GFCI issue

12 Posts
6 Users
0 Reactions
11.6 K Views
Posts: 179
Topic starter
(@mildog)
Estimable Member
Joined: 12 years ago
[#51898]

I have determined that I have a "bad" receptacle on a GFCI circuit. If I connect that receptacle to the load side of the upstream GFCI receptacle it pops instantly even with nothing plugged in.

Was thinking of calling an electrician to check it, but not sure if that is overkill.

I was wondering if anyone had any issue like this and if just replacing the bad receptacle would probably resolve the issue?


11 Replies
Posts: 446
Posts: 2507
(@mrgrumpy)
Famed Member
Joined: 12 years ago

If you don't have test equipment, then replace the receptacle with a new one as a test. If it still trips; you are wiring it wrong, because there is nothing in a receptacle that would trip it. Call that electrician. However, if it doesn't trip - throw the old receptacle out and move on to the next project.


Reply
Posts: 118
(@pjones)
Estimable Member
Joined: 11 years ago

Receptacles are cheep. It’s worth a try and if it doesn’t work then report here and we can try to help you to determine if there is a wiring issue.

Sent from my iPhone using Tapatalk


Reply
Posts: 179
Topic starter
(@mildog)
Estimable Member
Joined: 12 years ago

I did make a discovery... I checked that "bad" outlet and discovered another line connected to it. I believe this other line runs out to an external light that is installed in the yard. I am about 90% sure this is what is causing my problem. I did not have time to trace the wire, but I hope to get to it this weekend. If that external light is the problem then I will just disconnect it and wait to troubleshoot it until after the display comes down. I dont need that light on out there anyway.


Reply
RGB_Mixer
Posts: 270
(@rgb-mixer)
Reputable Member
Joined: 12 years ago

GFCI devices were not designed to be "STACKED". It is not recommended to plug in one GFCI into another GFCI.

GFCI trips can be a combination of issues. I currently have a 100' sixteen strand mega tree with GFCI issues. It stays lit on a generator - but will trip the GFCI on normal power. MULTIPLE GFCI devices are available. I have tested all of them (100A subpanel with 32 circuits).

What I have found in the past are bad extension cords - most times the HOT has been exposed usually by a cut. In this case, something like this will cause an imbalance between the HOT and NEUTRAL depending on the current drawn through that cut. FLIR imaging can find it pretty fast but not everyone can get to borrow or use this tool - NOT CHEAP.

My cure for this - most times - in a pinch, I have removed the "THIRD" prong - it is an equipment ground. MOST (if not ALL) 120v holiday lighting are TWO PRONG. Never using the THIRD PRONG. Some use polarized plugs.

Water gets into the cut(s) and creates a path for "LEAKAGE" ... thusly causing a NUISANCE trip. Resetting it? OKAY. It is good for a few minutes or hours and BAM. Trips again.

The maximum current differential to trip most GFCI devices? 5ma - MAX - that is all. An RGB pixel at WHITE? 6ma.

CHECK all extension cords for nicks and cuts - keep them as dry as possible.


Reply
Posts: 344
 TSL
(@tsl)
Reputable Member
Joined: 10 years ago

I don’t use GFI outlets for my display. I found if there is even a forecast for precipitation they’d trip. I just make sure 120v stuff is in protective places. Not where water can puddle. Never had an issue. Just use common sense when laying out 120v stuff.

Sent from my iPhone using Tapatalk


Reply
Posts: 2507
(@mrgrumpy)
Famed Member
Joined: 12 years ago
TSL wrote:I don’t use GFI outlets for my display. I found if there is even a forecast for precipitation they’d trip. I just make sure 120v stuff is in protective places. Not where water can puddle. Never had an issue. Just use common sense when laying out 120v stuff.

We live in two different words. For me, I would never use outdoor power unless it is GF protected, and I would never suggest anyone to eliminate GF. A lost power outlet is far better than a lost life. Even being proactively and extremely cautious when avoiding GFCI can easily take life.

Other than GF can trip a GFCI. Bad GFCI receptacle. Overload. Upstream or downstream circuits like motor circuits, or fluorescent lights. GF can be hard to find, but I’d rather be looking and testing for my GF issue than toe tagged in a morgue

For most of us GF is hard to fine....try trial and error eliminating one strand or element at a time.


Reply
Posts: 118
(@pjones)
Estimable Member
Joined: 11 years ago
RGB_Mixer wrote:GFCI devices were not designed to be "STACKED". It is not recommended to plug in one GFCI into another GFCI.

GFCI trips can be a combination of issues. I currently have a 100' sixteen strand mega tree with GFCI issues. It stays lit on a generator - but will trip the GFCI on normal power. MULTIPLE GFCI devices are available. I have tested all of them (100A subpanel with 32 circuits).

What I have found in the past are bad extension cords - most times the HOT has been exposed usually by a cut. In this case, something like this will cause an imbalance between the HOT and NEUTRAL depending on the current drawn through that cut. FLIR imaging can find it pretty fast but not everyone can get to borrow or use this tool - NOT CHEAP.

My cure for this - most times - in a pinch, I have removed the "THIRD" prong - it is an equipment ground. MOST (if not ALL) 120v holiday lighting are TWO PRONG. Never using the THIRD PRONG. Some use polarized plugs.

Water gets into the cut(s) and creates a path for "LEAKAGE" ... thusly causing a NUISANCE trip. Resetting it? OKAY. It is good for a few minutes or hours and BAM. Trips again.

The maximum current differential to trip most GFCI devices? 5ma - MAX - that is all. An RGB pixel at WHITE? 6ma.

CHECK all extension cords for nicks and cuts - keep them as dry as possible.

For the record it only takes 2 ma to kill a person. It will stop your heart and lock it up. There is no saving you after that. As I see it, this is literally the fatal flaw of a modern GFCI. The good news is if you are hit with a higher amperage then there is a chance you may live providing someone is there with you to provide medical assistance until the ambulance arrives. There is probably enough background leakage occurring in the circuit already to protect you from death if you get a shock. If there is 2mA existing then you only need to pass through an additional 1 mA through your body before it will trip. That 1mA would not kill you but it will probably hurt quite a bit.

If a device has a ground then it is either old enough to predate the modern standards or it is not a double insulated device. That means you may have exposed metal on it that requires grounding so it doesn’t become energized in the event of a failure. If removing the ground prong fixes the problem then the ground is doing its job because it is removing this potential because something has occurred to allow the metal to become energized. By removing the prong you have removed the safety attached to the exposed metal leaving it live and looking for a new path to ground. At that point you are relying on the GFCI to provide the protection when someone touches it. The problem is GFCI typically trips at 3ma or above. This has now introduced a hazard to a situation that used to be safer. You haven’t made it completely dangerous but you have opened up that window of opportunity, and now rely on a device that can fail. Rest assured It will still protect you from becoming crisp if the device works.

Long story short, it’s best if you find and fix the faults instead of removing the safety. In modern day standards they are placed there only for good reason. No manufacturer wants the added cost of a 3 prong plug if they don’t have to use it.

Sent from my iPhone using Tapatalk


Reply
RGB_Mixer
Posts: 270
(@rgb-mixer)
Reputable Member
Joined: 12 years ago

Just to be clear:

My cure for this - most times - in a pinch, I have removed the "THIRD" prong - it is an equipment ground. MOST (if not ALL) 120v holiday lighting are TWO PRONG. Never using the THIRD PRONG. Some use polarized plugs.

I should have said I use a 3 to 2 prong adapter ... that DOES remove the equipment ground. Not a good idea to remove the ground pin from the plug b/c you might need it in the future.

Agreeably: Try to locate and correct faults FIRST. If 100% sure you do not need the EQUIPMENT GROUND downstream, the adapter trick could work.

What most folks do not know is GFCI devices are a differential sensor. Power must flow equally on the HOT and NEUTRAL for it to remain CLOSED (ON). When it senses a difference greater than its designed TRIP POINT, it OPENS the circuit (Turns OFF).

All my years in the field, I know what it feels like to get BIT by 120v, 277v & 480v - the ladder being the worst and grateful it was on the palm of my hand (felt it completely through my body).

Today's GFIC designs, depending on model, will usually trip between 3-5ma. Hospitals require <3ma trips and these devices cost big bucks. Most testers for GFCI you can buy @ HOME DEPOT and other places ... use a 8-10ma current to ground (third pin) to test devices. I work with equipment I can SET to a predetermined TEST LOAD, for hospital testing.

Two factors still remain. Time and Current. A brief split second 'SHOCK' causes very little cell damage and we all walk away from it, generally cussing a bit.

If the current through your body is sufficient and with time beyond a few seconds, that WILL cause some serious cell damage.

The PATH the current flows also determines "LIVE OR DIE". Get bit on the hand? Not too bad. If it crosses your chest? That is dangerous and can be fatal.

So, if you are not a "TRIED AND TRUE" master electrician, TURN THAT STUFF OFF before trying to service it. MAKE SURE it is OFF. I have worked on HIGH VOLTAGE equipment ... 4160V and greater. Everything changes including the RULES for safety. Some people I know have been seriously injured in the past when 4160v gear was checked but not properly grounded ... still here with us today and still doing the same job.

Take the time to inspect your stuff. That is what causes GFCI trips. A way of telling you there is a problem.

Last thought: If the adapter trick does NOT work? It is the stuff you have plugged in. It is leaking current. If it happens only when it is RAINING? Something is damaged, exposing conductors to the weather.


Reply