Question for everyone. Did any of you upgrade your house circuit breakers to a higher amperage before you did your show? I'll be running power wires from my garage outlets and the outlets on the outside of my house. They are 20 amp circuit breakers and I'm upgrading them to 60 amp circuit breaks. That way won't shut power off to my house. Is what I'm doing necessary or overkill?
When I was using 90% incandescent lights, I spread the load across multiple 15A circuit breakers without any issues. Since switching to 99% LED, I now run everything on a single 15A breaker, so a 60A setup might be overkill. However, if you're running 32 x 360W power supplies, 60A may not be enough—you'll need to do the math to be sure.
For more details, check out the Power From The Grid section at WiredWatts:
https://www.wiredwatts.com/power-calculator
Not sure I am getting this. You have a few circuits in your garage that you want to convert from 20a to 60a by removing the existing wires and replacing them with 60a wires and connectors which would then require circuit panels to get to 20a outlets.
This would not protect the house from overloading and I would only do this if my panel did not have any more slots.
I have dedicated 20a circuits that only go to outside outlets. Works for me. Still cant run a hair drier + vacuum + show.
I assume you don't just "upgrade" the breakers but also replace the cables. 20A requires 12AWG cables. 60A requires something like 5AWG. That's a pretty big cable and you need to run this to all outlets that are on that circuit. If you don't do this, your house might go up in smoke...
If you go LEDs, you really don't need a whole lot of amps, though. Calculate how many LEDs you have, how many mW each consumes at max brightness, multiply this by the voltage and you get the DC wattage. Then calculate what that means in regards to AC consumption. Note that many cheap PSUs have an efficiency of 80-90% so you need to take this into consideration.
In my case, I have about 4 outlets along the eves on the first floor and maybe 3 on the second story. They are on different breakers. And then I have other outlets from the garage that are on another breaker.
From this thread your display would use about 25 kW in total if you're using regular pixels that draw 0.06A at full brightness. That would come to 210A at 120VAC, some fraction of that if you're using seed pixels. If you're sensible you will run the pixels at some fraction of full brightness, although people recommend designing for full brightness anyway.
That requires at least four 60A circuits, if you're going that route, and possible more depending on how you have the load split up. And as others have noted, you need to replace the existing wires on those circuits from the breaker panel to the outlets. I've never worked with loads of that size, but I'd suspect that you would use dedicated circuits for the pixel display, and you would want to have power splitters of some sort to connect to the individual power supplies. You've said that you've worked with electricity for 20 years, but asking that question indicates that this is new for you.