Downstream Renards not working

11 Posts
3 Users
0 Reactions
2,962 Views
Posts: 34
Topic starter
(@csledge)
Eminent Member
Joined: 15 years ago
[#38596]

I have 6 Renards connected via RS485 (USB converter out of the laptop, all Cat-5 cable). Only the first SS16 is working but nothing else downstream is working. Here's the setup:

Laptop > USB/RS485 > #1-SS16 > #2-SS8 > #3-SS16 > #4-SS16 > #5-SS8 > #6-SS8

I've tested each controller individually and all channels work. I swapped out #1 w/another SS16 - same issue. It works fine but nothing downstream. Also changed the network cable between #1/#2 - no change. I tested each network cable with cable tester (flashes LEDs for each wire) and all seem to be fine (all 8 wires are intact and straight-thru). These are the same cables I used last year with no problems (although they've been in the attic all year).

I'm leaning towards a software problem but not sure what else hardware-wise to check. I'm using a test sequence and have all controllers & elements patched and have all channels flashing on/off for 1 second for a duration of 4 seconds (have it looping). I also tried connecting directly to each controller with the downstream controllers attached - the connected controller works but nothing downstream. I know the channels should be coming on as they're working the display preview.

Windows 7/64-bit
Vixen 3.1u1

Thanks!

Colin


10 Replies
TazChaLet
Posts: 3042
(@tazchalet)
Famed Member
Joined: 13 years ago

in vixen how do you have your controllers setup maybe do a screen shot of your setup page in vixen are you running the normal default firmware


Reply
Posts: 34
Topic starter
(@csledge)
Eminent Member
Joined: 15 years ago

Here are some snapshots of the controller and display setup.

controllers
display config

Reply
TazChaLet
Posts: 3042
(@tazchalet)
Famed Member
Joined: 13 years ago

ok if you are daisy chaining your controller you have too look at them like they are one big controller you would set up 1 renard controller with 72 channels


Reply
Posts: 34
Topic starter
(@csledge)
Eminent Member
Joined: 15 years ago

Running standard operational firmware.


Reply
TazChaLet
Posts: 3042
(@tazchalet)
Famed Member
Joined: 13 years ago

you should download and install the newer version of vixen


Reply
Posts: 34
Topic starter
(@csledge)
Eminent Member
Joined: 15 years ago

Ok. I don't recall doing that last year but that would seem to make sense. I'll try that tomorrow.


Reply
TazChaLet
Posts: 3042
(@tazchalet)
Famed Member
Joined: 13 years ago

this is taken from the vixen website

One common mistake is for users to define multiple controllers when you should only be using one. Many hardware systems use a common data bus where data leaves the computer from one port and then travels down a data wire in and out of several controllers in a daisy chain configuration. The Renard protocol is a good example of this. If you have a chain of renards (regardless of type) that all connect to a computer at a single port, you need to define only one controller for that whole chain.


Reply
Posts: 34
Topic starter
(@csledge)
Eminent Member
Joined: 15 years ago

So if there was a second USB/RS485 converter with Renards connected, that would then require a second controller configured, correct? Different com port obviously.


Reply
TazChaLet
Posts: 3042
(@tazchalet)
Famed Member
Joined: 13 years ago

Yes each separate comm port gets set up but if you have 1 comm port with the controllers daisy chained it would be set as one big controller


Reply