P. Short wrote:
I've never worked with loads of that size,
The only time I handled such a high electrical load was during my military service, working with 3-phase systems connected to the PDISEboxes, which were powered by 60kW generators to supply power to large operation centers.
P. Short wrote:
From this thread your display would use about 25 kW in total if you're using regular pixels that draw 0.06A at full brightness.
In that discussion you mentioned, the 25 kW refers to the DC side. The AC side will be higher due to conversion and efficiency losses at the power supply units (PSUs).
Formula: Power Supply Count × (Power Supply Rated Wattage / Efficiency / Power Factor / AC Voltage) = Grid Amps Needed
Using the values: 76 x 85% / 52% / 115 VAC = 520.32 Grid Amps.
This results in approximately 59.8 kW, based on a scenario involving 35,000 pixels @ 100% brightness.
You're right, I was basically (incorrectly) ignoring the various power inefficiencies.
520.32 grid amps 😮 Our main panel is 200A but then I don't have 35k pixels. You probably can see the house from a satellite. The good news is that the 52% power factor is for a PSU with no power factor correction (PFC). If you have one with passive PFC the 52% is more like 70%. And with active PFC you are probably looking at 95+%. Since most pixels seems to be just in 3 props (mega tree, garage matrix, window matrix) the runs aren't that long you probably can get by with 5V pixels instead of 12V pixels. Still need power injection but using 5V pixels cuts it down quite a bit. Then you most likely won't run this at 100% light level which cuts down even more. Then instead of pixels you can consider seed pixels which again lowers the consumption. So if you combine all of this you can cut the power consumption by 10x - 15x. That brings you down to a manageable level.
So my approach would be, don't change breakers which requires you to change the cables in the wall. Instead, keep your existing breakers. If you go over what can be pulled then the breaker will trip. That probably only will happen as you test everything before the actual display, unless you hook up other stuff while the display is running but you didn't hook those things up while testing. I would also measure the amps you really pull and see if you are getting close to the breaker rating. And then power the different props from outlets that are on different breakers. I think that would do the trick.
This is one of the reasons why I wanted to use an EV charger--because a level 2 is 220v and runs on its own breaker. But I've been getting along fine with household 120v charging and haven't had any significant problems with my show tripping breakers, so haven't had the motivation to sink that kind of money.