Posts: 499
(@frederic)
Honorable Member
Joined: 14 years ago

At one point I started digging up my lawn to bury conduit 2' down, for the purpose of putting outlets all over my lawn for christmas lights. I intended to backhaul all of that to a sub panel that wouldn't be powered except during the holiday season.

I stopped that process about 1/5th of the way through because I realized, no matter where I choose to put the outlets now, I am probably going to re-arrange my display every year or two anyway so no matter what I do, I'm going to have extension cords all over the place at some point.

See, one of the lazy ways of making last year's display new again is to re-arrange the elements on the lawn. This year, arches go on the left, next year, arches go on the right, that kind of thing.

So a couple of years ago, I succumbed to extension cords on the lawn and just accepted it. But I did something cool (I think anyway).

On the front of my house is a 50A outlet in an outdoor box. Next to it is a bracket that I temporarily hang a 20-breaker, 40-circuit outdoor circuit panel on during the holiday season. Out all 20 of the bottom knockouts, are weather-resistant gland nuts with 15A capable molded wire and female 120V sockets on the end, those coming from 3' 15A outdoor extension cords I bought and simply cut the plugs off. Each extension cord section goes to it's own 15A breaker and they're numbered 1-20 to match the breaker. The extension cords I cut up have illuminated female sockets so it's very, very easy to troubleshoot power issues. If socket 4 isn't illuminated, I know breaker 4 tripped. If none of them are illuminated, I know the problem is further back (as in I forgot to turn on the 50A inside).

I do not use GFI outlets anymore. Instead, all of the breakers in that temporary, outdoor panel are GFI. I was confused for a while by how to ground and bond the temporary panel and I did so to this diagram:

OSkAm

So my 50A outlet and the plug/wire that goes to the temporary panel, has four conductors. Once I got this correct, I had no issues with GFI breakers tripping. It took a while because my electrical knowledge was a bit rusty.

The wire I used between the temporary panel and the outlet is only 3' in my case, but there's nothing wrong with making it longer within reason. You could put the panel in the center of the lawn on a wood post or stake and distribute from there. I chose to avoid the risk of it falling over and having to dig a post hole every year by hanging on the aforementioned bracket on the house and drawing the extension cords towards the house. For a while I debated putting the 50A outlet at the front of my lawn (in the garden area) and having extension cords coming from there but in my mind, drawing power from closer to the street and back across the lawn is pretty much the same as drawing power from the house forward on the lawn, except the 50A would be shorter with it on the house. That eliminated digging more trenches through clay filled with rocks.

Having individual breakers outside is very, very convenient. To work on stuff on circuit 5, I just flip the breaker and I'm safe. I have visual confirmation I flipped the right one because of the illuminated plugs being labeled and dangling in order of the breakers.

And to think many, many years ago I used to do static lights by daisy-chaining indoor power strips with long extension cords I bought in bulk at a dollar store.

Hope that helps.


Reply
Posts: 128
(@emuney18)
Estimable Member
Joined: 11 years ago

So the NEC codes are state dependent? I would have never guessed that. I can understand building codes that vary by state since all kind of factors can play a role but electricity is based on physical laws that do not change. Interesting.
In my case I am just going to run 2 wires and call it a day. Everything will be in the garage wall that shares the wall with the main panel and outside outlet that will be added or ran through the garage attic. As a best practice when I staple the wire to the garage ceiling supports in the attic should I follow a single board since they run the direction I want to go or should it have a small angle and span multiple bays?

Sent from my iPhone using Tapatalk


Reply
Posts: 2507
(@mrgrumpy)
Famed Member
Joined: 12 years ago
frederic wrote:At one point I started digging .................................

So my 50A outlet and the plug/wire that goes to the temporary panel, has four conductors. Once I got this correct, I had no issues with GFI breakers tripping. It took a while because my electrical knowledge was a bit rusty.

FYI: Your sub panel is correct as wired, but I suggest you include the term "Isolated Neutral (Non Bonding)"


Reply
Posts: 2507
(@mrgrumpy)
Famed Member
Joined: 12 years ago
Emuney18 wrote:So the NEC codes are state dependent? ...........................

Food for thought;

In California, Local jurisdiction governs where and how the code is applied. Typically its the City, then County, but when it comes to small towns, the Professional Electrical Engineer is the designer and inspector and Governing Body, they applies NEC. (I imagine there are also grouping of cities in rural areas - like "Gold Country" could exist. For very rural, I assume the contractor is the governing body.)

In my experience with all 50 states, I have yet to find any state applying the current code. The code book typically comes out every 3 years....again California....I suspect they are still working with 2011 code, and just starting to implement 2014. It would be too early for any part of 2017 to apply, unless the industry already implemented prior to 2017 being issued.


Reply
Posts: 274
(@akareaper)
Reputable Member
Joined: 10 years ago

Wow is right. Man, here we are in a community of Christmas light fanatics, but bordering on WWF or MMA fights. As you can see, many different opinions. I had the master electrician at work come over. People here will say we did it wrong. However, it meets code, and its simple. We ran (3) 20 amp circuits to (3) separate GFCI outlets in my crawl, then to (3) separate dual gang weatherproof boxes outside. Gives me 12 places to plug in. Technically 7,200 watts peak, or rather 5,760 usable watts. Well over 10,000 nodes worth of power I'll most likely never reach. I have two additional outside plugs as well, so any crazy expansion is compensated for. Materials, two cases of beer, and an invite to the shows debut is all it cost me. Talk to some local guys, look on craigslist, tell them what you are doing, you'd be surprised how cheap it can be as guys want easy side jobs, etc. Remember, everyone here is an enthusiast, and takes pride in their set ups. They defend them to the teeth, so take it all in, go with your gut.


Reply