I have a Simple Ren32 running with 6 DirkCheapSSRs, 1 NEON, and 4 channels sitting unused. These 6 are for arches and no troubles.
A Ren64 with 13 DirkCheapSSRs and the rest on it is a couple Neons and an SSRez. No snags there everything powers up. These are for wreaths / window frames and lighting poles.
I have a couple sequences that turn everything on and I haven't seen any problems. Fades and speed look to be working too.
I put a kill-a-watt on my Ren64 and it pulls between 0.13 normally and 0.14 amps when everything is on.
Everything on a DirkCheapSSR is just a single strand of LEDs (if that matters). The parts are from the group buy or like parts I bought later.
Should I just snip out the diagnostic LEDs on the REN64 to be on the safe side?
Now I swore I saw some oddly slow fades at one point when testing but I was using DMX if that matters. I haven't seen anything odd with using RS485/Renard protocol.
-
Jason
It's not cold here, but two of my 3 dirkcheaps are experiencing some sort of problem. I have no idea what the problem is yet, I'll be debugging one in the garage tonight after the kids go to bed and one tomorrow with a multimeter on the roof. I'm really hoping neither have anything to do with this... I really don't want to retrofit the dirkcheaps with 330 ohm resistors. Especially since I don't have any 330 ohm in my case o' resistors!
aixelsyd wrote:I have a Simple Ren32 running with 6 DirkCheapSSRs, 1 NEON, and 4 channels sitting unused. These 6 are for arches and no troubles.A Ren64 with 13 DirkCheapSSRs and the rest on it is a couple Neons and an SSRez. No snags there everything powers up. These are for wreaths / window frames and lighting poles.
I have a couple sequences that turn everything on and I haven't seen any problems. Fades and speed look to be working too.
I put a kill-a-watt on my Ren64 and it pulls between 0.13 normally and 0.14 amps when everything is on.
Everything on a DirkCheapSSR is just a single strand of LEDs (if that matters). The parts are from the group buy or like parts I bought later.
Should I just snip out the diagnostic LEDs on the REN64 to be on the safe side?
Now I swore I saw some oddly slow fades at one point when testing but I was using DMX if that matters. I haven't seen anything odd with using RS485/Renard protocol.
-
Jason
I only saw a .09 pull from my Ren64 with all channels on 100% and on-board LEDs installed. Maybe my Kill-a-watt is broken?
It snowed here today -- and all my controllers are already covered with the stuff. Current temperature is 30F and headed down from there. One of the controllers has a Simple24 and a MegaDirkCheap inside it, which is essentially 6 DirkCheaps on one board. It is powered by a healthy 1.5A wall wart, mounted inside the CG1000 case with everything else, which includes a Ren-W as well.
It's worked flawlessly all night. I think that perhaps one key is having a power supply that's got enough headroom to ensure that there's ample current to drive all the electronics.
I will run my test show all of tomorrow evening so I will know how much I will be affected. There are a couple of songs that have small areas of heavy movement of lights (DirkSSR's was used on a 14ft long, 7ft tall arch filled with lights, 20 channels total with 1-100ct incan per channel) The board is powered by the supply from the group buy on the Ren64.
I would have to believe that if there are trigger issues from the VO2223 this would cause dimming issues, very well could be intermittent based on the load of the controller.
I guess I'll find out if and how much tomorrow.
I don't want anyone to get the impression that they should not use these, Everyone's conditions will be different and my experience with this SSR may be different from others. I am only letting everyone know my experience... That's what we are here for right?
My DirkCheaps need to be modified somehow. I will likely have to swap out resistors.
I have one that I plan on using for one set of incans per channel that won't work with about 40' of cat-5 between the Ren64 and the SSR. If I plug it in near the Ren64 it works fine.
What is the best way to go about determining the proper resistor value? Also, if I just get "close" by using something I have on hand, is it better to go up or down in resistance, and by how much after finding a calculated value?
Materdaddy wrote:My DirkCheaps need to be modified somehow. I will likely have to swap out resistors.I have one that I plan on using for one set of incans per channel that won't work with about 40' of cat-5 between the Ren64 and the SSR. If I plug it in near the Ren64 it works fine.
What is the best way to go about determining the proper resistor value? Also, if I just get "close" by using something I have on hand, is it better to go up or down in resistance, and by how much after finding a calculated value?
Well, replaced with an SSRNeon and I still cannot get that section to work. My cheap CAT-5 tester shows that cable as "OK", but I think something is strange. I re-crimped both sides of the cable, but nothing...
Materdaddy wrote:Well, replaced with an SSRNeon and I still cannot get that section to work. My cheap CAT-5 tester shows that cable as "OK", but I think something is strange. I re-crimped both sides of the cable, but nothing...
Thanks for reporting back. I was getting nervous. Most of my runs are between 15 and 25 feet. I'm more concerned about the 24 channels I'm driving with a 24lv. I can't change that transformer easily.
This is the first year where I don't have extra equipment hanging around. So my options for resolving problems are limited.
Materdaddy wrote:Well, replaced with an SSRNeon and I still cannot get that section to work. My cheap CAT-5 tester shows that cable as "OK", but I think something is strange. I re-crimped both sides of the cable, but nothing...
Coupler.
Thought I had it narrowed down twice. First was the cable. It had a pin that wasn't compressed by my crimper. I had re-crimped and tested before my last post, so I knew the cable was good. Then I used my mutlimeter to test voltage at the SSR end where I found low voltage on pins 1/7. (Pin 1 was the previously uncrimped one). Turns out the un-crimped pin screwed up my RJ45 couplers' pin-1 spring. Since I was trying so many things, I botched 3 separate couplers before realizing that was the problem. Luckily they're easily popped open and the pin can be bent back so they're not broken for good.
Goes to show, just because there's a popular thread discussing random problems with something doesn't mean it's your problem! :omg:
Here's the question: As a quick fix would cutting the diagnostic LEDs out of the Ren64 help?
I don't have the problem occuring but I'd like a fall back incase it does happen. My cable runs are about 50' at the longest (only one of those) and from there it goes down 5 or so feet for each of my 7 runs to my roof.
Also could/will the Simple Renard 32's have a problem with this too? My cable runs for those are very short (15' at most). I plan on using more of those next year so I need to plan.