Using 3 strand romex

36 Posts
15 Users
0 Reactions
12.4 K Views
Posts: 65
Topic starter
(@neophaetr)
Trusted Member
Joined: 18 years ago
[#7872]

Is it suitable to usie 14ga romex for temporary power distribution from the main panel to a spider in the front yard? Mind you, the cable will be protected by weatherproof conduit. Here are my plans...
run the cables from the main panel through the crawl space to a junction box just under the eaves. From the junction box down through metal conduit to another junction box with a threaded end attached to weatherproof conduit going to a breaker box mounted on a stand of some sort. This stand will serve as a junction box for all the power wires. The breakers in the main panel will be of the gcfi type.

Does this sound like a safe setup? My father in law is an electrician and I will have him examine my setup before applying power. I just want some input as to how people get power to their displays if there are no available wall warts on the outside. Is this design a suitable one, or is there another way of doing it?

There are only a couple months to go and I need to get a move on. Im already 2 years in...this will be my first year...hopefully.
I have the board 80% done with 10 SSRs ready to rock. Cable runs still need to be run.
And I thought the holidays were rough!!!


35 Replies
Virtus
Posts: 1182
(@virtus)
Noble Member
Joined: 19 years ago

While that sounds like a fine solution (without knowing the load) I would put it in front of the father-in-law before construction to see if he recommends a different solution...he may even offer some parts/discounts if you flatter him enough!


Reply
Posts: 283
(@eswets)
Reputable Member
Joined: 18 years ago

First make sure romex is code. Second, 14g is only rated 15 amps. Make sure that you use a 15amp breaker. Third, use the ground (bare wire) in your setup. I am amusing that 3 strand is black, white and bare.


Reply
Posts: 65
Topic starter
(@neophaetr)
Trusted Member
Joined: 18 years ago

The load is whatever the ren64 board can handle while the channels would not be fully loaded. The max load on it will be two trees with 3 strands (.99A) and 10 mini trees @ .99A. Other than these high amperage channels, nothing 3-4 20A breakers can't handle at 80% or less.


Reply
Posts: 65
Topic starter
(@neophaetr)
Trusted Member
Joined: 18 years ago

Good call on the 15A capacity...totally slipped my mind. Yes, the strand has the bare wire in the middle and the ground will be used. I am a bit paranoid about running electricity anywhere!!!


Reply
Posts: 1423
(@oldcqr)
Noble Member
Joined: 18 years ago

Romex being solid core is not designed for temporary installations. Each time you pick it up and roll it up, you will weaken the wires inside, until one or more break.

If however you are running the wire as a permanent installation Romex is fine.


Reply
Posts: 65
Topic starter
(@neophaetr)
Trusted Member
Joined: 18 years ago

Would it be safe to say that, using my plans in the first post, from the main panel to the last junction box, romex would be an acceptable wiring solution. After, the last junction box, 12ga wires run through liquid tight conduit to a breaker box would be a safe move in order to get power out to the yard?

Disclaimer: Folks, my intent here is to make a very safe christmas light display with a frugal mindset. Any suggestions made are meant purely for speculation purposes with the risk and safeguards to be solely the responsibility of the installer.


Reply
Posts: 577
(@photovor)
Honorable Member
Joined: 19 years ago

Why not actually run some 14-3 (Red, Black, White, Bare) and give yourself 2x 15A circuits out there, so you have some room for expansion. 14 guage isn't too expensive right now.

Just keep in mind that if you put breakers at the end like you were saying, they can't be more than 15 Amp, or if you have a lighter guage wire somewhere in the installation, the breakers must be rated for the lesser.

Also, for your breakers at the end, make sure they're in a weather proof NEMA-6 rated enclosure/disconnect.

If you want to be sure, check with your local building codes.


Reply
dirknerkle
Posts: 10293
(@dirknerkle)
Illustrious Member
Joined: 18 years ago
Photovor wrote:
Just keep in mind that if you put breakers at the end like you were saying, they can't be more than 15 Amp, or if you have a lighter guage wire somewhere in the installation, the breakers must be rated for the lesser.

That's a key point -- I have a neighbor who once said "I kept blowing my 15A breaker so I replaced it with a 20A and it solved the problem" -- without giving a thought that the gauge of the wiring through their walls was probably not suitable for 20amps! Luckily, they haven't had a fire (yet) but I've warned him that what he's done is the very definition of dangerous and if they survived the ensuing fire, it would probably invalidate their homeowners insurance coverage after the inspectors sift through the debris and find the 20A breaker where it shouldn't be!

"Achhh....we'll be fine," he said... and downed another forkfull of lutefisk...

You can tell a Norwegian sometimes, but you can't tell 'em much!!! 😉


Reply
Posts: 485
(@sjwilson122)
Honorable Member
Joined: 19 years ago

Only thing I would add to what has already been said is, if total run of your new circuit is over 100 feet go up to the next wire size (ie 12ga) but keep the breakers at 15 amp.

Scott


Reply