The lor board will be a learning curve also. But will have the heavy work done for you as far as the circuits go.
Pcguy17 wrote:10 amps from what i understand
the outlets are 15amps
So No i don't plan to max them out... But i think im using bigger wires then most use... its 14 gauge.
Ok, So my concerns are confirmed and it leads me to a few more questions.
1) How many power feeds are you going to have coming in to this enclosure?
2) How many Amps per feed?
3) Are you going to fuse the outlets?
4) If yes, what size fuses are you going to use?
If the SSR’s are rated at 10 Amp and you only load them to 5 Amps with 8 relays you are still looking at 40 Amps. Of course fully loaded that is 80 Amps and this is a huge problem with how you are wiring them. The daisy chained neutral is not big enough to handle anywhere near 40 Amps, much less 80 Amps. I am not sure that your Ground is even big enough in the event of a case short to Ground.
Some more detail as to what you are trying to run with this as far as electrical load would be immensely helpful in helping you build a safe and functional circuit.
Regards,
John.
wirenut1980 wrote:The connecters I posted are called push in connectors. They should have them at the hardware stores. If not try Amazon. The blue connectors you posted are to be used for low voltage wiring only. Like in your cars 12v system. Do not use them to connect AC current as this could be dangerous. The way the relays work is there is a 5v side {if that's what the rating is on yours} that is the controlling side from the pi. The switching side is the high voltage side. They work kinda like your light switch. There is 110v in your home walls. Pretend you are the raspberry pi. Your brain says turn on the light. You use a low voltage energy {your hand} and flip the switch controlling the high voltage. Like a relay you are physically touching the switch but never the high voltage. The 5v and 110v are going to be somewhat in the same location but never touch.
Oh, i didn't even think about that with the connectors.. only hardware store around my town is a family owned place that never had what i need. but i bet another place i know about would have them or i will just order some online.
wirenut1980 wrote:The lor board will be a learning curve also. But will have the heavy work done for you as far as the circuits go.
Why you say that? its already build.. just plug up the two cords, and a Ethernet cable and set the Vixen for it and turn it on should be...
your right i wont have to be building anything.
jmruth72 wrote:Ok, So my concerns are confirmed and it leads me to a few more questions.
1) How many power feeds are you going to have coming in to this enclosure?
2) How many Amps per feed?
3) Are you going to fuse the outlets?
4) If yes, what size fuses are you going to use?
If the SSR’s are rated at 10 Amp and you only load them to 5 Amps with 8 relays you are still looking at 40 Amps. Of course fully loaded that is 80 Amps and this is a huge problem with how you are wiring them. The daisy chained neutral is not big enough to handle anywhere near 40 Amps, much less 80 Amps. I am not sure that your Ground is even big enough in the event of a case short to Ground.
Some more detail as to what you are trying to run with this as far as electrical load would be immensely helpful in helping you build a safe and functional circuit.
Regards,
John.
1> Power feeds? only one, as main power. it have 5v from the PI then the 110 from the plug in.
2>Amps, not sure i have to test some lights and do some math
3>fuse the outlets? you mean from the outlets themselves? isnt that what the Relays do? im not sure how you would fuse those... I mean all christmas lights have fuses inside the plug in for them
4> its 10 amps per relay.. and so there are just 2 sockets on one outlet.. so you don't think you can pull 20 amps through 14 gaudge wire?
I don't get why it would be any driffrent from me plugging in (6) 100 light sets of lights into a 100 foot drop cord that is plugged into a outlet on the side of the house?
I know for a fact that Christmas lights really don't pull that many amps.. LED christmas lights even less...
I run 2 sets of 100 light Christmas lights, along with a lighted candy cane, a 2 foot Santa Claus figure off of a 200 watt power inventor on my truck every year it runs all of that just fine. I think i was at around 2 amps total. its been a while since i checked it i will be checking them again this year want to add more so might use my 400watt inventor. Are you a licensed electrician?
You should check out this guys set up.... it looks.... interesting to say the least
Bwinter wrote:You’re given a lot of good VALID advice. I don’t understand why you won’t listen.
What do you mean? I came here looking for help from people who has done the same exact thing i am wanting to do.. and i have tried to do what people have told me.
Pcguy17 wrote:1> Power feeds? only one, as main power. it have 5v from the PI then the 110 from the plug in.
2>Amps, not sure i have to test some lights and do some math
3>fuse the outlets? you mean from the outlets themselves? isnt that what the Relays do? im not sure how you would fuse those... I mean all christmas lights have fuses inside the plug in for them
4> its 10 amps per relay.. and so there are just 2 sockets on one outlet.. so you don't think you can pull 20 amps through 14 gaudge wire?I don't get why it would be any driffrent from me plugging in (6) 100 light sets of lights into a 100 foot drop cord that is plugged into a outlet on the side of the house?
I know for a fact that Christmas lights really don't pull that many amps.. LED christmas lights even less...
I run 2 sets of 100 light Christmas lights, along with a lighted candy cane, a 2 foot Santa Claus figure off of a 200 watt power inventor on my truck every year it runs all of that just fine. I think i was at around 2 amps total. its been a while since i checked it i will be checking them again this year want to add more so might use my 400watt inventor. Are you a licensed electrician?
There isn't a difference in running 2 LED light strings off this or off a single extension cord. But that is the information people need to know to tell you if your wiring will work. Each relay is rated for 10 amps, making the relay board capable of passing 80 amps. However, your "feed" power cord isn't rated for 80 amps, and most likely the outlet you'll run this off of isn't rated for 80 amps, and the wire daisy chain isn't rated for 80 amps etc. The point they're making is they need to know what the max load you're designing for is. No one can tell you "your setup looks correct and safe" without knowing what you're going to plug into it. If you plan on using less than 2amps per outlet, that is what people need to know to help you.
well channel I know for a fact that these will have these amounts on them
channel #8 )50 lights LED
#7)50 lights LED
#6 )200 lights LED
#5) 100 or 200 at max encans
#4-1 are the ones I need to test. I want those to run my megs tree ( it's only a 10 ft tree with encans lights) also I wanted it to run 200 lights on each of my mini trees. but maybe that would be to much power? I've not got my tester out to test them yet.
so what is a safe amount to run through this set up? I know the LOR boxes have 2 110v plug ins for power. and been told they need to be plugged into driffrent outlets on driffrent breakers to get there full 30 amps of power but I'm sure I'm not pulling 30 amps at least never at once... these are sqenced lights so there never all on at the same time..
I appreciate the ones trying to help and well you just built same thing how many lights are you planing to hook up to urs?
So sold all of the daisy chained neutrals and white wires be split in the middle and have a input plug on each half? hard to half 5 of something guess 2 could be on one side and 3 on the other .
at this point I'm so frustrated I'm about to just drag out my Mr christmas box and use it again. and spend the money I was going to buy a lor box and buy lot more led lights
thanks
Sent from my SM-S920L using Tapatalk
My SSR is rated for 2 amps per relay, total of 16 amps at max. I built mine with a max of 16 amps in design, but I'm only using .5 amp per outlet and don't intend to ever have more than 1 amp per outlet. With 100 count LED strings from Wal-Mart this equates to about 10 strings for 1 amp (1000 lights!). If you can't fit 2 wires in your relay to chain them then I would recommend running a short wire from your "feed outlet" to each relay instead of using smaller wire.
Pcguy17 wrote:well channel I know for a fact that these will have these amounts on them
channel #8 )50 lights LED
#7)50 lights LED
#6 )200 lights LED
#5) 100 or 200 at max encans
#4-1 are the ones I need to test. I want those to run my megs tree ( it's only a 10 ft tree with encans lights) also I wanted it to run 200 lights on each of my mini trees. but maybe that would be to much power? I've not got my tester out to test them yet.so what is a safe amount to run through this set up? I know the LOR boxes have 2 110v plug ins for power. and been told they need to be plugged into driffrent outlets on driffrent breakers to get there full 30 amps of power but I'm sure I'm not pulling 30 amps at least never at once... these are sqenced lights so there never all on at the same time..
I appreciate the ones trying to help and well you just built same thing how many lights are you planing to hook up to urs?
So sold all of the daisy chained neutrals and white wires be split in the middle and have a input plug on each half? hard to half 5 of something guess 2 could be on one side and 3 on the other .
at this point I'm so frustrated I'm about to just drag out my Mr christmas box and use it again. and spend the money I was going to buy a lor box and buy lot more led lights
thanksSent from my SM-S920L using Tapatalk
One standard outlet has a maximum rating of 15 amps so that is the most you should plan for. If there are other things on this circuit that will be on at the same time, you need to consider those, too, so the total doesn't exceed 15 amps. Your wiring should be 14 gauge or better. If your wiring is 14 gauge, you don't need to split the neutrals. Your house wiring is set-up in a similar fashion, i.e. multiple plugs on one power feed. Frustration is part of the learning process but as with many things, the end result is worth it. Hang in there!
Jediosu wrote:My SSR is rated for 2 amps per relay, total of 16 amps at max. I built mine with a max of 16 amps in design, but I'm only using .5 amp per outlet and don't intend to ever have more than 1 amp per outlet. With 100 count LED strings from Wal-Mart this equates to about 10 strings for 1 amp (1000 lights!). If you can't fit 2 wires in your relay to chain them then I would recommend running a short wire from your "feed outlet" to each relay instead of using smaller wire.
oh wow only 2 amps. I thought they were all 10 amp I guess like anything you can get driffrent rated anything .
my mega tree has 1300 lights on it so I'm guessing that's to much for this set up. it's not 1300 on one channel it has 4 sets of lights on it red,green,blue,clear it has 300 of each color on it and i wanted to hook each color to a driffrent output.
so maybe that wouldn't be to much but there not led so I have to test how many amps they pull
Sent from my SM-S920L using Tapatalk
It sounds like you got a mechanical relay where I have a solid state one, thus the difference in ratings. The above advice for designing around 15 amps maximum sounds like a good idea. Once you know how much power each string and decoration uses you'll have a good idea of what you can do.