algerdes wrote:Something about all these suggestions is not making sense to me.30 AMP @ 12 volts (output of a power supply) is 3 AMP @ 120 volts.
A typical 15 AMP circuit can handle 5 power supplies on a circuit.
A typical 20 AMP circuit can handle 6 power supplies (with headroom) on a circuit.Note that ALL of these calculations are based on FULL POWER being used by ALL the power supplies at the same time. It has never happened here.
For the past 5 years, I have run 5 power supplies off of a single 15 AMP circuit and have never approached the full 15 AMP load. (We actually run the whole show - 15 power supplies - off of 3 ea. 20 amp circuits.)
holy crap really? I was thinking this all wrong, lol
I was having outlets added based on me doing a current draw test and seeing that my tree with 2 12v/360W power supply was drawing around 5 amps per output so a total of 80 amps at full white on (which rarely happens) but really from the 20 amp breaker outlet standpoint thats only drawing around 8 amps total? So i can get 3 trees (6 12v power supplies) on 1 20amp on a normal show?
The shared neutral only handles the imbalance between the phases. So if you draw 10A on circuit 1 and 7A on circuit 2, the nuetral only gets 3A.
This would be true if the circuits were 180 degrees out of phase. Since they are only 120 degrees, your 7/10 example would be closer to 4A but that is nit picking. Yes the breakers would need to be bonded. At that point it would be better to use 220v supplies and not abuse the neutral line. A 220V 360W supply would draw about 1.6A you could put 11 of them on the circuit and not break any codes.
Emuney18 wrote:I am in this same boat right now and will be hiring an electrician but I want to know what is going on. So if he adds twin 15A that also means 2 outlet boxes correct? Or with your shared ground scheme can you have 2 circuits in one box?
Not sure what code would say having receptacles in the same box....should be ok since it is nothing more than a smaller amp dryer outlet circuit. You could even wire 240V here too.
MartinMueller2003 wrote:This would be true if the circuits were 180 degrees out of phase. Since they are only 120 degrees, your 7/10 example would be closer to 4A
Isn't most RESIDENTIAL power delivered as split-phase which *is* 180-degrees apart? (comes from a center-tap "pole pig").
*If* the building is fed with 3-phase power, then I would agree with your statement about 120 degrees. But for most of us here, I suspect that the original scenario (split-phase @ 180 degrees) holds true.
In my town, two separate circuits (not sharing neutrals) in the same box IS allowed. They are NOT allowed to share the neutrals and it does not matter which phases they are on. Much simpler to just use 220v/240v since most of the power supplies we use have a neat little switch on the side to work at that voltage.