Renard16 Problem
 
Notifications
Clear all

Renard16 Problem

9 Posts
7 Users
0 Reactions
2,624 Views
Posts: 7
Topic starter
(@andrewshumate)
Active Member
Joined: 18 years ago
[#5508]

Hello,

I have two renard16 boards daisy chained together. I set my plugin to renard 1-32. Sometimes board two will stop functioning. Misc lights will stay on through the whole sequence and will not reset. Board 1 operates fine through the whole sequence. I switched board 1 and board 2 and the same problem reoccurs expect to the opposite board (originally board1). I believe that should rule out a hardware problem. I also spoke to my buddy with the same setup. He has also been experienced the same problem. Would appreciate any suggestions to a fix!

Thanks,
Drew


8 Replies
rstehle
Posts: 4348
(@rstehle)
Illustrious Member
Joined: 19 years ago

How are you powering your boards? You might check the voltage on board #2 (at TP2 & TP1). Should be somewhere near 12 vdc.


Reply
Posts: 7
Topic starter
(@andrewshumate)
Active Member
Joined: 18 years ago

Voltage is ok. The 5V regulator is spitting out a constant 5Vdc on the board.


Reply
XmasInGalt
Posts: 526
(@xmasingalt)
Honorable Member
Joined: 19 years ago

How long is the cable between Ren #1 & Ren #2? You might have a cable problem. If the cable is long, see if the problem still exists with less cable. On the Ren16s I have, the longest cable distance between two Ren16s is about 30 ft.


Reply
rstehle
Posts: 4348
(@rstehle)
Illustrious Member
Joined: 19 years ago

I would also suggest checking the cable to the 2nd Ren. I don't think distance is a problem. I have a couple that have 50 to 60 feet between them and they run fine.


Reply
WWNF911
Posts: 1722
(@wwnf911)
Noble Member
Joined: 19 years ago
rstehle wrote:I would also suggest checking the cable to the 2nd Ren. I don't think distance is a problem. I have a couple that have 50 to 60 feet between them and they run fine.

Good call Randy. Out of all, I think the most problems I've had this year had to do with intermittent, bad cat5/ cable crimp problems.

Leon


Reply
Posts: 6720
(@p-short)
Illustrious Member
Joined: 20 years ago

You should be able to run the inter-board connection out to several thousand feet so long as you are just running ground and data through the cable. This assumes that the cable is made with the proper wires paired up. It would be another matter altogether if you are trying to run power through the cable.


Reply
Posts: 7
(@obliterous)
Active Member
Joined: 19 years ago

The other thing to check, is to make sure that the second board isn't running hot. High loads (over 2 amps) on a triac can cause then to get VERY hot and stall them in a conducting state. If they're hot when they stall, add heatsinks.

(Okay, brain fart, are the ren16's using scr's or triacs? I cant remember. Either way, check for heat)


Reply
Posts: 188
(@johnbyrne)
Estimable Member
Joined: 19 years ago

Distance isn't a problem unless it is between the computer and the first board and you are not converting to RS485. I have two 150 foot runs in my display (didn't think that one through lol) and have no problems. RS485 can run thousands of feet according to the net tech sites.

The R16 uses Triacs and if you used the one in the original parts list it is rated at 8 amps. Without a heat sink you may have problems with this much of course. I have several channels pushing 600 lights per channel with no problems.

Bad cable is the first thing I'd suspect. I had one on a long run this year. Replaced the cable and never looked back. I wonder though if your 12v power supply has an issue and your voltage is dropping too low at the second board. Probably not though.


Reply
Share: