Can someone confirm this power plan (attached image) for my WS2812B pixel strips? I have 50 Meters I am putting up and am planning to run no more than 150 before inserting power with 14g 2 conductor returning home. Power cable runs not exceeding 35-40 feet.
A few things I wouldn't mind being confirmed
- Is it "correct" to just loop the data line
- I believe I tie the V- (negative) of the two power supplies together?
- Two power supplies of different specs are ok if they are not tied together on the positive side?
- Will I need resistors on the data line? I've read that I may need them at the beginning and end of a transmission line. I will probably try without to start as I only have about 20 feet to the first string and most strings will be no more than 10 feet from the last one.
- Are there any issues with powering the strings from the far end if it makes more sense?
Just want to get this right before I go and put it all up... Thanks in advance!
First off, I think your power lines 14awg is far to small for a 35ft run. Assuming full white, specs mention 50ma/pixel (on white) and you have 1500 pixels = 75A. If you evenly distribute this across all 4 injection points =18.75A. Voltage drop at this current with 14awg at 35ft is 3.31V, so if you're injecting 5.5V you'll get 2.19V which is obviously way to low. I believe the consumption is overspec'ed, more realistic is 40ma but this only reduces your voltage drop by 20%. Can you locate one power supply closer? This is the big issue with 5V pixels. I ended up running 10awg just for a 15ft run up my megatree to keep my voltage drop less than 0.5V. If you don't have larger gauge wire, you can run parallel wire. Rule of thumb is to half the voltage drop (halfing the resistance) you drop by 2awg which is a pair of the same gauge wire. 2x14awg = 12awg or 4x14awg=10awg. 10awg at 18.75A the Vdrop is 1.31V. If you feed 5.5V voltage at injection = 4.19 which is fine for the first maybe 20 pixels but then you accumulate resistance as you move down the strip and Vdrop increases.
- Is it "correct" to just loop the data line, Unsure I understand the question. Yes, you Daisy chain all the data signals. If you're making a matrix you can flip the strips to minimize this connection and correct for this in the controller.
- I believe I tie the V- (negative) of the two power supplies together? Yes, if they are close, otherwise they will be grounded by default through the strips
- Two power supplies of different specs are ok if they are not tied together on the positive side? Yes, keep the voltages as close as possible
- Will I need resistors on the data line? I've read that I may need them at the beginning and end of a transmission line. I will probably try without to start as I only have about 20 feet to the first string and most strings will be no more than 10 feet from the last one. I've never had to use any resistors but I'm using different controllers for my WS2811 pixels (J1Sys)
- Are there any issues with powering the strings from the far end if it makes more sense? Relocate the second power supply
For that long of a distance and that many pixels you may want to consider 12v or 24v supplies and DC-DC converters. There are many advantages doing it this way but I won't go into all that since that wasn't part of your questions. (There is a paper about all that if you want to read it).
If you do not want to go that route, Pagrossa has good points..If you are doing a matrix you may want to consider putting your power supplies right at the matrix and keep the wires short as practical. I would also add consider your fusing needs once you figure out the exact wiring you are going to use. Be safe.
As well, you didn't mention whether you are using 30 or 60 LEDs/M strips. Assuming 30 LEDs/M you will start to get color shift on white after about 1.5 meters. At the end of 5 meters your white will be warm white instead of cool white. If you are able, inject power at both ends, that will help immensely and may be good enough for your purposes.. but if you are putting up a matrix consider that LED video walls have "binned" LEDs. Meaning every LED in the bin has a color temp range that falls within a certain spec for that bin, (unlike the strips we use from China). They do that so when powered the same, they look the same. When you put them in a cluster like that, you can really tell the color temp differences when you start using whites and yellow.. Another discussion for sure..
I am not sure about your controller but 1500 pixels in a single line seems a bit high to me. There may be data rate transfer issues with that with the WS2812 chips and maybe even your controller.. don't know.. have never used one of those and I have never gone over 170 pixels in a single data string, though I know some are saying 1024.. not sure if that is pixels or channels.
Sorry, this is eaves / house outlines (not a matrix) and they are 30 leds per meter.
Yes I should have indicated in the drawing that I an powering each 150 leds (5m) string with it's own 14AWG run back to home. In testing I didn't notice any issues but only ever powered up two strips. surprisingly I didn't even insert power between them and didn't really notice any major issues. Only a few times I lost the last pixels and full white was falling off half way through the second strip as I would expect. Mind you all of this testing was indoors at night and up close. Strips are going outside over the next few days so I can get a full test then.
You mention inserting power at both ends. Is this OK? ie Is this what you mean? (see image).
Thanks again! Dave
Actually you are better off injecting at 2/3s the distance of the strip from the starting power point since power can go both down to the end of the strip and back toward the starting power point.
For example on a 150pixel strip the start power point would be at pixel 1 then you inject at 100. The injection would carry 2/3 of the load and basically power pixels 50-150.
Krusty wrote:Sorry, this is eaves / house outlines (not a matrix) and they are 30 leds per meter.Yes I should have indicated in the drawing that I an powering each 150 leds (5m) string with it's own 14AWG run back to home. In testing I didn't notice any issues but only ever powered up two strips. surprisingly I didn't even insert power between them and didn't really notice any major issues. Only a few times I lost the last pixels and full white was falling off half way through the second strip as I would expect. Mind you all of this testing was indoors at night and up close. Strips are going outside over the next few days so I can get a full test then.
You mention inserting power at both ends. Is this OK? ie Is this what you mean? (see image).
Thanks again! Dave
Yes, what you have drawn here would be very beneficial. Inject at every end. Pagrosse is right about injecting at 2/3 but that is not really practical for people using full waterproof strips. If you are ok how it looks in your house powering the strips from one end... then when you take them outside I suggest you do as your drawing shows. Inject at every end. Also, the closer you get the supplies to the pixels the better. If you can mount them somewhere near the center of the runs that is the best.