I know the general consensus is a data issue, but I just want to chime in again about power one last time.
Are you using one power supply for the 16 trees and subsequent extensions out to the trees? If so, I would say your Power supply is tapped out and could be getting hot.
2.125 X 16 = 34 amps. Have you been using that arrangement for your sequences for a few years or was that just in place for last year?
Oh and +1 to Dave's suggestion on the REN24DC, I bought the kit in the pre-sale and plan on using for house outline due to the increased amperage of the controller. Very nice controller and very easy to build.


Reply
Posts: 2229
(@plasmadrive)
Famed Member
Joined: 15 years ago
RobertB wrote:Plasmadrive - I will give that a try. Trying to think back to Nov / Dec, I honestly think I tried "Jerry Rigging" some resistors on both ends. I probably need to just go buy some rj-45's (is that the right number for the connector?) and crimp in a resistor...the correct way 😉

Not sure you can use RJ45s and crimp in a resistor, but clean connection is important for sure.

Looking at your video from earlier and the newest one makes it seem more apparent that the flicker is not power related. Power supplies don't act like that when loaded down. For thermal they shut off for some time while the temp cools down. For current overload, they may recover right away, depends on the supply, but you are getting flicker with single colors and far too fast for it to be a supply issue. If it were a current issue, I would expect to see it only during "white" and it would flash off/on and perhaps throttle back voltage or completely shut down until the load is less... at least with most supplies. The ones I use actually require power recycling if they hit current limit. That way it forces you to find out what the problem is.

Keep looking for data issues...


Reply
Posts: 326
Topic starter
(@robertb)
Reputable Member
Joined: 17 years ago

I was using one supply for both sets. However in monitoring it, it never shut off. Amperage wise it was safe too. It has a amp meter on the supply I could watch. I also ran a 4" fan on the cooling fins. But........ that being said. I am going to run power supplies right at the controller next year. I have enough power supplies now (the kind everyone uses with their setups...that are rated at 30amps) I could run two supplies if need be. I had planned on having a spare supply in a battery box, cabled up and ready to go. Just in case of a breakdown on one. So good experiment to try at the first of the season next year.

On the rj45, could you just not crimp in a resistor and plug the rj45 into the open ethernet plug? (on the controller at the ends of the chain)


Reply
Posts: 2229
(@plasmadrive)
Famed Member
Joined: 15 years ago
RobertB wrote:I was using one supply for both sets. However in monitoring it, it never shut off. Amperage wise it was safe too. It has a amp meter on the supply I could watch. I also ran a 4" fan on the cooling fins. But........ that being said. I am going to run power supplies right at the controller next year. I have enough power supplies now (the kind everyone uses with their setups...that are rated at 30amps) I could run two supplies if need be. I had planned on having a spare supply in a battery box, cabled up and ready to go. Just in case of a breakdown on one. So good experiment to try at the first of the season next year.

On the rj45, could you just not crimp in a resistor and plug the rj45 into the open ethernet plug? (on the controller at the ends of the chain)

I think the RJ45s are good for 22g at best.. You might get an 1/8th watt in there.. but that could be pushing it. If you do, let me know.. that would be great info.


Reply
Posts: 2171
(@mschell)
Noble Member
Joined: 18 years ago

How far was the data line running? Given that the SANdevices was driving it, you don't need a terminator of any type at that end, but you might need one at the end of the line near the 27 channel controller.

A termination resistor only helps if it's a signal reflection issue on long runs.

It's much more likely that some type of external signal that could cause the flickering. It's recommended to NOT run the data line near or in parallel with AC lines. Some type of line driver or repeater might also help if the distance is quite long from sender to receiver. On the other hand, if the E68X is right near the 27 channel controller, it should be rock solid.


Reply
budude
Posts: 10400
(@budude)
Illustrious Member
Joined: 18 years ago
mschell wrote:How far was the data line running? Given that the SANdevices was driving it, you don't need a terminator of any type at that end, but you might need one at the end of the line near the 27 channel controller.

Actually - termination is normally required at both ends of an RS-485 line. All USB-DMX dongles have a beginning terminator and you are expected to put a terminator at the far end of the line - but only at the end device in the line.


Reply
Posts: 187
(@qbert-pns)
Reputable Member
Joined: 13 years ago

Sidebar.
Can the REN24DC be configured to work with DMX?
Thanks in advance


Reply
dlovely
Posts: 3167
(@dlovely)
Famed Member
Joined: 17 years ago
Qbert-PNS wrote:Sidebar.
Can the REN24DC be configured to work with DMX?
Thanks in advance

Using the 16F688 PICs yes its already done. Phil is working on the DMX code for the newer 16F1825 PIC.


Reply
kingofkya
Posts: 2165
(@kingofkya)
Noble Member
Joined: 15 years ago
mschell wrote:How far was the data line running? Given that the SANdevices was driving it, you don't need a terminator of any type at that end, but you might need one at the end of the line near the 27 channel controller.

A termination resistor only helps if it's a signal reflection issue on long runs.

It's much more likely that some type of external signal that could cause the flickering. It's recommended to NOT run the data line near or in parallel with AC lines. Some type of line driver or repeater might also help if the distance is quite long from sender to receiver. On the other hand, if the E68X is right near the 27 channel controller, it should be rock solid.

The entire point of rs485 aka: a differential driver is to stop that kinda noise.

Edit Nvm i was thinking about ethernet with the isolation transformers/magnents.


Reply
Posts: 326
Topic starter
(@robertb)
Reputable Member
Joined: 17 years ago
budude wrote:Actually - termination is normally required at both ends of an RS-485 line. All USB-DMX dongles have a beginning terminator and you are expected to put a terminator at the far end of the line - but only at the end device in the line.

You know it funny you say that. I just remember this (of course this last Oct....for Halloween...that things were put together). 2 seasons ago I was using a RPM dongle. This year I used E1.31 to run the e682. Then I came out of the e682 with a dmx signal. I HAD to have the RPM dongle pulled into the computer or the e682 would not work. I guess it was acting as a terminator for the RS-485 line?

BTW the e682 was right at the 2 - 27ch controllers for the mini trees (so no signal loss there) and THEN it went to the 7 trees to the right of the display (could be some signal loss there...35 to 40ft)