Hopefully someone can help me out here.
I've got the Ren64 board built and am tying to get it to work.
The Wiki tells me to remove the U6 chip and replace it with one that has the diagnostics on it. On my board, the U6 chip is small so... I tried U7. This ran through the diagnostics successfully except for sending data from Vixen.
When I put the chip in U10, the diagnostics power-on routine finishes and then the two LEDs blink (2 & 5). When I run a sequence in Vixen, lights 6&7 come on solid while there is output in the sequence.
According to the Wiki, LED 7 should not be on.
I do not see blinky LEDs when I run a sequence. I used the beta diagnostics software, if that helps.
Thank you,
Derek
derekbackus wrote:Hopefully someone can help me out here.I've got the Ren64 board built and am tying to get it to work.
The Wiki tells me to remove the U6 chip and replace it with one that has the diagnostics on it. On my board, the U6 chip is small so... I tried U7. This ran through the diagnostics successfully except for sending data from Vixen.
When I put the chip in U10, the diagnostics power-on routine finishes and then the two LEDs blink (2 & 5). When I run a sequence in Vixen, lights 6&7 come on solid while there is output in the sequence.
According to the Wiki, LED 7 should not be on.
I do not see blinky LEDs when I run a sequence. I used the beta diagnostics software, if that helps.
Thank you,
Derek
Derek,
Looks like I did not finish editing that portion of the TS steps. I will work on that...now #7 is a Framing Error which means your data from the PC is not correct. This should be the same thing in U7 as well. Did you get your PC serial port setup + Vixen Serial port setup + PIC serial data setup the same?
The baud rate from Vixen in an output profile settings should also match the firmware programming. Another question, are you using a serial DB9 from the computer to DB9 on the Ren64 J22, or are you using some other configuration? And, are you trying to run a vixen sequence with the diagnostic firmware in, I don't believe you can run a sequence with diagnostics firmware, I've never tried though.
The diagnostics firmware will accept a sequence but will only indicate that the data is good (Channel 6) or bad (Channels 7 & 8).
Good to know, Thanks Ernie!
I'm using an RS485 interface (LOR). I do not have the LOR installed, just a straight through ethernet cable to the USB->485.
I first flashed with DMX. When I couldn't get that working, flashed with Renard. When that didn't work, I flashed the beta diagnostics.
When I get home, I'll plug 'er in and make sure the settingings match Vixen. I know vixen is set to 57K, 8-N-1. I didn't see anything about parity or stop bits in the debug ASM file.
I'll let you know if I can figure out anything else.
Quick question, can I put just one chip in to test this or do I need them all? I put them all in for the testing I've done, but flashing back and forth and swapping all is getting tedious.
Thank you!
Derek
If you are using the LOR RS-485 dongle to Renard you must swap pins 4 & 5 around. The D+/D- lines are swapped around between the two controller types. I used my LOR dongle a ton the year before for my Renard stuff but have moved to E1.31/DMX.
derekbackus wrote:Quick question, can I put just one chip in to test this or do I need them all? I put them all in for the testing I've done, but flashing back and forth and swapping all is getting tedious.
Yes, just use U10 til you are confident it is working correctly. You shouldn't need to run the diagnostics in any PIC slot other than U10.
budude wrote:If you are using the LOR RS-485 dongle to Renard you must swap pins 4 & 5 around. The D+/D- lines are swapped around between the two controller types. I used my LOR dongle a ton the year before for my Renard stuff but have moved to E1.31/DMX.
It worked! Just had to reverse pin 4 & 5. Thank you for this. I thought I was losing my mind!
Now to try it flashed with DMX
Derek