I know this has probably been answered, but instead of searching through hundreds of threads, I am going to just ask. I need help in connecting incandescent C9's on a roof because I am not comfortable with the power issue. My ex-husband has been installing lights for years (who I learned from) and he did things such as cutting off the end with the fuse and wiring together the strands. My question is this. If you can only attach 3 strands end to end, do I need to cut off the end with the fuse? Can I connect 4 strands if I cut off the fuse end? If I connect 3 strands on the left side of a house, 3 strands on the right side of a house, can i connect those to a 3 way on the roof plugged into an extension chord and run to 1 outlet? Can multiple sets of 3 be plugged in the same outlet or do they need to be split up. I have tried researching this online and the extensive math makes my head hurt. Sorry for so many questions, I just need some directing! I was trying to go solid LED this year, but it seems most can't afford it, hence I wouldn't be running into this issue. I do understand how to connect the strands with lamp chord on the roof but as far as how much I can connect to an outlet, I am at a loss. Thank ya'll!


4 Replies
Posts: 91
(@bigpav)
Estimable Member
Joined: 17 years ago

I used to line my yard with C9 incads. What I found to work for me was taking the fuse out and wrapping it in tin foil and put the fuse back in. I had 10 sets of 25 on each side. To plug them in I would limit it to 5 per socket. Man back when I was all incad in would usually take me a week to figure where to plug everything in without tripping the breaker. However, from past experience you should be fine with plugging all 6 together just wrap the fuses first because you don't want to climb the roof to replace a fuse. Hope this helps.


Reply
Braveit1
Posts: 577
(@braveit1)
Honorable Member
Joined: 19 years ago

Ouch! The fuses are there for a reason. Bypassing them isn't a great ideal if you don't know any better. They are there so you don't exceed the rated amperage of the wire, not just the circuit breaker. Plugging in more lights on a wire that was only designed to carry a small load could cause a fire.


Reply
Posts: 91
(@rednelb)
Estimable Member
Joined: 13 years ago

yeah, don't wrap the fuses.
Although most c9 strings can handle more than the rating of the fuse, i wouldn't push it.

For convenience I will cut off the first plug on any of my strings and splice it back in at the controller. If a fuse blows, I can get to it.

Again, please don't use foil.


Reply
Macrosill
Posts: 9739
(@macrosill)
Member
Joined: 20 years ago

Please do not bypass any fuses. They are there for a reason and they may save your house and possibly your or others lives under certain circumstances.

Now, you can plug 3 sets of lights end to end. You can cut the plugs off and hard wire them together as long as the first set has the fuses in the 1st plug. We will call these 3 sets plugges end to end Group 1. You can have multiple groups plgged into the same outlet or extension cord or triple tap adapter jut keep in mind the current rating of the circuit and extension cords.

If you have 6 sets of lights on the roof you could bring up one extension cord and a triple tap adapter and 2 groups of 3 sets of lights. Each Group plugs directly into the triple tap adapter from the center of the roof outward.

Or you could run a cord up the left side with 1 group of 3 sets and another cord up the right side with a second group of 3 sets.

Whatever you do make sure you have a set of fuses of the proper rating to protect the christmas light sets and your house!