Troubleshooting Guide The Renard SS16: Difference between revisions
Phil Short (talk | contribs)  New page: This page hasn't been entered yet...  |
				No edit summary  |
This page   | =='''Introduction'''==  | ||
:This page is intended to help identify/isolate some of the common problems individuals encounter when building/operating the Renard SS16 controller board.    | |||
:The troubleshooting procedures provided here are presented in a detailed step-by-step systematic approach.  This approach is not necessarily the quickest way to find your problem.  If you are looking for a quick fix, then swap anything/everything that you can and come back to these procedures if you are still having problems.  | |||
:The following procedures require the individual to be familiar with the operation of a digital multimeter (or voltmeter/ohmmeter if you prefer).  If you currently do not know how to measure resistance or how to measure voltage, please take some time now an learn these basic skills before attempting these procedures.  This [http://www.doctronics.co.uk/meter.htm website] provides some basic information on using multimeters.  | |||
{| style="width:60%; font-size:100%" border="1" cellspacing="0" cellpadding="10" align="center"  | |||
! <center>'''Multimeter Usage Tip'''</center>  | |||
| All DC voltages in this document are referenced to GND.  So for all measurements, the multimeter negative (-), usually black, lead needs to be connected to a GND point on the PCB.  The best location would be the GND Test Point located below U1.  The positive lead (+), usually red, gets connected to the location called out in the procedure.  | |||
=='''Disclaimers'''==  | |||
:Due to the nature of the information contained on this page, it is imperative that all individuals read and understand the disclaimers contained [[Disclaimers | here]].  | |||
=='''Basic Troubleshooting Info'''==  | |||
==='''Verify Setup'''===  | |||
:The first step to successful troubleshooting is to ensure that your setup is correct.  | |||
::*Verify that the Renard SS16 is assembled correctly as compared to the [[Assembly Instructions - The Renard SS16 | Renard SS16 Controller Assembly Instructions wiki]].  | |||
::*Verify that you have power/control cables connected correctly as compared to the [[The Renard SS16 Controller Board#Hooking Up the Renard SS16 | Renard SS16 Controller wiki]].  | |||
::*Verify that you have the Vixen plug-in settings correct as compared to the [[The Renard SS16 Controller Board#Computer Setup | Renard SS16 Controller wiki]].  | |||
==='''Most Common Problems'''===  | |||
:These are the most common problems encountered by individuals who have built Renard SS boards since their debut to the DIYC community:  | |||
::*'''Missed solder pads or bad solder joints'''.  Many individuals get in a rush when assembling their boards and will occasionally miss a solder pad or just do a poor job on a particular solder pad.  This type of problem can usually be easily identified by closely inspecting all the solder pads on the board after assembly is complete.  Missed solder pads may/will cause many different problems that will cause you to spend many hours troubleshooting only to find that it was as simple as a missed solder pad.  So take your time and closely inspect your solder work when you are done with the assembly.  | |||
::*'''Bad data cable coming from the computer'''.  Many individuals assume that all serial cables are identical, but that is far from the truth.  Just because a cable has the correct DE9 connectors on each end doesn’t mean that the wires inside are going to the correct pins for Renard operation.  It is always best to physically check the pin continuity to verify that the cable will work for Renard operation.  | |||
::*'''PICs with corrupted firmware or no firmware'''.  This mostly affects individuals who get their PICs from a “group buy” with the firmware already loaded but also does impact those who program their own PICs.  For whatever reason, sometimes a PIC (believed to be correctly programmed) will not behave correctly and needs to be re-flashed with the firmware.  Once it is re-flashed then it works correctly.  This is why all individuals who are using these boards should invest in a PIC programmer.  A programmer will also enable you to switch to the diagnostics firmware, which will help tremendously during troubleshooting.  | |||
::*'''Incorrect Vixen Settings'''.  It cannot be emphasized enough, the Renard boards will not work correctly if Vixen is not setup correctly.  Verify that you have the Vixen plug-in settings correct as compared to the [[The Renard SS16 Controller Board#Computer Setup | Renard SS16 Controller wiki]].  | |||
=='''Renard SS16 Troubleshooting Flow'''==  | |||
[[Image: Wiki - TSG Renard SS16 troubleshooting tree.gif|center|800x800px]]  | |||
<br>  | |||
<br>  | |||
=='''Troubleshooting Power Problems'''==  | |||
==='''Symptom(s): '''===  | |||
:*LED not lit   | |||
:*IC Chips hot to the touch   | |||
:*Transformer hot to the touch   | |||
==='''Possible Problem(s): '''===   | |||
:*No input voltage present   | |||
:*Transformer bad   | |||
:*Voltage Regulator bad   | |||
:*LED installed backwards   | |||
:*Blown fuse   | |||
==='''Troubleshooting Flow'''===  | |||
[[Image: Wiki - TSG Renard SS Power troubleshooting tree.gif|center|800x800px]]  | |||
==='''Troubleshooting Steps'''===   | |||
<ol>  | |||
<li>Remove power from Renard SS16   | |||
<li>Disconnect all cables.    | |||
<li>If installed, remove all 21 IC chips from their sockets (U2, U4 thru U7, and M1 thru M16).   | |||
:*This is to prevent them from being damaged further if you do have power problems.    | |||
<li>If not installed already, install an appropriate rated fuse in the left side fuse holder. Use the smallest value fuse that you have available for this portion of testing.   | |||
:*Using a smaller fuse here is for safety during initial power testing. If there are any problems with bad triacs, bridged solder pads or a bad transformer during first power application, a small fuse will blow before any permanent damage to the PCB can occur.    | |||
<li>If installed, remove the fuse from the right side fuse holder.    | |||
<li>Connect an AC power cable to the left side [N 120V] terminal block. The 120V neutral line (wide blade on a polarized plug) goes to the N terminal and the 120V hot line goes to the 120V terminal.   | |||
<li>Turn ON AC power.   | |||
<li>Did the fuse blow?   | |||
:*If it did, go to step 17  | |||
<li>Measure DC voltage at [[media: Wiki - TSG Renard SS16 Pwr Meas01.jpg |+5 Test Point]].   | |||
:Voltage should be +5 VDC +/- 0.05  | |||
:*If incorrect, go to step 13   | |||
<li>Did the PWR LED light?   | |||
:*If it did, go to step 21  | |||
<li>Measure DC voltage on [[media: Wiki - TSG Renard SS16 Pwr Meas02.jpg | right side of R6]].    | |||
:Voltage should be approx. 2.0-3.0 VDC.  | |||
:*If correct, then either the LED is installed backwards or is bad  | |||
<li>Measure DC voltage on [[media: Wiki - TSG Renard SS16 Pwr Meas03.jpg | left side of R6]].    | |||
:Voltage should be approx. 5.0 VDC.  | |||
:*If correct, then double check the value of R6  | |||
:*If this is incorrect, restart the troubleshooting process.  | |||
<li>Measure DC voltage at [[media: Wiki - TSG Renard SS16 Pwr Meas04.jpg | cathode of D3 & D4]].    | |||
:Voltage should be above +6 VDC but less than +12 VDC.  | |||
:*If correct, voltage regulator U1 is probably bad.   | |||
<li>Measure AC voltage [[media: Wiki - TSG Renard SS16 Pwr Meas05.jpg | between R1 and R2]].  | |||
:Voltage should be above 6 VAC   | |||
:*If correct, one or more diodes D1 thru D4 could be bad or incorrectly installed.  | |||
<li>Measure AC voltage between [[media: Wiki - TSG Renard SS16 Pwr Meas06.jpg | top side of F1]] and any N terminal.  | |||
:Voltage should be 115-120 VAC   | |||
:*If correct, transformer TF1 is probably bad.  | |||
<li>Measure AC voltage between [[media: Wiki - TSG Renard SS16 Pwr Meas07.jpg | bottom side of F1]] and any N terminal.  | |||
:*If correct, fuse F1 is probably bad.  | |||
<li>Turn OFF AC power  | |||
<li>Remove F1  | |||
<li>Turn ON AC power  | |||
<li>Recheck AC voltage between [[media: Wiki - TSG Renard SS16 Pwr Meas07.jpg | bottom side of F1]] and any N terminal.  | |||
:*If the voltage is now correct but was low or missing in step 16 or blew the fuse at initial turn-on, possible problems could be:  | |||
::Bad transformer (shorted primary)  | |||
::Bad/shorted triac  | |||
::Shorted/bad solder connection(s)  | |||
:*Carefully inspect the board for any possible problems with the solder connections.  Fix any possible problems and then restart the troubleshooting process.  | |||
:*After other attempts to fix the problem have failed, the last resort would be to remove each triac and the transformer til good power was seen with F1 installed.  | |||
<li>If you have gotten to this step, then your board has good +5 VDC and the PWR LED turns ON when AC power is applied without any of the IC chips installed.    | |||
<li>Install one of the IC chips (U2, U4 thru U7, and M1 thru M16) into its respective socket.   | |||
:*If it did not, then the last IC chip installed is bad and needs to be replaced.   | |||
:*If it did, then repeat steps 22 thru 25 until all IC chips are installed.  | |||
<li>Your Renard SS board should now have all the IC chips installed and have good DC power on the board.  | |||
</ol>  | |||
<br>  | |||
<br>  | |||
=='''Troubleshooting Diagnostics Problems'''==   | |||
:*Diagnostic LEDs do not light   | |||
:*HB and ZC LED do not flash  | |||
:*SD LED does not come on when receiving Vixen data  | |||
:*FE and/or OE LEDs light  | |||
:*Oscillator bad   | |||
:*Zero Cross signal bad   | |||
:*Bad or no data coming from Vixen  | |||
:*Vixen settings incorrect  | |||
:*Diagnostic LEDs bad or installed backwards   | |||
:*PIC bad  | |||
[[Image: Wiki - TSG Renard SS Diagnostics troubleshooting tree.gif|center|800x800px]]  | |||
<ol>  | |||
<li>Remove PIC chip U6   | |||
<li>Install a PIC programmed with the [[Renard Firmware#Beta Diagnostic Firmware | Beta Renard Diagnostic Firmware]] into the U6 position.  | |||
<li>Place a shunt (jumper) on JP3  | |||
<li>If desired, attached lights to terminal blocks [N  Ch1] thru [N  Ch8].  The diagnostics can be done with only the on-board LEDs.  | |||
<li>Ensure that the data cable from the computer running Vixen is connected to either J2 or JDP1.  | |||
<li>If receiving RS232 data from the computer, place a shunt on JP1.  | |||
<li>PWR LED should be lit  | |||
:*If incorrect , then go to the [[Troubleshooting Guide – The Renard SS16#Troubleshooting Power Problems | Troubleshooting Power Problems Steps]].  | |||
<li>The [[Renard Firmware#Beta Diagnostic Firmware | Beta Renard Diagnostic Firmware]] should perform the following channel test:  | |||
:*All channels ON for approx. 2 seconds  | |||
:*All channels OFF for approx. 2 seconds  | |||
:*Channel 1 turns ON for approx. 1 second then turns OFF  | |||
:*Channel 2 (HB LED) turns ON for approx. 1 second then turns OFF  | |||
:*Channel 3 turns ON for approx. 1 second then turns OFF  | |||
:*Channel 4 turns ON for approx. 1 second then turns OFF  | |||
:*Channel 5 (ZC LED) turns ON for approx. 1 second then turns OFF  | |||
:*Channel 6 (SD LED) turns ON for approx. 1 second then turns OFF  | |||
:*Channel 7 (FE LED) turns ON for approx. 1 second then turns OFF  | |||
:*Channel 8 (OE LED) turns ON for approx. 1 second then turns OFF  | |||
:*:The above routine is done three times <br>  | |||
<li>If no LEDs/channels came on during the above routine:  | |||
:#Verify that the LEDs are operational  | |||
:#Reflash the PIC with the [[Renard Firmware#Beta Diagnostic Firmware | Beta Renard Diagnostic Firmware]]   | |||
:#If the problem continues, then edit the [[Renard Firmware#Beta Diagnostic Firmware | Beta Renard Diagnostic Firmware]] to change from using the external oscillator to using the internal oscillator.  If you don't know how to do this, then download this version of the [[media:Ren-diag-beta-20090117 (intosc).asm | Beta Renard Diagnostics Firmware]].  | |||
:::*If the LEDs/channels are now working, then there is a problem with the oscillator U3.  Check the solder pads and/or replace U3.  | |||
:::*If no LEDs/channels came on,then either the PIC is bad or you have no DC power to the PIC.    | |||
<li>If the LEDs appear dim when all are on but normal when only a single LED is lit, then it is possible that resistor network RN1 is installed backwards.  | |||
:*You can choose to live with this condition but you will have to make sure that JP3 is not installed while running the operational firmware.  | |||
<li>If any (but not all) LEDs did not come during the step 10 routine, then go to the  [[Troubleshooting Guide – The Renard SS16#Verifying Diagnostic LEDs | verifying diagnostic LEDs steps]]  | |||
<li>If you used lights hooked up the channels and they did not respond correctly, then go to [[Troubleshooting Guide – The Renard SS16#Troubleshooting SSR Circuitry Problems | troubleshooting SSR circuitry problems]]  | |||
<li>The [[Renard Firmware#Beta Diagnostic Firmware | Renard Diagnostic Firmware]] should now be blinking the HB LED (channel 2) and ZC LED (channel 5).  All other channels/LEDs should be OFF.  | |||
<li>If the ZC LED (channel 5) is not blinking:  | |||
:Measure voltage at U6 pin 4 or U2 pin 5, should only be approximately .3 VDC.  If you have an oscilloscope, you should see a signal like the purple trace in this [[media:ZeroCross.gif | image]].  | |||
::*If voltage is around 5.0 VDC , then the ZC is not working.  Possible solutions:  | |||
:::#Replace U2  | |||
:::#Check the values of R1 & R2  | |||
:::#Check the solder pads on all the above components  | |||
<li>If you have gotten to this step, then your board appears to be functioning correctly so far.  Now it is time to see if it will communicate with the computer.  | |||
<br>  | |||
<span style="color:#D2691E">  | |||
<blockquote> <center>'''REMINDER:''' <br>   | |||
'''Make sure that Vixen is configured correctly before attempting the next step. <br> The settings for the Renard Dimmer Plug-In should be set as shown on <br>[[The Renard SS16 Controller Board#Computer Setup | The Renard SS16 Controller Board wiki page]]'''. </center></blockquote>  | |||
</span>  | |||
<br>  | |||
<li>Run a Vixen sequence  | |||
<br>  | |||
<span style="color:#9400D3">  | |||
<blockquote> <center>'''NOTE:''' <br>   | |||
'''Vixen only sends out data when there is a change in event data.  <br> So make sure that the test sequence you are using has frequent changes in the event data.'''.</center></blockquote>  | |||
</span>  | |||
<br>  | |||
<li>SD LED will be ON whenever Vixen sends data to the Renard SS16.  The FE and OE LEDs should remain OFF.  | |||
:*If this is correct, then your Renard SS16 has passed the diagnostics test.  | |||
<li>If the SD LED was ON and either or both the FE or OE LED came ON, then double check the Renard Dimmer plug-in settings in Vixen and retry.  | |||
<li>If no LEDs were lit in step 19, then it seems that you are not getting any data from the computer.  Try the following:  | |||
:#Make sure that your interconnect cable is built according to the [[The Renard SS16 Controller Board#data cables | Renard SS16 Controller wiki]].  | |||
:#Make sure that the Renard Dimmer plug-in is selected in Vixen.  | |||
:#Replace U5  | |||
:#Inspect the solder pads of U5 and the input data connector   | |||
</ol>  | |||
<br>  | |||
==='''Verifying Diagnostic LEDs'''===   | |||
<ol>  | |||
<li>If not already installed, place a shunt (jumper) on JP3.  | |||
<li>Power LED should be lit and the DC voltage at the [[media: Wiki - TSG Renard SS16 Pwr Meas01.jpg |+5 Test Point]] should be 5.0 (+/- .5) VDC.   | |||
:*If incorrect , then go to the [[Troubleshooting Guide – The Renard SS16#Troubleshooting Power Problems | Troubleshooting Power Problems Steps]]  | |||
<li>Momentarily connect a jumper (small piece of wire) between U6 [[media: Wiki - IC socket 13-14.jpg | IC socket pin 13 and pin 14]]   | |||
:*HB LED should light  | |||
<li>Momentarily connect a jumper between U6 [[media: Wiki - IC socket 10-14.jpg | IC socket pin 10 and pin 14]]  | |||
:*ZC LED should light  | |||
<li>Momentarily connect a jumper between U6 [[media: Wiki - IC socket 9-14.jpg | IC socket pin 9 and pin 14]]  | |||
:*SD LED should light  | |||
<li>Momentarily connect a jumper between U6 [[media: Wiki - IC socket 8-14.jpg | IC socket pin 8 and pin 14]]   | |||
:*FE LED should light  | |||
<li>Momentarily connect a jumper between U6 [[media: Wiki - IC socket 7-14.jpg | IC socket pin 7 and pin 14]]   | |||
:*OE LED should light  | |||
<li>If all the LEDs in steps 6 thru 10 did light, then the diagnostic LEDs are operational.  | |||
<li>If all of the LEDs in steps 6 thru 10 did not light:  | |||
:Check for 5.0 VDC at U6 IC socket pin 1  | |||
::*If incorrect, check the solder pads and/or go back to the [[Troubleshooting Guide – The Renard SS16#Troubleshooting Power Problems | Troubleshooting Power Problems Steps]]  | |||
:Check for 5.0 VDC on the pins  (on underside of board) of resistor network RN1  | |||
::*If correct, then probably all the LEDs are installed backwards  | |||
::*If incorrect, check to make sure the shunt (jumper) is good  | |||
<li>If any (but not all) of the LEDs in steps 6 thru 10 did not light, measure the DC voltage at the appropiate location on the IC socket for U6.  The voltage measured at each location should be approximately 3.0-3.5 VDC.  | |||
<br>  | |||
{| border="1" cellpadding="5" style="text-align: center; margin: 1em auto 1em auto"    | |||
!width="150"|   | |||
!width="250"|   | |||
!|Diagnostic LED || Measure DC voltage at  | |||
|HB ||U6 IC socket pin 13  | |||
|ZC ||U6 IC socket pin 10  | |||
|SD ||U6 IC socket pin 9   | |||
|FE ||U6 IC socket pin 8  | |||
|OE ||U6 IC socket pin 7   | |||
<br>  | |||
<li>If any voltage measured in step 13 was 0 VDC, then most probably the associated LED is installed backwards.  | |||
<li>If any voltage measured in step 13 was 5 VDC, then most probably the solder pads for the associated LED are bridged.  | |||
</ol>  | |||
<br>  | |||
<br>  | |||
=='''Troubleshooting SSR Circuitry Problems'''==   | |||
:*Channel remains on constantly  | |||
:*Channel does not come on when commanded  | |||
:*Triac gate resistor burnt/blown  | |||
:*Bad triac  | |||
:*Bad opto  | |||
:*Bad/missed solder joints  | |||
[[Image: Wiki - TSG Renard SS16 SSR Circuits troubleshooting tree.gif|center|800x800px]]  | |||
<ol>  | |||
<li> Turn OFF AC power  | |||
<li>Are any of the triac gate resistors (R26-R41) burnt/blown/damaged?  | |||
:*If so, replace that resistor and check the solder pads on the associated triac.  Blown gate resistors are usually caused by a missed solder connection on the triac.  | |||
<li>Are all channels 9-16 bad?  | |||
:*Check the right side fuse  | |||
:*Check the power connection to the right side of the board  | |||
:*Check the solder pads on the right side fuse holder  | |||
<li>Is the problem channel (channels 9 thru 16) controlled by U7?  | |||
:*Go to step 22  | |||
<li>Is the problem channel (channels 1 thru 8) controlled by U6?  | |||
:*If not, then what are you doing at this step.  Start over.  | |||
<li>If installed, remove the shunt (jumper) on JP3.  | |||
<li>If not already installed, attach some test lights to the terminal block of the failing channel.  | |||
<li>Test lights should be OFF  | |||
:*If the test lights are ON, go to step 37  | |||
<li>Using the following table, momentarily use a jumper to turn ON the test lights  | |||
:*Test lights should come ON when the jumper is connected to the locations in the table  | |||
<br>  | |||
!width="70"|   | |||
!width="100"|   | |||
!width="100"|   | |||
!width="250"|   | |||
!|Channel || Optoisolator || Test Lights at <br> Terminal Block || Connect jumper between  | |||
|1 ||M1 || [N  Ch1]  | |||
|align="left"|  | |||
:U6 [[media: Wiki - IC socket 3-14.jpg | IC socket pin 3 and pin 14]]  | |||
|2 ||M2 || [N  Ch2]  | |||
|align="left"|  | |||
:U6 [[media: Wiki - IC socket 13-14.jpg | IC socket pin 13 and pin 14]]  | |||
|3 ||M3 || [N  Ch3]  | |||
|align="left"|  | |||
:U6 [[media: Wiki - IC socket 12-14.jpg | IC socket pin 12 and pin 14]]  | |||
|4 ||M4 || [N  Ch4]  | |||
|align="left"|  | |||
:U6 [[media: Wiki - IC socket 11-14.jpg | IC socket pin 11 and pin 14]]  | |||
|5 ||M5 || [N  Ch5]  | |||
|align="left"|  | |||
:U6 [[media: Wiki - IC socket 10-14.jpg | IC socket pin 10 and pin 14]]  | |||
|6 ||M6 || [N  Ch6]  | |||
|align="left"|  | |||
:U6 [[media: Wiki - IC socket 9-14.jpg | IC socket pin 9 and pin 14]]  | |||
|7 ||M7 || [N  Ch7]  | |||
|align="left"|  | |||
:U6 [[media: Wiki - IC socket 8-14.jpg | IC socket pin 8 and pin 14]]  | |||
|8 ||M8 || [N  Ch8]  | |||
|align="left"|  | |||
:U6 [[media: Wiki - IC socket 7-14.jpg | IC socket pin 7 and pin 14]]  | |||
<li>Does the previously bad channel now work?  If it does:  | |||
:#Turn OFF AC power  | |||
:#Install PIC chip U6  | |||
:#Begin testing again where previous failure was noted  | |||
<li>Replace the opto (M1-M8) controlling the bad channel  | |||
:*Return to step 8 and repeat tests with the new opto  | |||
<li>Continue here if replacing the opto did not fix the problem  | |||
<li>Remove the opto (M1-M8) controlling the bad channel  | |||
<li>Momentarily use a jumper wire and connect between pins 4 and 6 of the opto socket  | |||
<li>If the lights still do not come on, it should only be one of the following things:  | |||
::*Bad triac  | |||
::*Bad/open triac gate resistor  | |||
::*Bad solder joints on the triac, opto socket, triac gate resistor or the terminal block  | |||
<li>If the lights did come on, measure the voltage at the opto socket pin 1  | |||
:It should be 5 VDC  | |||
:*If incorrect, check the current limiting resistor (R10-R17) associated with that opto.  You should be able to read approx 5 VDC on both sides of the resistor.    | |||
<li>Remove PIC chip U7   | |||
!width="70"|   | |||
!width="100"|   | |||
!width="100"|   | |||
!width="250"|   | |||
!|Channel ||Optoisolator || Test Lights at <br> Terminal Block || Connect jumper between  | |||
|9 ||M9 || [N  Ch9]  | |||
|align="left"|  | |||
:U7 [[media: Wiki - IC socket 3-14.jpg | IC socket pin 3 and pin 14]]  | |||
|10 ||M10 || [N  Ch10]  | |||
|align="left"|  | |||
:U7 [[media: Wiki - IC socket 13-14.jpg | IC socket pin 13 and pin 14]]  | |||
|11 ||M11 || [N  Ch11]  | |||
|align="left"|  | |||
:U7 [[media: Wiki - IC socket 12-14.jpg | IC socket pin 12 and pin 14]]  | |||
|12 ||M12 || [N  Ch12]  | |||
|align="left"|  | |||
:U7 [[media: Wiki - IC socket 11-14.jpg | IC socket pin 11 and pin 14]]  | |||
|13 ||M13 || [N  Ch13]  | |||
|align="left"|  | |||
:U7 [[media: Wiki - IC socket 10-14.jpg | IC socket pin 10 and pin 14]]  | |||
|14 ||M14 || [N  Ch14]  | |||
|align="left"|  | |||
:U7 [[media: Wiki - IC socket 9-14.jpg | IC socket pin 9 and pin 14]]  | |||
|15 ||M15 || [N  Ch15]  | |||
|align="left"|  | |||
:U7 [[media: Wiki - IC socket 8-14.jpg | IC socket pin 8 and pin 14]]  | |||
|16 ||M16 || [N  Ch16]  | |||
|align="left"|  | |||
:U7 [[media: Wiki - IC socket 7-14.jpg | IC socket pin 7 and pin 14]]  | |||
:#Install PIC chip U7  | |||
<li>Replace the opto (M9-M16) controlling the bad channel  | |||
:*Return to step 23 and repeat tests with the new opto  | |||
<li>Remove the opto (M9-M16) controlling the bad channel  | |||
::*Bad triac  | |||
:*If incorrect, check the current limiting resistor (R18-R25) associated with that opto.  You should be able to read approx 5 VDC on both sides of the resistor.    | |||
<li>Remove the opto (M1-M16) controlling the bad channel  | |||
<li>Is the test light still ON?    | |||
:*If the light is still ON then it could be either a bad triac or possibly a bridged solder joint on the triac, opto socket, triac gate resistor or the terminal block.  | |||
:*If the light is OFF, then replace the opto with a new one and retest  | |||
</ol>  | |||
Revision as of 00:46, 26 October 2009
- This page is intended to help identify/isolate some of the common problems individuals encounter when building/operating the Renard SS16 controller board.
Verify Setup
- Verify that the Renard SS16 is assembled correctly as compared to the Renard SS16 Controller Assembly Instructions wiki.
- Verify that you have power/control cables connected correctly as compared to the Renard SS16 Controller wiki.
- Verify that you have the Vixen plug-in settings correct as compared to the Renard SS16 Controller wiki.
- Bad data cable coming from the computer. Many individuals assume that all serial cables are identical, but that is far from the truth. Just because a cable has the correct DE9 connectors on each end doesn’t mean that the wires inside are going to the correct pins for Renard operation. It is always best to physically check the pin continuity to verify that the cable will work for Renard operation.
- PICs with corrupted firmware or no firmware. This mostly affects individuals who get their PICs from a “group buy” with the firmware already loaded but also does impact those who program their own PICs. For whatever reason, sometimes a PIC (believed to be correctly programmed) will not behave correctly and needs to be re-flashed with the firmware. Once it is re-flashed then it works correctly. This is why all individuals who are using these boards should invest in a PIC programmer. A programmer will also enable you to switch to the diagnostics firmware, which will help tremendously during troubleshooting.
- Incorrect Vixen Settings. It cannot be emphasized enough, the Renard boards will not work correctly if Vixen is not setup correctly. Verify that you have the Vixen plug-in settings correct as compared to the Renard SS16 Controller wiki.
Symptom(s):
- LED not lit
 - IC Chips hot to the touch
- No input voltage present
 - Transformer bad
 - Voltage Regulator bad
 - LED installed backwards
 - Blown fuse
- Remove power from Renard SS16
 - Disconnect all cables.
 - If installed, remove all 21 IC chips from their sockets (U2, U4 thru U7, and M1 thru M16).
 - Turn ON AC power.
 - Did the fuse blow?
- If it did, go to step 17
- If incorrect, go to step 13
 - Did the PWR LED light?
- If it did, go to step 21
- Voltage should be approx. 2.0-3.0 VDC.
- If correct, then either the LED is installed backwards or is bad
- If correct, then double check the value of R6
 - Measure AC voltage between  top side of F1 and any N terminal.
 - Measure AC voltage between  bottom side of F1 and any N terminal.
 - Turn OFF AC power
 - Remove F1
 - Turn ON AC power
 - Recheck AC voltage between  bottom side of F1 and any N terminal.
 - Bad/shorted triac
 - Turn OFF AC power
 - Install one of the IC chips (U2, U4 thru U7, and M1 thru M16) into its respective socket.
 - Turn ON AC power
Symptom(s):
 - HB and ZC LED do not flash
 - FE and/or OE LEDs light
- Oscillator bad
 - Zero Cross signal bad
 - Vixen settings incorrect
 - PIC bad
- Turn OFF AC power
 - Remove PIC chip U6
 - Turn ON AC power
 - PWR LED should be lit
- If incorrect , then go to the Troubleshooting Power Problems Steps.
 - The  Beta Renard Diagnostic Firmware should perform the following channel test:
- Verify that the LEDs are operational
 - If no LEDs/channels came on,then either the PIC is bad or you have no DC power to the PIC.
 - If any (but not all) LEDs did not come during the step 10 routine, then go to the verifying diagnostic LEDs steps
 - If you used lights hooked up the channels and they did not respond correctly, then go to troubleshooting SSR circuitry problems
- Measure voltage at U6 pin 4 or U2 pin 5, should only be approximately .3 VDC.  If you have an oscilloscope, you should see a signal like the purple trace in this  image.
- Replace U2
 - Check the values of R1 & R2
REMINDER:
The Renard SS16 Controller Board wiki page.
 - Run a Vixen sequence
NOTE:
 - SD LED will be ON whenever Vixen sends data to the Renard SS16.  The FE and OE LEDs should remain OFF.
- If this is correct, then your Renard SS16 has passed the diagnostics test.
 - If no LEDs were lit in step 19, then it seems that you are not getting any data from the computer.  Try the following:
- Make sure that your interconnect cable is built according to the Renard SS16 Controller wiki.
 - Replace U5
- Turn OFF AC power
 - Turn ON AC power
- HB LED should light
- ZC LED should light
- SD LED should light
- FE LED should light
- OE LED should light
- Check for 5.0 VDC at U6 IC socket pin 1
- If incorrect, check the solder pads and/or go back to the Troubleshooting Power Problems Steps
 - Check for 5.0 VDC on the pins  (on underside of board) of resistor network RN1
 - If incorrect, check to make sure the shunt (jumper) is good
 - If any (but not all) of the LEDs in steps 6 thru 10 did not light, measure the DC voltage at the appropiate location on the IC socket for U6.  The voltage measured at each location should be approximately 3.0-3.5 VDC.
Symptom(s):
- Bad triac
 - Bad opto
 - Bad/missed solder joints
- Turn OFF AC power
 - Are any of the triac gate resistors (R26-R41) burnt/blown/damaged?
 - Are all channels 9-16 bad?
- Check the right side fuse
 - Is the problem channel (channels 9 thru 16) controlled by U7?
- Go to step 22
 - Is the problem channel (channels 1 thru 8) controlled by U6?
- If not, then what are you doing at this step. Start over.
 - Turn ON AC power
 - Test lights should be OFF
- If the test lights are ON, go to step 37
- Turn OFF AC power
 - Install PIC chip U6
 - Turn OFF AC power
 - Turn OFF AC power
 - Turn ON AC power
- Bad triac
- It should be 5 VDC
 - Remove PIC chip U7
 - Turn ON AC power
- Turn OFF AC power
 - Install PIC chip U7
 - Turn OFF AC power
- Return to step 23 and repeat tests with the new opto
 - Turn OFF AC power
 - Turn ON AC power
- Bad triac
 - Turn OFF AC power
 - Remove the opto (M1-M16) controlling the bad channel
 - Turn ON AC power
 - Is the test light still ON?
