I'm just getting into all this and beginning to understanding on how most of all this works but I still have some questions that I cannot find answers to. So far I've wired everything up and got my first string of lights to turn on but I notice that I am not getting 12volts at the start of my string.
My Setup:
I have a 3 wire 18awg power cord wired into a Meanwell LRS-350-12 (Set to exactly 12v) when I first turned it on it read 11.8v so I adjusted the dial until it read 12v. I have 10awg wire going from the power supply to the Falcon F16V3 (powering up both sides of the board). Then I have a 20 foot 18awg 3 conductor wire running from the board to my first set of 100 pixels which are ALITOVE 12v ws2811 pixels (Power: 0.3W/pixel, 15W/unit 20awg wire). When I set the string of pixels to white at 30% brightness and test the voltage at the begging of the strand I get around 11.4v-11.7v and at the end of the string I get around 9.8v to 10v. I know I will more then likely need to power inject since I want that strand to be 143 pixels and read you should power inject after 100pixels. My concern is that in a video i watched on youtube for powering injecting it said you should see 12.23v at the beginning of the strand is that correct? If so since I only have 11.4v-11.7v at the start any ideas on what I am doing wrong.
elroyjets wrote:I'm just getting into all this and beginning to understanding on how most of all this works but I still have some questions that I cannot find answers to. So far I've wired everything up and got my first string of lights to turn on but I notice that I am not getting 12volts at the start of my string.My Setup:
I have a 3 wire 18awg power cord wired into a Meanwell LRS-350-12 (Set to exactly 12v) when I first turned it on it read 11.8v so I adjusted the dial until it read 12v. I have 10awg wire going from the power supply to the Falcon F16V3 (powering up both sides of the board). Then I have a 20 foot 18awg 3 conductor wire running from the board to my first set of 100 pixels which are ALITOVE 12v ws2811 pixels (Power: 0.3W/pixel, 15W/unit 20awg wire). When I set the string of pixels to white at 30% brightness and test the voltage at the begging of the strand I get around 11.4v-11.7v and at the end of the string I get around 9.8v to 10v. I know I will more then likely need to power inject since I want that strand to be 143 pixels and read you should power inject after 100pixels. My concern is that in a video i watched on youtube for powering injecting it said you should see 12.23v at the beginning of the strand is that correct? If so since I only have 11.4v-11.7v at the start any ideas on what I am doing wrong.
The answer is in a voltage drop calculator. You have 20' of 18AWG wire. You are going to lose about 0.3v at idle and 0.75v at full white for each 50 of your pixels you have at the end of the feed wire. Your wire is marginal for your load at that distance. Yes you can crank up the input voltage to 12.5v and you should be ok.
First off, I agree with your conclusions...
However, where do those number come from? From Wikipedia the resistance of 18AWG copper wire is .006385Ω/foot, so the resistance of 20 feet of that wire is .1277Ω. I'm assuming that both the power and ground wire are 18AWG, and that 100 RGB pixels draw 6A at full white. This puts the voltage drop at 0.77V in both the power and ground wires, or 1.54V total across the pixel-end of the feed wires. This is a little bit different than what you described.
You said you adjusted your power supply to output 12VDC which means you will not see a larger voltage (the 12.23 VDC you are referring to) at the beginning of your string. You have what appears to be a reasonable voltage drop for the beginning and end of your string. I am assuming the video referenced that value to ensure you have a high enough voltage for your last pixel(s). Just remember that as you increase your voltage with the same resistance the current will go up slightly.