Ok so I have an alphapix16 both banks running on the same PSU. My question is I have 2 props near each other and I want to use an 18awg 5 core wire. One prop is on back A and the other is on bank B. Can they share the same ground wire? Data and power both from the separate banks just shared ground.


2 Replies
Posts: 740
(@ezellner)
Prominent Member
Joined: 11 years ago

The ground wire needs to be able to carry the sum of the currents in the two power leads.


Reply
Posts: 67
Topic starter
(@mitoga)
Trusted Member
Joined: 10 years ago

Cool thanks makes logical sense