hello,
I have added up the total Amp's my '08 display will require.
A little over 56A if all ch's are on. All ch's will not be on at the same time, so I added Amp's by color/ch. Red is the largest at 13.5A.
My question is, should I double this then round up to 30A for an add-on sub panel?
Or, should I round up the total, if all lights are on, count to 60A for a sub panel?
Current main panel is 100A.
Thanks in advance,
Brad
Brad Riley wrote:Think I found the answer.Brad
Some good stuff in that thread...
Brad Riley wrote:hello,I have added up the total Amp's my '08 display will require.
A little over 56A if all ch's are on. All ch's will not be on at the same time, so I added Amp's by color/ch. Red is the largest at 13.5A.
My question is, should I double this then round up to 30A for an add-on sub panel?
Or, should I round up the total, if all lights are on, count to 60A for a sub panel?Current main panel is 100A.
Thanks in advance,
Brad
In the NEC you should take the total load and add 125%. In the case of blinking lights I would take my largest one time demand add 125% and go with that. Rember it is cheaper to go ahead and allow for the future the first time. If that is not possiable, I would just add a 20amp circut on #12 guage wire. This is fused at 20 amps since 13.5amps x 125% is only 16.9 amps you would be covered as long as all the channels aren't turned on. If the run is over 100' voltage drop issues can occur and the wire must be up sized. When adding a sub-panel or new wiring at-least get an electrician to inspect your work normally it is a minumial charge and it is very comforting to the soul. We want light shows not fireworks!
Rocketman,
Thanks for the advice.
Brad