I've put together a plan for my pixel tree tree this year. It's my first crack at this and would love some input/suggestions on it. If you see anything that looks wrong or have suggestions please let me know. I want to make sure my power injection plan will work and that it is enough, and I would also like some input on fusing the power. I'm not sure how and where I need to go about the fuses.
* 11 - 12v WS2811 50 count nodes, will double them so 25/strand. 20 strands total + 1 Star
* using weatherproof pigtails for stings and T's for power injection
* PixLite4 controller
* 350w 12v 30amp PS
* Raspberry Pi show cpu
The layout looks good, except 511 pixels at 50ma (some say 60ma) full white each is 306.6 watts. That's *really* pushing it for one 350watt power supply.
I think you'll want to fuse all 4 lines coming out of the power supply. Put inline fuses at/near the power supply. The PixLite outputs are already fused.
Thanks for the help!
I'm calculating the use of all 11 strings so that's 550 pixels, just to be on the safe side.
The specs on the stings I've purchased are:
All white - 45ma/.55watts per node
All white - 2.268amps/27watts per string
80% of a 30amp PS is about 24amps. 80% of 350watts is 280watts.
Based of the specs, My setup is at 24.9amps and 302.5watts but I obviously won't know exactly what I'm pulling until I get the strings and meter them myself.
So is it better to calculate the power based off the wattage or the amperage? Or what consideration do I take when looking at both values to allow me to make the decision on moving to multiple power supplies?
Soundman516 wrote:So is it better to calculate the power based off the wattage or the amperage?
If your voltage is constant at 12 volts (technically it isn't due to resistance, but that's beyond this conversation), your amps and watts will always be in proportion with each other, so it doesn't matter which one you use.
Or what consideration do I take when looking at both values to allow me to make the decision on moving to multiple power supplies?
I wouldn't push a power supply over 80% - at least not for very long. You're also dealing with a lot of wire and resistance that will be a factor in efficiency. You might be good to go pushing the single supply, but you'd certainly be set if you went with two supplies.
IMO, you will be fine with the one supply, with the addition of the fuses mentioned. The reason I say this is because in reality, how often will you have every pixel on at full intensity, or even all on at one time for that matter. :biggrin2:
rstehle - I had the same thought. I'll see how it goes with one for initial testing, but i can easily pic another up if needed.
apollosmith - thanks for the info regarding both values, that bring much clarity for me going forward.
What's the worst case scenario? A fire due to overload? Overall less intensity for the pixels? Pixel discoloration? I'm just unfamiliar with all symptoms of an overloaded power supply.
You may be fine with no injection at all. I personally would just set this up with no injection and if you find that you have to inject just add ground and power, from the same power source, to the end of the 3rd string, every 150px (including at the end of the star).. not using a T, just 2 cores of a normal pigtail connector.
With this approach you should be find with 7amp fuses on the controller, but if you tap power directly from the power supply then you'll need to add an inline fuse.
If you really want to plan for injection, you might as well redesign this so you control the entire tree off a single output from the pixlite. You have one output, and a T connector every 150px to inject new power and ground both directions (and one more an additional T before the star). If you get this working well, you could add more props, or even 3 more identical trees all ran off the same controller. The only T's you would need for this would be the ones with 2 cores on the bottom, they are designed to send power both directions and keep data the same.
With this approach fuse at every T Connection, to the left and the right of the T where the T connects to the pixels (7 amps should be the max, but 5 should be fine).
efreeman1980 wrote:You may be fine with no injection at all.
550 pixels (around 24 amps worth) and 100+ feet of wire off one Pixlite output that's fused at 5 amps? Not going to work.
If you really want to plan for injection, you might as well redesign this so you control the entire tree off a single output from the pixlite. You have one output, and a T connector every 150px to inject new power and ground both directions (maybe one more an additional T before the star).
This would work, and it would free up data outputs. Data for the entire tree would be continuous from the beginning to the star with power injected as needed. The argument against this is that it becomes more difficult to isolate problems because you no longer have distinct power/data sections. One problem in one place will kill the rest of the tree from that point on - and if it's a power issue or blown fuses, you may not know which injection point or string is failing.
For fusing- I would fuse between every 2 strings;
This doesn't make much sense. What would happen with a short between that fuse and the power supply? Unless you mean that you would do this IN ADDITION to a fuse at the power supply.
apollosmith wrote:550 pixels (around 24 amps worth) and 100+ feet of wire off one Pixlite output that's fused at 5 amps? Not going to work.
Pixlite's 5 amp fuses may be replaced with 7 amp fuses. 1 pixlite output per 150 pixels. , inject at end if needed.
150 pixels is probably pushing limits without injecting; but sometimes is doable.
This doesn't make much sense. What would happen with a short between that fuse and the power supply? Unless you mean that you would do this IN ADDITION to a fuse at the power supply.
I revised while you were posting 😉
efreeman1980 wrote:1 pixlite output per 150 pixels. , inject at end if needed.
150 pixels is probably pushing limits without injecting; but sometimes is doable.
Ah. I see. Yes, it would be pushing it, but perhaps possible. This would also be pushing the total amperage for the Pixlite and the power supply.
I revised while you were posting 😉
:thup: I guess fusing between the strings (if not an injection point already) could be helpful to protect additional pixels if things go really bad.