I've looked at some online pixel how-tos recently, printed and video, and one item seems to be overlooked. Most of the DC power supplies commonly used to power pixels do not have an internal connection between the (-) side of the DC output and the ground terminal from the AC power cord. From a safety standpoint, it is good practice to connect the DC- and the AC ground together. This is most easily done with a short jumper wire between one of the DC- terminals and the terminal with the green ground wire of the AC cord.
Since there is no ground reference in the ethernet connection, the only way that a pixel system can get a ground reference is if the pixel power supply's minus is tied to the earth ground conductor of the AC power cord. There are 2 possible hazards if this isn't done. One is that leakage current, or an internal fault in the pixel power supply could result in there being 120V of AC on the whole system. The other is an accidental short circuit in the wiring to the pixel power supply. If the AC hot lead accidentally comes in contact with either the + or - leads of the DC output, this could put a lethal voltage on all of the components of the pixel system.
Can one determine if this internal connection exists by doing a continuity check between the DC- and AC Ground side? I'm not sure mine is setup properly and will need to make this adjustment if it's not. Thanks for bringing this up Jim!
Yes you can just measure resistance between - and ground.
I agree that this lack of a ground connection seems wrong.
But, two things to consider (this my only apply to the UK):
1. If the manufacturer (or the certifier of the standards) didn’t consider this connection required then there must be a reason (even the Chinese suppliers units are exact copies of the Meanwell certified designs).
2. Normally this type of supply is to offer a safe low voltage so as to not cause danger to people or animals. I can see good reason for connecting the V- (or ground) side of the DC output to an EARTHED connection. But if people are using 2 wire vampire plugs – under no circumstances should the V- (ground) be connected to anything on the input side of the power supply.
This could result in one of two things happening:
1. If the none live conductor becomes disconnected for any reason. All the elements connected to the power supply will be raised to mains voltage.
2. If the vampire plug is plugged in the wrong way round. All the elements connected to the power supply could have a part that is raised to mains voltage.
Now none of this is a serious problem, unless another fault occurs.
The bottom line is that most of you have mains voltage lights in your display and use GFIs (I think you call them).
I agree with Jim that this is something that needs to be looked at – but think that it is a little more complicated than the initial post.
i use the ground plug for most of my dc to help keep it safe, without worrying if the neutral is wired correctly, but that makes my dc power suplys 3 wire, and thus not usable with vampire plugs at all.
gigogig wrote:i use the ground plug for most of my dc to help keep it safe, without worrying if the neutral is wired correctly, but that makes my dc power suplys 3 wire, and thus not usable with vampire plugs at all.
I 2nd that! Old pc power cords work awesome. My E680 gets its own "special" cord from the outlet directly, no sharing with anything else in the yard(it's greedy like that :dry: ).
Barnabybear wrote:I agree that this lack of a ground connection seems wrong.
But, two things to consider (this my only apply to the UK):
1. If the manufacturer (or the certifier of the standards) didn’t consider this connection required then there must be a reason (even the Chinese suppliers units are exact copies of the Meanwell certified designs).
2. Normally this type of supply is to offer a safe low voltage so as to not cause danger to people or animals. I can see good reason for connecting the V- (or ground) side of the DC output to an EARTHED connection. But if people are using 2 wire vampire plugs – under no circumstances should the V- (ground) be connected to anything on the input side of the power supply.This could result in one of two things happening:
1. If the none live conductor becomes disconnected for any reason. All the elements connected to the power supply will be raised to mains voltage.
2. If the vampire plug is plugged in the wrong way round. All the elements connected to the power supply could have a part that is raised to mains voltage.
Now none of this is a serious problem, unless another fault occurs.
The bottom line is that most of you have mains voltage lights in your display and use GFIs (I think you call them).I agree with Jim that this is something that needs to be looked at – but think that it is a little more complicated than the initial post.
I suspect that they don't come that way from the factory because there are situations where you would not want to ground either dc output pin, an example would be if 2 power supplies were wired in series, or in certain circumstances you want want a negative voltage with respect to ground, so you would ground the +pin.
As far as #2, there would be no benefit in doing this if the power supply itself is not grounded via a 3-wire plug.
jstjohnz wrote:I suspect that they don't come that way from the factory because there are situations where you would not want to ground either dc output pin, an example would be if 2 power supplies were wired in series, or in certain circumstances you want want a negative voltage with respect to ground, so you would ground the +pin.As far as #2, there would be no benefit in doing this if the power supply itself is not grounded via a 3-wire plug.
Way back in the days before most of the people on here were even born (yes I am older than dirt it seems) Jim is correct on the term of wanting to have negative voltage in respect to ground. Also in those olden days of crazy things like wire wrapped circuit boards and actual transistors, capacitors, and such there were many problems with harmonics and dirty AC power that could sneak through the ground side of circuits so it was not a recommended thing to tie the AC ground to the negative terminal of your power supply. Of course you had to design things so that you did not end up with floating ground problems or potential differences too. Also there were no polarized plugs so many times you had the hot lead on the ground side if not paying attention which was solved many times by using an isolation tranformer and additional circuitry.
There were many different problems back then that do not apply in the modern times now and are lost on the newer generations of people working with electronics. You don't see tubes much anymore which had their own set of rules to use and design with as well.
Probably just as well though as I used to spend many hours trying to "find" very irritating glitches in circuits that would drive me crazy. Sometimes you could end up just scraping something as it would not work not matter what you did, yet another of the same item would work flawlessly!
Just an old guys opinion.
jstjohnz wrote:Most of the DC power supplies commonly used to power pixels do not have an internal connection between the (-) side of the DC output and the ground terminal from the AC power cord. From a safety standpoint, it is good practice to connect the DC- and the AC ground together. This is most easily done with a short jumper wire between one of the DC- terminals and the terminal with the green ground wire of the AC cord.
Is this also true for PC Power Supplies (used to drive pixels)? I looked at a couple of sample schematics for a switching power supply, and it didn't look like there was an internal connection but there were a lot of lines so I might have missed it.
don
djulien wrote:Is this also true for PC Power Supplies (used to drive pixels)? I looked at a couple of sample schematics for a switching power supply, and it didn't look like there was an internal connection but there were a lot of lines so I might have missed it.don
I'm pretty sure that's the case. The negative sides of the individual outputs (black wires) are tied to chassis ground at some point and I'm pretty sure that it's done in the power supply.