I am in the process of building some boxes to power some window matrix's. I have 4 meanwell LRS-350-12 psu's and 4 hanson power8 power distribution boards per box. I was planning to install inline fuses between the psu and the power distro board (red wires in the picture below). I have read some conflicting info on here about this. Some say it is needed. Some say the meanwell's dont need an external fuse, they have an interal one. And since i would be powering everything (pixels and controller) from the power distro boards, which all the outputs will be fused, do i really need an inline fuse between the psu & power dist board?
Second question is regarding the psu's. Is it recommended to install a ground wire at the 120v ground terminals that would tie all of the psu's together, giving them all the same reference to ground? All of these 120v circuits are being fed from a dedicated 100a sub panel in my garage if that makes a difference.
Thanks for the help,
Tim
The PSUs should be using three wire feeds to the mains. You do not need to tie an additional ground between them.
Yes, i am using 3 wire 120v power cords. Hot, neutral & ground wire.
No, don't need to fuse between power supply and fused distribution board.
No, don't need extra 120vac ground wire.
You dont need extra ground wire between PSUs when you are using a three wire connection to the mains.
As for a fuse between the PSU and the and the fuse distro board, it depends on how far the PSU is from the distro board. 10cm? I would not. 1m? Yes. A fuse exists to protect the wire between a current source (PSU in this case) and a current sink (Distro Board). Unless the aggregate of all of the fuses on all of the distro boards add up to less than the capacity of the wire between the current source and sink, you will need some sort of protection between source and sink. You state that your current source has a built in fuse, that is fine as long as the WIRE between the source and sink can handle the total load of that fuse. In your case, that would be wire with a carrying capacity of 30A. Every wire between the PSU and the distro boards must be able to handle 30A. I use three wires between the PSU and three distro boards. Each wire can carry 14A and is fused at 10A. If I did not have the 10A fuse at the PSU and one of my wires became shorted, the wire would go up in flames as the PSU goes into and out of a fault state (found this out the spectacular way). The Meanwells have a great ability to shut the load down on a dead short but as the wire degrades the PSU just things it is in a high current state and pumps out max power.