Hello all,
I have a Ren-w v6, that's the small board, that is transmitting my signals, but the receivers are not sending anything to the Ren64. Here's the set up.
Computer to E1.31 converter.
Converter output to Ren-w v6 set to transmit.
Ren-w v6 set to receive to a Ren64.
The converter normally would hook right to the Ren64. In fact, when I hook it to the 64 all is well. The 64 responds appropriately. When I hook it to the transmitter and I look at the terminal window on the X-CTU software, on a separate computer from the Vixen, I can see the code being transmitted and received by the radio hooked through the programming board. Lines of FF's and 00's. But, the Ren64, with a receiver hooked to it does not respond.
It's not cabling. All have been checked and changed several times. The XBee setup is the same on all radios. The receive boards are set to receive. I'm about to pull my hair out.
Dave suggested it had something to do with the E1.31 converter, so I hooked it to the serial port. Same problem. The E1.31 send out a 485 signal. If it didn't then the Renards would not respond when plugged directly to it.
Any help, anybody??
Am I reading that you have two PCs, and have verified that the REN-W connection between the modules is operating as expected.
You then disconnect the receiver module from the second PC, and plug it into your REN64, at which time you get *nothing*.
Is this correct?
I know you said you have the RenW set to receive so don't take this personally but, are you sure you jumpered the "RX" pins? I only ask because I went through an hour of troubleshooting yesterday only to realize I DID NOT do this! 😉
Thanks,
-joni-
Lab Rat,
I have 2 computers. On #1 I have the programming board for the ren-w v6. I have an XBee plugged into that. Using the X-CTU software you can send or receive signals from this XBee.
On computer #2 I have the Vixen program and sequences. From it is a ren-w v6 set to transmit. Then there is a ren-w v6 hooked to a ren64 that is set to receive. It may be receiving, no way to tell, but there is nothing getting to the ren64.
When #2 is running a sequence you can see the code on the #1 using the X-CTU software, so I am fairly confident that it is transmitting.
FYI, I have used 2 different ren64's and 5 other ren-w v6's. All the ren-w's will transmit, but nothing will receive!
One more thing to look at, do your plug-in/COM port settings in Vixen match the configuration of the XBee's? For RenW's this is typically 57600 baud, 8, *M*, 1.
Thanks,
-joni-