No edit summary  |
				m Ravinglunatic moved page The Renard SS24 Controller Board to Renard SS24 Controller Board: to make it easier to find  |
(No difference)
Revision as of 22:08, 4 May 2013
- The Renard SS24 is a PIC microcontroller based Christmas light controller with 24 solid state relay circuits incorporated into the board. The board design is based on the PIC-based 8-port dimmer concept originally developed by Phil Short. Information on the original concept can be viewed here. Generic information pertaining to current Renard designs (including maximum channel count) can be found on the Renard wiki page.
The Board
Board Availability
Circuit Diagram
- Key circuit components
- Connectors
- J1 – RS485 outgoing data
- Connectors
- IC Chips
 - U6-U8 – PIC16F688 Microcontrollers
 - M1-M24 – MOC3023 Optoisolator, triggers the triac
- IC Chips
- Resistors
- R34-R57 – Triac gate resistors. The value of these resistors in the BOM was selected for locations using 115/120 VAC power.
- Resistors
- Diagnostic LEDs
- Diagnostic LEDs
- Other Components
 - T1-T24 – BTA06-600CW
- Other Components
- Jumpers
 - JP2 – 120 ohm termination resistor enable. Normally a shunt will be installed on JP2 when receiving RS485 data. Remove the shunt if you are experiencing problems with incoming data.
- Jumpers
- Test Points
 - GND – Ground
 - ZC – Zero Cross signal
- Test Points
- The PICs (U6,U7 & U8) must be programmed with the correct firmware for the board to operate correctly. There are two types of firmware available: Operational and Diagnostic. The Operational firmware is what you need for normal board operation. The Diagnostic firmware is a troubleshooting aid to use when there are problems with the board.
- Renard SS Operational Firmware:
- Renard SS Operational Firmware.asm – source code that needs to be compiled
- Renard SS Diagnostic Firmware:
- Renard SS Diagnostic Firmware.asm – source code that needs to be compiled
- DMX Firmware:
- Since there are many options available with the Renard DMX firmware it is impractical to post a dedicated Renard SS board version here. Users desiring to use DMX should get the firmware here.
Powering the Renard SS24
DC power:
- The Renard SS24 generates all the DC voltage that it requires on-board and no external DC voltage source is required.
AC Power:
- The Renard SS24 requires AC power for generation of the DC voltage, the SSR (opto/triac) circuitry and for generation of the Zero Cross signal. The information in this wiki is targeted at users who are using 115/120 VAC power.
AC Power Handling Capability
Maximum Input Load
- The Renard SS24 is divided into two banks of twelve triacs. Each bank of triacs is capable of carrying up to 15 amps of current based on the trace width used on the pcb.
Triac Loads
- Based on the pcb trace widths, each triac can handle up to two amps of current. A heat sink is highly recommended when running the triacs at two amps. Care must be taken to ensure that the total load of the twelve triacs in each bank does not exceed the rating of the fuse protecting the triac bank or 15 amps (whichever is less).
- Each bank of triacs is independently protected by its own fuse. The size of the fuse selected to use for each bank of triacs is dependent on how the Renard SS24 is connected to the AC power. When each bank of triacs has its own dedicated AC input, the size of the fuse cannot exceed the current handling capability of the input wire or 15 amps (whichever is less).
Hooking Up the Renard SS24
Data Connections
Data Cables
Cable Lengths
AC Power Connection
- Connection Option #1
- The size of each fuse cannot exceed the current handling capability of the orange/black wires or 15 amps (whichever is less).
- Connection Option #2
- AND
- Connection Option #3
- AND
Configuring the jumpers on Renard SS boards
- JP1 & JP2 Configuraton
- JP1 installed
 - JP2 not installed
- JP1 not installed
- JP3 Configuraton
Computer Setup
- VIXEN Settings
- Protocol Version: 1
 - Parity: None
 - Data bits: 8
 - Stop bits: One
- If you are unsure that you have built your hardware correctly, you should follow the procedures contained in the Renard SS24 Beginners Setup Guide. These procedures will guide you through the steps to help setup the hardware for the first time.
- If you encounter any problems with your Renard SS24, you can go to the Troubleshooting Guide The Renard SS24. The troubleshooting guide contains a methodical process to try to isolate problems/malfunctions and gives suggestions of what to do to fix them.