both my e682s do it , not the e681.5's. both E682 are on 4.033. others are on lower versions.


Reply
Posts: 29
Topic starter
(@diszip)
Eminent Member
Joined: 16 years ago
EE351 wrote:I'm going to start sounding like a broken record (already posted this):

Here's how I power on my GECE pixels:

1. Turn on power to the controller first. Make sure power to the pixels are off and no data is being sent from sequencer.
2. Turn on power to the pixels.
3. Start a sequence.

I was running into similar startup problems (for the last 3 years) and the procedure above works for me every time (I've been doing it this way thru testing and setup for this year). I suspect that if the gece pixels are powered first, and then the controller is turned on, there might be some noise on the output pins of the controller during initial startup that is causing the pixels to enumerate incorrectly.

I remember reading that the E68X controllers output data to the pixels regardless if there is any incoming data (presumably all zeroes), maybe this is the problem? Even if zeroes are sent, there will still be high/low transitions on the pixel data line.

FYI, I'm using a custom controller that I designed that only outputs to the pixels when there is incoming data. Otherwise the output is held low (o volts).

So basically the opposite power up sequence than I was trying. I thought that the controller is outputting data to the pixels all the time, even with no sequence running, and as the GECE's are self addressing, wouldn't this cause the pixels to be addressed with a random starting pixel? While the "stuck on" pixel problem would go away, if you need the pixels to be addressed in a certain order (which I do for the matrix), this would not work.

Or am I not understanding either how the E682 is outputting all the time, or the self-addressing of the GECE's.

Do you sell your custom controller and does it support E1.31?


Reply
Posts: 555
(@zaker)
Honorable Member
Joined: 19 years ago

Just swapped controllers, my E862 has stuck pixels on a different test set, quick check on my upgraded e861, no stuck pixels. Both are running 4.033


Reply
Posts: 313
(@ee351)
Reputable Member
Joined: 13 years ago
diszip wrote:So basically the opposite power up sequence than I was trying. I thought that the controller is outputting data to the pixels all the time, even with no sequence running, and as the GECE's are self addressing, wouldn't this cause the pixels to be addressed with a random starting pixel? While the "stuck on" pixel problem would go away, if you need the pixels to be addressed in a certain order (which I do for the matrix), this would not work.

Or am I not understanding either how the E682 is outputting all the time, or the self-addressing of the GECE's.

Do you sell your custom controller and does it support E1.31?

My controller does support E1.31, more details here:

http://doityourselfchristmas.com/forums/showthread.php?32352-Another-pixel-controller

http://forums.parallax.com/showthread.php/157645-GE-color-effects-assembly-driver?p=1303479


Reply
Posts: 1249
(@jstjohnz)
Noble Member
Joined: 17 years ago

I have not been able to duplicate this problem. I have a firmware to try. This is only for E682s. This *may* help. Feedback appreciated.


Reply
jchuchla
Posts: 8698
(@jchuchla)
Illustrious Member
Joined: 15 years ago

The GECEs should be definitely on and ready for data before the controller. If you have the controller on first, it is not aware of when the pixels become ready and they'll start get initialized with whatever first data packet they receive. So you could end up with the pixel addresses rotated.
GECE pixels take a fairly long time to reset. I've observed that they hold their address for over 30 seconds after power off. So if you're power cycling them to reset them, you should make sure they get a good 40 seconds of off time before powering them back on. Im hesitant to suggest this openly, but... A brief shunt from pixel power to pixel ground will usually bleed them off very quickly and they can be restarted much quicker. This is only to be done when the power supply is off and you can no longer see the power light fading out. I think this is a power supply thing and not a pixel thing. I think (never measured) with the big switching power supplies we often use for these that there's enough voltage bleed for long enough that it keeps the GECEs powered just enough for quite some time for them to retain their addresses so long.
So, power on pixels, there must be no data nor noise that looks like data. Then power on controller. It should take a few seconds for the controller to boot and send data. And then when it's ready it will start sending data starting at address 1 and going to however many you have set up in software. It doesn't actually do anything special to address them, the first frame of data starting at 1 is sufficient to enumerate them properly. The 68x series will constantly send a round robin of the data bits for every pixel over and over, regardless of whether or not there's incoming data, or if that data is changing.

--Jon Chuchla--

Sent from my iPhone using Tapatalk


Reply
Posts: 555
(@zaker)
Honorable Member
Joined: 19 years ago

Did some testing, v4.033 almost 7:1 I got a stuck pixel on power up, first one. Different colors, waited in between cycles, put a resistor between power supply leads to bleed caps.

Put new firmware on, new behavior. Stuck pixel isn't always stuck on one color ( has always been first one) now changes color, but not correct, as if it has wrong address.


Reply
Posts: 9
(@boostin4hp)
Active Member
Joined: 15 years ago

I just built a new e862 and also have stuck pixels on startup.


Reply
Posts: 1168
(@keith-r)
Noble Member
Joined: 19 years ago
jchuchla wrote:The GECEs should be definitely on and ready for data before the controller. If you have the controller on first, it is not aware of when the pixels become ready and they'll start get initialized with whatever first data packet they receive. So you could end up with the pixel addresses rotated.
GECE pixels take a fairly long time to reset. I've observed that they hold their address for over 30 seconds after power off. So if you're power cycling them to reset them, you should make sure they get a good 40 seconds of off time before powering them back on. Im hesitant to suggest this openly, but... A brief shunt from pixel power to pixel ground will usually bleed them off very quickly and they can be restarted much quicker. This is only to be done when the power supply is off and you can no longer see the power light fading out. I think this is a power supply thing and not a pixel thing. I think (never measured) with the big switching power supplies we often use for these that there's enough voltage bleed for long enough that it keeps the GECEs powered just enough for quite some time for them to retain their addresses so long.
So, power on pixels, there must be no data nor noise that looks like data. Then power on controller. It should take a few seconds for the controller to boot and send data. And then when it's ready it will start sending data starting at address 1 and going to however many you have set up in software. It doesn't actually do anything special to address them, the first frame of data starting at 1 is sufficient to enumerate them properly. The 68x series will constantly send a round robin of the data bits for every pixel over and over, regardless of whether or not there's incoming data, or if that data is changing.

+1
I am running 4.026 and never had an issue. Always power the GECE's on first.


Reply
Posts: 99
(@sulrich)
Estimable Member
Joined: 13 years ago

GECE similar issues caused me just to remove my 40' long MEGA-ARCH over my driveway. Now i have a spare E6804 and will do testing, the MEGA-ARCH may be resurected soon if i canfind the bug. Hats off the the SANDEVICES.COM controllers.. I do like the interface and ease of troubleshooting. Besides the ease of assembly.

Best of luck!
Sulrich


Reply