27.
- If you only have a PIC programmed with the Renard Operational Firmware then go to step 43.
- Install PIC microcontroller U10 programmed with the Renard Diagnostic Firmware.
- If desired, attach SSRs with lights to J12 and J8 with CAT5 Cable. The diagnostics can be done with only the on-board Channel LEDs.
- Turn ON AC power
NOTE:
The following step only applies if you are using the Beta Renard Diagnostic Firmware.
If you are using the proven/existing Renard Diagnostic Firmware just skip this step.
- The Renard Diagnostic Firmware should perform the following channel test:
- All channels ON for approx. 2 seconds.
- All channels OFF for approx. 2 seconds.
- Channel 1 LED and Channel 1 turns ON for approx. 1 second then turns OFF.
- Channel 2 LED and Channel 2 (HB LED) turns ON for approx. 1 second then turns OFF.
- Channel 3 LED and Channel 3 turns ON for approx. 1 second then turns OFF.
- Channel 4 LED and Channel 4 turns ON for approx. 1 second then turns OFF.
- Channel 5 LED and Channel 5 (ZC LED) turns ON for approx. 1 second then turns OFF.
- Channel 6 LED and Channel 6 (SD LED) turns ON for approx. 1 second then turns OFF.
- Channel 7 LED and Channel 7 (FE LED) turns ON for approx. 1 second then turns OFF.
- Channel 8 LED and Channel 8 (OE LED) turns ON for approx. 1 second then turns OFF.
- The above routine is done three times.
- The Renard Diagnostic Firmware should now be blinking the HB LED (Channel 2) and ZC LED (Channel 5). All other channels/LEDs should be OFF.
- If either step 30 or step 31 failed, then go to the Renard 64XC Troubleshooting Guide.
- Connect a data cable to the computer running Vixen to either J4 or J22 on the Renard board..
- If receiving RS232 data from the computer place a shunt on JP1.
- Turn ON AC power.
- Wait for the diagnostics routine in steps 30/31 to complete.
REMINDER:
The Renard 64XC Controller Board wiki page. The only difference would be to
set the baud rate to 19200 for the non-beta Renard Diagnostic Firmware.
- Run a Vixen sequence.
NOTE:
- SD LED (Channel 6) will be ON whenever Vixen sends data to the Renard 64XC. The FE (Channel 7) and OE LEDs (Channel 8) should remain OFF.
- Turn OFF AC power
- Remove U10
- To verify other functional PICs, repeat steps 27 thru 40 with the other seven (7) PICs
- Install PIC microcontrollers U7-U14 programmed with the Renard Operational Firmware.
- Turn ON AC power
REMINDER:
- If the outputs do not respond correctly, then go to the Renard 64XC Troubleshooting Guide
