I'm trying to use hockey puck SSR's to switch the neutrals on my mega tree to change the colors. The SSR's are AC input 90-280 VAC. The outputs of course are also AC rated at 25A. Operation is erratic. The inputs don't seem to like the shape of the wave forms coming from the triacs. Perhaps some filtering is needed to turn the waveform back into more of a sine wave. Not sure what to do at this point.
Does anyone have any suggestions?
Thanks for any help
Jack:confused:
So you're driving external SSRs from the SS24's 120vac output triacs?
A normal SS24 board has all the A/C power you need to drive 120vac directly right from the outbound triacs along the long edge of the board. To use external SSRs you'd have to take the output from the SS24's optocouplers and feed it to the external triacs and bypass the SS24's triacs altogether. I'm not sure how well that would work btw... 😐
What Hockey-Puck SSRs are you using, and what do you mean by 'operation is erratic''?
The SSR's are Crydom A1225-B. They are rated 25A 120VAC. The input is 90-280VAC.
I put C7 bulbs in parallel with the inputs and they light up fine. I think I'm getting sime interaction with the SSR output and the SS24 triac output. It appears trying to use triacs on the hot side and neutral is probably not a good idea.
I'm in the process of switching over to regular relays with 115VAC coils. The relays won't respond as fast but if I'm reasonably careful with how I sequence them I think they will be fine. They should have 100ms or less response time. They are old Potter & Brumfield relays 4PDT. So I can parallel contacts for better current handling.
Jack