Posts: 2507
(@mrgrumpy)
Famed Member
Joined: 12 years ago
MartinMueller2003 wrote:The shared neutral only handles the imbalance between the phases. So if you draw 10A on circuit 1 and 7A on circuit 2, the nuetral only gets 3A.

This would be true if the circuits were 180 degrees out of phase. Since they are only 120 degrees, your 7/10 example would be closer to 4A but that is nit picking. Yes the breakers would need to be bonded. At that point it would be better to use 220v supplies and not abuse the neutral line. A 220V 360W supply would draw about 1.6A you could put 11 of them on the circuit and not break any codes.

Ah, but now you are dealing with expensive 2 pole GFI breakers like hot tub circuits......but yes, you can have 220 too! (or 230 or 240 what ever your utility provides)


Reply
MartinMueller2003
Posts: 7613
(@martinmueller2003)
Illustrious Member
Joined: 14 years ago

Interesting statement about balanced (180 degree systems)

The U.S. National Electrical Code provides rules for technical power installations.[3] The systems are not to be used for general-purpose lighting or other equipment, and may use special sockets to ensure only approved equipment is connected to the system. Additionally, technical power systems pay special attention to the way the distribution system is grounded.


Reply
MartinMueller2003
Posts: 7613
(@martinmueller2003)
Illustrious Member
Joined: 14 years ago

But how much more expensive is a 220V GFI than two 110V GFI breakers?


Reply
Posts: 2507
(@mrgrumpy)
Famed Member
Joined: 12 years ago
MartinMueller2003 wrote:But how much more expensive is a 220V GFI than two 110V GFI breakers?

I typically use GFIC Receptacles @ $14 without feed thru - I have one installation with 4 GFI Receptacles off one 15A circuit in one box - helps spreads the wet across the 4 receptacles. Single Pole GFIC Breaker $38 and a Two Pole is $76+

So costs could be similar vs you use multiple GFI receptacles.

But if you are doing 220 then you are back to 14/2 with a ground. Maybe still run the 14/3+G so you could also have a 120V outlets


Reply
Posts: 2507
(@mrgrumpy)
Famed Member
Joined: 12 years ago

OK, to analyze, here is a sketch showing the 14/3+G circuit and a SubPanel. Other than the additional breakers (which add nothing) there is no difference.

Disclaimer: I am only giving you food for thought. You must verify with your local code, anything/everything I have discussed prior to using.
(CYA)

143G

Reply