My control system uses a RS422 multidrop data bus for Vixen communication as well as the zero cross signal. All controllers are connected with CAT5. I am seeing some interesting issues. I have 7 control boxed (16 channels each) connected to the bus, and the 5th, 6th, and 7th box seem to "pick up" a zero cross signal even when i am not generating one on the zero cross data bus (unplug zero cross detection circuit). If I have vixen running and transmitting data, that data is somehow generating a ZC signal. Vixen talks on pins 1, 2 and the ZC is on pins 3, 4, 12v on 5, 6 and gnd on 7, 8 of the RJ45 connectors. Anyone have any idea why the data might be causing a ZC to be generated? Attached is a block diagram of the data and ZC control signals, and the black line is where the ZC signal gets all messed up. Good thing this bizarre behavior does not really mess up the show!


5 Replies
David_AVD
Posts: 991
(@david-avd)
Noble Member
Joined: 17 years ago

A couple of questions:

Are the data inputs on the controllers electrically isolated?

Are all of the controllers fed from the same power point?

I'm thinking that you may be having an issue with the common mode voltage being exceeded on the controller's data inputs.


Reply
Posts: 6728
(@p-short)
Illustrious Member
Joined: 20 years ago

I'm not sure what the issue is, but the pinout selection is not the best for normal CAT5. With a CAT5 cable assembled in the standard fashion you will find that one twisted pair is on pins 3&6, another on 4&5. You should have put the serial signals on one twisted pair (either 4&5 or 3&6), and the ZC signal on another twisted pair with a ground (again, either 3&6 or 4&5).


Reply
David_AVD
Posts: 991
(@david-avd)
Noble Member
Joined: 17 years ago

Good catch! I never even noticed that he wasn't using actual pairs!


Reply
Posts: 138
Topic starter
(@chris2879)
Reputable Member
Joined: 19 years ago
David_AVD wrote:A couple of questions:

Are the data inputs on the controllers electrically isolated?

Are all of the controllers fed from the same power point?

I'm thinking that you may be having an issue with the common mode voltage being exceeded on the controller's data inputs.

I am not sure the definition of electrically isolated, so I can't answer that question. Yes, all the controllers are fed from the PC power supply, and all use the ground on the power supply of the PC. There is about 150' of cable, so there might be a voltage drop due to the impedance of the cable, might that be causing some issues.

I should also add that i am powering the RS422 drivers with 12v,so the differential voltage should be pretty drastic to get the correct logic state regardless of the voltage drop over the cable length.

I should have specified that i am not using a "normal" cat5 wiring. I am using pin 1 orange, pin 2 orange/white, pin 3 brown, pin 4 brown/white, pin 5/6 12v grn, blu, pin 7, 8 grn/wht, blu/wht. Good observation Phil!

Thanks for the responses!


Reply
Posts: 138
Topic starter
(@chris2879)
Reputable Member
Joined: 19 years ago

Well i figured out the problem after taking the oscilloscope on the front yard to do some measurements. The control cable that contains the A/B 422 pair for the ZC signal had a bad connection on the B line. Replaced cable, and system functioned normally.


Reply