Renard 64XC
Revision as of 04:22, 1 February 2010 by G2ktcf (talk | contribs) (The Board)
The Board
File:REN64XC PCB.jpg
The Renard 64 measures X" x X"
Circuit Diagram
Key circuit components
Connectors
  • J1 – RS485 outgoing data
  • JDP1 – RS232 incoming data, DE9 connector for direct connect to show computer serial port.
IC Chips
  • U4 & U5 – ST485BN, RS232/RS485 Transmitter/ Receiver
  • U6-U8 – PIC16F688 Microcontrollers
  • M1-M24 – MOC3023 Optoisolator, triggers the triac
Resistors
  • R34-R57 – Triac gate resistors. The value of these resistors in the BOM was selected for locations using 115/120 VAC power.
Diagnostic LEDs
Other Components
  • T1-T24 – BTA04-700T, these are gate sensitive triacs that only require 5mA of current on the gate signal. They were selected as a dual use triac for both LEDs and regular incandescent lights.
Jumpers
  • JP2 – 120 ohm termination resistor enable. Normally a shunt will be installed on JP2. Remove the shunt if you are experiencing problems with incoming data.
Test Points
  • GND – Ground
  • ZC – Zero Cross signal
The PICs (U6,U7 & U8) must be programmed with the latest firmware for the Renard SS24 to operate properly. The firmware can be found on the Renard Firmware wiki page.
Powering the Renard SS24
Input power requirements: An AC source
DC power:
The Renard SS24 generates all the DC voltage that it requires on-board and no external DC voltage source is required.
AC Power:
The Renard SS24 requires AC power for generation of the DC voltage, the SSR (opto/triac) circuitry and for generation of the Zero Cross signal. The information in this wiki is targeted at users who are using 115/120 VAC power.
AC Power Handling Capability
Maximum Input Load
The Renard SS24 is divided into two banks of twelve triacs. Each bank of triacs is capable of carrying up to 15 amps of current based on the trace width used on the pcb.
Triac Loads
Based on the pcb trace widths, each triac can handle up to two amps of current. A heat sink is highly recommended when running the triacs at two amps. Care must be taken to ensure that the total load of the twelve triacs in each bank does not exceed the rating of the fuse protecting the triac bank or 15 amps (whichever is less).
Each bank of triacs is independently protected by its own fuse. The size of the fuse selected to use for each bank of triacs is dependent on how the Renard SS24 is connected to the AC power. When each bank of triacs has its own dedicated AC input, the size of the fuse cannot exceed the current handling capability of the input wire or 15 amps (whichever is less).
If both banks of triacs are being powered by the same AC input and a jumper is used to connect the two banks together, then the size of both fuses added together cannot not exceed the current handling capability of the input wire.
The BOM calls for a 10 amp fuse under that assumption that each bank of triacs will be independantly powered by a common/generic extension cord. Most of the common extension cords used by DIYC members are rated for only 13 amps and 13 amp fuses are not commonly found.
Hooking Up the Renard SS24
Data Connections
Typical connection between computer running Vixen and Renard SS24 boards
Typical connection between RS485/DMX/Renard and Renard SS24 boards
Data Cables
Data cables for Renard SS board hookup directly to computer COMM port
PC DE9 Pin 3 to RJ45-pin 4
Data cable for Renard SS board hookup using a RS232->RS485 converter
Due to the many different types of RS232->RS485 converters available the drawing only refers to the signals coming from the converter. Check the documentation for your converter to figure out how/where to hook up the correct wires.
RS485(-) Signal to RJ45-pin 4
RS485(+) Signal to RJ45-pin 5
Data cable for Renard SS board hookup in a DMX environment
DMX using XLR Connectors
Data cable for Renard SS board hookup to other Renard boards
Cable Lengths
AC Power Connection
Connection Option #1
In the above layout, each bank of triacs has its own dedicated AC input (orange/black wires).
  • The size of each fuse cannot exceed the current handling capability of the orange/black wires or 15 amps (whichever is less).
Connection Option #2
In the above layout, the main AC input [orange/black wires] is connected to two sets of feeder wires [blue/green wires] by a twist-on wire connector (commonly referred to as a wire nut). The feeder wires are then connected to the triac banks.
Key things to remember in this layout are:
  • The size of the fuses cannot exceed the current handling capability of the feeder wires [blue/green wires] or 15 amps (whichever is less).
AND
  • The size of both fuses together cannot exceed the current handling capability of the main AC input [orange/black wires].
Connection Option #3
In the above layout, the right side banks of triacs are powered by jumper wires [blue/green wires] coming from the left side [N 120V] terminal block. This means that both banks of triacs are being powered by the same AC input [orange/black wires].
  • The size of the right fuse cannot exceed the current handling capability of the blue/green wires or 15 amps (whichever is less).
AND
  • The size of both fuses together cannot exceed the current handling capability of the AC input [orange/black wires].
Computer Setup
VIXEN Settings
  • Protocol Version: 1
  • Parity: None
  • Data bits: 8
  • Stop bits: One
If you are unsure that you have built your hardware correctly, you should follow the procedures contained in the Renard SS24 Beginners Setup Guide. These procedures will guide you through the steps to help setup the hardware for the first time.
If you encounter any problems with your Renard SS24, you can go to the Troubleshooting Guide The Renard SS24. The troubleshooting guide contains a methodical process to try to isolate problems/malfunctions and gives suggestions of what to do to fix them.
Beginners Setup Guide The Renard SS24
Assembly Instructions The Renard SS24
Renard Main Page
Renard Firmware
Part Substitutions
VIXEN
Glossary of DIYC Terms
Electronic Symbols