adding electrical circuits / outlets - looking for pointers

85 Posts
21 Users
0 Reactions
30.9 K Views
Posts: 3735
(@algerdes)
Famed Member
Joined: 15 years ago

Something about all these suggestions is not making sense to me.

30 AMP @ 12 volts (output of a power supply) is 3 AMP @ 120 volts.
A typical 15 AMP circuit can handle 5 power supplies on a circuit.
A typical 20 AMP circuit can handle 6 power supplies (with headroom) on a circuit.

Note that ALL of these calculations are based on FULL POWER being used by ALL the power supplies at the same time. It has never happened here.

For the past 5 years, I have run 5 power supplies off of a single 15 AMP circuit and have never approached the full 15 AMP load. (We actually run the whole show - 15 power supplies - off of 3 ea. 20 amp circuits.)


Reply
MartinMueller2003
Posts: 7613
(@martinmueller2003)
Illustrious Member
Joined: 14 years ago

14/3+G (at similar cost) you get 30A

Not sure I agree with that statement. You are then trying to push the entire 30A through the single 15A return line. That will overheat the neutral wire. Even if you put the hot lines on two different phases, you would still be trying to run 30A through the individual wires (kirkoffs law https://www.google.com/search?q=kirchoff%27s+law+current&rlz=1C1CHBF_enUS699US699&oq=kirkoffs&aqs=chrome.5.69i57j0l5.4090j0j7&sourceid=chrome&ie=UTF-8 is pretty hard to get around).


Reply
JasonPortwood
Posts: 753
Topic starter
(@jasonportwood)
Noble Member
Joined: 17 years ago
mrGrumpy wrote:That is 90 degree C, or 194 F.....You are good with that 90

Dang it, I forgot it's C....

From Futurama....
Moon Farmer: Yep, drops down to minus-173.
Fry: Celsius or Fahrenheit?
Moon Farmer: First one, then the other.


Reply
Posts: 114
(@dmpeaceman)
Estimable Member
Joined: 16 years ago
MartinMueller2003 wrote:14/3+G (at similar cost) you get 30A

Not sure I agree with that statement. You are then trying to push the entire 30A through the single 15A return line. That will overheat the neutral wire. Even if you put the hot lines on two different phases, you would still be trying to run 30A through the individual wires (kirkoffs law https://www.google.com/search?q=kirchoff%27s+law+current&rlz=1C1CHBF_enUS699US699&oq=kirkoffs&aqs=chrome.5.69i57j0l5.4090j0j7&sourceid=chrome&ie=UTF-8 is pretty hard to get around).

This was my original thought as well, was thinking that 30A could potentially run through the neutral - but I did some research, and it looks like mrGrumpy right. There's some voodoo I don't quite understand going on with the split breaker that balances the load appropriately through the 2 hot wires.


Reply
MartinMueller2003
Posts: 7613
(@martinmueller2003)
Illustrious Member
Joined: 14 years ago

Only if they are on different phases. If both hots are on the same phase then the common neutral will be overloaded.


Reply