Seperate breakers
 
Notifications
Clear all

Seperate breakers

20 Posts
10 Users
0 Reactions
7,736 Views
Posts: 2629
(@dynamoben)
Famed Member
Joined: 19 years ago
But, a breaker should be ran at no more than 80-85%.

Where did you come up with this? I've been doing electrical work (personal and professional) for a long time and never heard of such a thing. Breakers are actually designed to exceed their rating for a short snap of time. Often times you can run over 15A and still won't get the breaker to trip...not recommended but true.


Reply
Posts: 1084
 ben
(@ben)
Noble Member
Joined: 19 years ago
DynamoBen wrote:But, a breaker should be ran at no more than 80-85%.

Where did you come up with this? I've been doing electrical work (personal and professional) for a long time and never heard of such a thing. Breakers are actually designed to exceed their rating for a short snap of time. Often times you can run over 15A and still won't get the breaker to trip...not recommended but true.

http://www.planetchristmas.com/FigurePower.htm

When I said no more I meant don't load a breaker at 20A all season. If you are testing it and its high that is fine but I have heard from members that a breaker will wear out alot faster.

Ben


Reply
Posts: 196
(@michael)
Reputable Member
Joined: 20 years ago

Do all of your best guess calculations, setup everything, and then test the true load with an amp meter.
The Kill-a-watt is a cheap and simple plug in meter. I got mine online for under $20. Used it as I was seting up just to make sure each main feeder extension cord and circuit was under the limit. Only used it for about 10 minutes, but it sure feels good to know the actual power draw instead of guessing.

- Michael


Reply
Posts: 2629
(@dynamoben)
Famed Member
Joined: 19 years ago
ben wrote:
http://www.planetchristmas.com/FigurePower.htm

When I said no more I meant don't load a breaker at 20A all season. If you are testing it and its high that is fine but I have heard from members that a breaker will wear out alot faster.

From that article:
"It's good practice to never put more than 80% load on your breakers/fuses... strictly as a safety measure."

Basically they are saying this is a nice thing to do, I wouldn't call this a hard a fast rule. I have run circuits at their max for extended periods of time, it’s not an issue. The breaker is your safety measure as long as you don't exceed its rating you are good to go.


Reply
Posts: 1084
 ben
(@ben)
Noble Member
Joined: 19 years ago
DynamoBen wrote:
http://www.planetchristmas.com/FigurePower.htm

When I said no more I meant don't load a breaker at 20A all season. If you are testing it and its high that is fine but I have heard from members that a breaker will wear out alot faster.

From that article:
"It's good practice to never put more than 80% load on your breakers/fuses... strictly as a safety measure."

Basically they are saying this is a nice thing to do, I wouldn't call this a hard a fast rule. I have run circuits at their max for extended periods of time, it’s not an issue. The breaker is your safety measure as long as you don't exceed its rating you are good to go.

Well, I planned on that 80% margin since I will blow that and it won't be too high.

Ben


Reply
Posts: 2629
(@dynamoben)
Famed Member
Joined: 19 years ago

Fair enough I'm careful about this sort of stuff because we are dealing with electricity. I just want to make sure everyone has the facts.

It’s good to have rules of thumbs to guide folks in execution but I want to make sure there is a distinction between "good habitits" and actual laws/regulations/practices.

Not trying to be the storm cloud and rain on everyones parade. 😉


Reply
Posts: 1084
 ben
(@ben)
Noble Member
Joined: 19 years ago
DynamoBen wrote:Fair enough I'm careful about this sort of stuff because we are dealing with electricity. I just want to make sure everyone has the facts.

It’s good to have rules of thumbs to guide folks in execution but I want to make sure there is a distinction between "good habitits" and actual laws/regulations/practices.

Not trying to be the storm cloud and rain on everyones parade. 😉

yeah. I being 14 cannot afford to burn down a hose or pay for any serious damages. I would rather run one at 80% than push it.

Ben


Reply
Posts: 20
(@wwwgator)
Eminent Member
Joined: 19 years ago

The factor rating is usually set to trip at 80% CONTINUOUS load.
While it's true that you can get more amperage out of a rated breaker, this is called in-rush current, but it is for a brief time only. The manufacturers and UL, have allowed for up to 300% in-rush current to help start heavy loads ( motors, compressors in your fridge, washing machines....).
General rule is 80% continuous- and no more than 10 outlets per breaker.
This is a general "residential" rule with a few exceptions.

Above all, please be safe. If you have any doubt, call a licensed sparky.

Walt G.
Master Electrician/ Commercial Inspector
Evil Genius ( apprentice)


Reply
Trepidati0n
Posts: 256
(@trepidati0n)
Reputable Member
Joined: 19 years ago

The reason for 80% is simple..that is the number in effect where breakers/fuses begin to "time". You can run it higher than 80%, it is just that the amount of time before the breaker trips or fuse blows is not near infinity. Therefore designing for 80% continuous is safe and reasonable. Designing for less just means wasted capacity IMO.


Reply
Posts: 1084
 ben
(@ben)
Noble Member
Joined: 19 years ago
Trepidati0n wrote:The reason for 80% is simple..that is the number in effect where breakers/fuses begin to "time". You can run it higher than 80%, it is just that the amount of time before the breaker trips or fuse blows is not near infinity. Therefore designing for 80% continuous is safe and reasonable. Designing for less just means wasted capacity IMO.

that is why I am setting up a chart that will help me keep me at 80% of my power all the time. Basically during most of my dispay the same # of lighs will be on just different ways.

Ben


Reply