adding electrical circuits / outlets - looking for pointers

85 Posts
21 Users
0 Reactions
30.9 K Views
beeiilll
Posts: 869
(@beeiilll)
Prominent Member
Joined: 19 years ago
mrGrumpy wrote:
NEC 201.4(B) allows

More reading http://mjobee.com/projects&news/nec%20art%20210.4.pdf
Look at exhibit 210.1

Speedometers can go up to 200 MPH but that doesn't mean you should do it!

I didn't mention also that Arc Fault circuits require 3 conductors with ground as well so that is another use for 14/3 in many rooms if you are running 15 amp circuits.

The NEC, UL, and other local codes are the baseline guidelines for electrical installations and can vary from local to local (and do here in NY). The inspectors for electrical here will not allow the example of branch circuit wiring that you show from 201.4(B) here in NY. Also, Arc Fault breakers will not work with it either which is why they don't allow it here.

I am not "Mr.Perfect" as you say, but I do take electrical work very seriously as I have seen the results of poor workmanship along with what happens when someone says "Oh, this will work "Okay" for what you need".
People are free to do whatever they want but that not always makes it right or the best way. Sorry that you feel that yours is the only way in this case but the risk is no way worth it IMO.

And with that, I end my responses to this thread.


Reply
Posts: 2507
(@mrgrumpy)
Famed Member
Joined: 12 years ago
JasonPortwood wrote:I'll hopefully be able to post more pictures tonight - busy evening. I'll get one pic by the panel where I'd put the circuits inside the garage. Also a couple more for the possible inside / outside location.

- - - - - - - - - - -
When I start this I'll flip those range breakers out for a 50/2 breaker. When I took the picture I thought it was odd it wasn't that way. Thank you!

First.....sorry you buried you in other topics.......

I not a fan of tie bars, but they are widely used so maybe the Breaker Tie is the right solution for you on your range breaker. Likely that was there and fell off. (Fell off - why I do not like or use on my projects)

One more thing. Typically I would not load 2 higher amp breakers across from each other. When you're doing other work, consider moving the Furnace Breaker above the Dryer Breaker. I think the original installer considered grouping the Furnace and Air more than load balancing. Not a big issue, actually not an issue...just best practice. Remember to change the markings too.


Reply
rayhjr
Posts: 972
(@rayhjr)
Noble Member
Joined: 12 years ago

I just spent the last whatever time reading this thread and wow. Did not know that sharing a Neutral was not common Practice. I have not done a lot of residential and could not quote local code at all, BUT, I have been sharing Neutrals for a long time. I have been on several Commercial jobs with all 3-phase sub panels and all Receptacle circuits were 3 circuits sharing 1 neutral. I have also done this in single phase panels with 2 circuits. As long as they are different phases. I personally have have 2 GFCI recp sharing 1 neutral. A 4-wire direct burial cable running from my panel (1 ground, 1 neutral, and 2 hots from 2 different breakers) going under my house's crawl space and up to the first GFCI Recp. You MUST pigtail the Neutral to the first GFCI Recp. and then take it to the next GFCI Recp. First hot goes the first Recp. then 3 wire to next recp.(Hot,neutral, Ground) If you put the Neutral on the first GFCI Recp. and then even come off the same screw to next Recp. it wil not work, Must be pigtailed before recp. as indicated in post #3.
That being said, get local advice if you plan on doing it yourself. Location of recp. should be determined by where you need the power. Going to a j-Box then out to recp. or installing a sub panel would be up to you and your need/budget. I like to install conduit (PVC) and pull single conductors (Stranded over solid). That way I have more options in the future, and you could pull a neutral for each circuit and not have to deal with most of this tread or even most of my reply!:ohwell:
Good luck, and feel free to ask any questions you may have in the future.


Reply
Posts: 30
(@inspector-steve)
Eminent Member
Joined: 15 years ago

I also just read through this and my name is what I do for a living. (currently enforce the 2014 National Electrical Code). I am going to sleep just fine at night knowing I approved thousands and thousands of shared neutral circuits. Completely acceptable by my work bible for years and years. Here in the State of Ohio the NEC is adopted state wide and must be enforce as is.

Steve


Reply
MartinMueller2003
Posts: 7613
(@martinmueller2003)
Illustrious Member
Joined: 14 years ago

I spoke to an electrician here in my area of MA and was told it is not allowed. So the answer must be: Check your local codes.