I have 10 E682s with about 1K pixels per controller, using most channels of each controller. As such, I ALWAYS seem to have something flickering, Ray_Wu type. Tonight, I decided I needed to understand exactly why this could happen. Here is what I found;
1. E682 sends data ALL THE TIME! if your lights are off, E682 is sending packets of "off"-still packets.
2. With as little as 50pF of capacitance on hookup wire, signal rise time suffers greatly.
3. Each pixel repeats last data forward - I E bucket brigade.
4. This data is phase delayed as it receives 24 bits then appears to forward, bitwise.
5. the "off" packets, and the shunt capacitance and series resistance (inductance) of the hook up wire, and the pixel repeat, the phase delay, and ground bounce all combine to a perfect storm (I think).
If you view the attached scope plot, you will see the yellow trace is the original signal. In this case, I placed a 100pF shunt at the pixel to simulate wire capacitance. Note that the yellow data can be seen in the BLUE trace waveform (VERY NEXT PIXEL IN STRING) in the form of ground bounce, proceeding the blue data actual rise. note also the voltage of the ground bounce-~1.3V. As such, it appears to greater than VIH max, but not quite VIL min-I.E. keep out region I regularly see periods of ~1.3uS appears to be valid high. my guess is that these minor timing violations are enough to turn led on.
On the bench, i can make minor adjustments to series resistance (INDUCTANCE) and shunt capacitance to result in everything to minor occasional red flicker to total white.
With regard to ground bounce, keep in mind the wire between pixels is RayWu wire. The longer the hookup wire, the worse the signal looks. The aggressive rise time speed must be just enough for bounce to occur. I also think the hookup wire might have inductance which would be just as bad as capacitance in this case. Twisted pairs might actually make this worse, not better.
Thoughts?
More thoughts;
INDUCTANCE
I have found that simply rearranging hook-up wire on ground, how it lies, can impact flicker. THis makes me wonder again if inductance of wire is fairly relevant.
Noise
I have found that routing wire over an AC power cord can cause flicker.
Connectors
Having connectors in hookup wire has cause me several flicker issues. Especially during rain.
Metal
Running hook up wire against metal, such as EMT conduit or gutters can cause flicker.