So i am running e682s with a 12v, 16A power supply ((waterproof) - hom many 12 v pixels can i run off that.
I plan on power injection - using the std ones from Ray Wu - what stretch would you inject at - any reason i cant just inject power at each end? would make wiring simpler (as log as i keep the ends correct)
Lastly - i would then have 2 wires from a power supply divided many times - what is a neat way of doing that - any suggestions before i solder lots of wires together branching out?
Following
Sent from my iPhone using Tapatalk
About 320 if you set up to run 100% full white. It's about 50 mA per pixel. Inject every 100. Make sure you properly size the wires for power injection. If you run one set of wires out and divide at the prop(s), it needs to be sized for the total current it will be carrying. Wire size is dependent on current being carried and distance it's going. Figure 12 or 14 gage if running a single set of power cables to the prop(s) and then dividing from there. A power distribution board makes a nice way of splitting the power. https://www.pixelcontroller.com/store/index.php?id_product=46&controller=product or https://www.crockettfantasyoflights.com/product-category/2017presale/presalepowerdistro/ . These are nice because the power injection should be be fused just like the outputs on the E682.
Note with the version 5 firmware for the E682 you can set a max power in the controller. By reducing max power to the pixels to 70 -80% (not discernible to the human eye), you can get more pixels out of that one power supply. At 80% max power, you could get 400 pixels.
Thats great! Can i ask how you calculated the power for a 16a supply? You would rn 14g to the splitter - what size from there?and i guess i would use the same fuses as come with the 682 for each? Thanks so much! R
Power is Volts times Amps. 16 x 12 = 192 Watts. Not sure that's really your question though. To calculate the number of pixels it's capable of powering, I found the typical max Amperage of a Ray Wu string of 12 Volt bullet pixels which was 0.050 Amps per pixel (that's 100% intensity white). Dividing 16 by 0.050 gives the maximum number of pixels your power supply can handle. I should provide a caveat here and that is you really shouldn't push the power supply to its limit. Most folks use 80% as a good safety factor. This means in your case, 80% of 16 or 12.8 Amps is what you should plan for. Running your pixels at 80% of their max power via the controller would cap you at 320 pixels or if you didn't want to limit their light output, 256 pixels at 100%.
I'd probably run 14 gage to the splitter if the distance isn't too long (less than 50 feet). Up to 100, use 12 gage. Both ground and power need to be of the same gage. Assuming your splitter is close to your strings, 18 gage should be fine between splitter and strings. I would fuse each branch the same as the E682 at 5 Amps.