Line 122: Line 122:
===Voltage Drop Example===
# What is the voltage drop when using 5V  and drawing 500ma over a 10M pair of Cat5 wire?<br/>Since Cat5 wire has a loop resistance of about 0.19 &Omega;/M, the 10 M length will have a resistance of (10)(0.19)=1.9 &Omega;<br/>  By Ohm's Law we know that V=IR, then<br/>V=IR=(0.5)(1.9)=0.95 V drop, so only 4.05 V will be at the far end of the wire.<br/>
#What is the voltage drop when using 5V and drawing 30A over a 2ft length of 18ga wire?<br/>  Since 18 ga wire has a loop resistance of about 0.013 &Omega;/ft, the 2ft wire will have a resistance of (2)(0.012) = 0.024 &Omega;<br/>  By Ohm's Law we know that V=IR, then<br/>V=IR=(30)(0.024)=0.72 V drop, so only 4.28 V will be at the far end of the wire. The wire will get hot because it is dissipating P=VI=(0.72)(30)= 21W!  You must use larger wire for high currents!<br/>
This is a [http://doityourselfchristmas.com/forums/showthread.php?20242-New-tools-for-estimating-pixels-string-voltage-drops thread] that discusses voltage drop.<br/>
Revision as of 04:21, 25 June 2013
Ohm's Law
V=IR
Voltage = Current x Resistance
Ohm's Law Diagram
Voltage (V)
AC Voltage
  • AC Alternating Current
    • Common values:
DC Voltage
  • DC Direct Current
    • Common values:
      • The voltage of a typical NiMh AA battery is 1.25 volts DC (VDC).
      • Many integrated circuits require 5 volts DC (VDC) to power them.
Voltage Formulas
  • V=IR
  • V=√PR
  • V=P/I
Voltage Examples
  1. What is the voltage drop across a 4 Ω resistor that has a current of 0.3A?
    V=IR, V=(0.3)(4)=1.2V
  2. What is the voltage across a 5W lamp with a resistance of 2 Ω?
    V=√PR=√(5)(2)=√10=3.16V
  3. What is the voltage across a 1 W LED that has a current of 0.35A running thru it?
    V=P/I, V=1/0.35= 2.86V
Current (I)
  • Common values:
    • A typical string of 100 count incandescent lights draws 0.33A.
Current Formulas
  • I=V/R
  • I=P/V
  • I=√P/R
  • IParallel= I1+I2+I3+...In
Current Examples
  1. How much current flows thru a 680 Ω resistor that has 5V applied to it?
    I=V/R, I=5/680=0.007A (7 ma)
  2. How much current is used by a 75W floodlight using 120V?
    I=P/V, I=75/120=0.625A
  3. What is the current thru a 5W lamp with a resistance of 2 Ω?
    V=√P/R=√(5)/2=2.24/2=1.12A
  4. How much current is required by 1 RGB pixel that draws 20ma (0.02A) each per color?
    IParallel= I1+I2+I3=0.02+0.02+0.02=0.06A, or 60mma
  5. How much current is required by 4 RGB pixels that draw 60ma (0.06A) each when lit white?
    IParallel= I1+I2+I3+I4=0.06+0.06+0.06+0.06=0.24A, or 240 ma
Resistance (R)
  • Common values:
Resistance Formulas
  • R=V/I
  • R=V²/P
  • R=P/I²
Resistance Examples
  1. What value resistor do you need to drop 3V and allow 20ma thru the circuit?
    R=V/I=3/0.020=150Ω
  2. What is the resistance of a 120V light string that draws 40W?
    R=V²/P=(120)²/40=14400/40=360Ω
  3. What is the resistance of a 1W LED that draws 350ma?
    R=P/I²=1/(0.35)²=1/0.123)=8.16Ω
Power (P)
P=VI
Power=Voltage x Current
  • Common values:
Power Formulas
  • P=VI
  • P=I²R
  • P=V²/R
Power Examples
  1. How much power does a 100 count string of 120V incandescent lights that use 0.33A use?
    P=VI=(120)(0.33)=39.6 W
  2. How much power does a 4 Ω resistor dissipate as heat that has 0.3A running thru it?
    P=I²R=(0.35)²(4)= (0.123)(4)=0.49 W
  3. How much power does a 10 Ω resistor dissapate as heat that has 12V across it?
    P=V²/R=(12)²/10=144/10=14.4W
LED Resistor Calculator
By using Ohm's Law you can calculate the current limiting resistor needed to include in a circuit with a LED. LEDs need a resistor in a circuit to limit the amount of current flowing though it to prevent it from being destroyed. The current used by LEDs depends on the type of LED being used. Common values are:
LED TypeTypical Current I
Optoisolator LED6ma
Typical 5mm LED20ma
Piranha Superflux LED20ma
"1/3 W" LED100ma
1 W LED350ma
LED Color Typical VF
Optoisolator1.2-1.6 V
Red1.9-2.3 V
Green2.9-3.5 V
Blue2.9-3.5 V
White3.2-3.4 V
LED Resistor Example
  1. What resistor would you use with a 5VDC power supply and a Blue 5mm LED with a VF of 3.0V?
    First you need to calculate the voltage that the resistor needs to drop. That is equal to
    The table above recomends a current I of 20 ma for a 5mm LED. The formula for resistance gives us:
    To calculate the wattage resistor needed you use the formula for Power:
    P=VI=(2)(0.02)= 0.04W. You would use the next standard size up resistor, 1/8 W.
  2. What resistor would you use with a 5VDC power supply and an optoisolator with a VF of 1.2V?
    VDrop=VPowerSupply - VF=5-1.2=3.8V
    The table above recomends a current I of 6 ma for an optoisolator. The formula for resistance gives us:
    R=V/I=3.8/0.006=633Ω Generally you choose a resistor for that value or the next higher standard resistor value, 680Ω.
    P=VI=(3.8)(0.006)= 0.02W. You would use the next standard size up resistor, 1/8 W.
Single LED Calculator
Array of LEDs Calculator
Pixel Voltage Drop Calculator
  1. What is the voltage drop when using 5V and drawing 500ma over a 10M pair of Cat5 wire?
    Since Cat5 wire has a loop resistance of about 0.19 Ω/M, the 10 M length will have a resistance of (10)(0.19)=1.9 Ω
  2. What is the voltage drop when using 5V and drawing 30A over a 2ft length of 18ga wire?
    Since 18 ga wire has a loop resistance of about 0.013 Ω/ft, the 2ft wire will have a resistance of (2)(0.012) = 0.024 Ω