Beginners Setup Guide The Renard SS16: Difference between revisions
Wayne J (talk | contribs)
(14 intermediate revisions by 4 users not shown)
Line 43: Line 43:
<li>Measure DC voltage at the +5 test point (below U1).
:*It should be 5.0 (+/- .5) VDC
:*If incorrect , then go to the [[Troubleshooting Guide - The Renard SS16#Power Problem | Renard SS16 Troubleshooting Guide]]
:*If incorrect , then go to the [[Troubleshooting_Guide_The_Renard_SS16#Troubleshooting_Power_Problems | Renard SS16 Troubleshooting Guide]]
<li>Power LED should be lit.
:*If it didn’t , then go to the [[Troubleshooting Guide - The Renard SS16#Power Problem | Renard SS16 Troubleshooting Guide]]
:*If it didn’t , then go to the [[Troubleshooting_Guide_The_Renard_SS16#Troubleshooting_Power_Problems | Renard SS16 Troubleshooting Guide]]
<li>Place a shunt (jumper) on JP3.
Line 65: Line 65:
:*OE LED should light
<li>If any of the LEDs in steps 11 thru 15 did not light, then go to the [[Troubleshooting Guide - The Renard SS16#Diagnostic LED Problem | Renard SS16 Troubleshooting Guide]]
<li>If any of the LEDs in steps 11 thru 15 did not light, then go to the [[Troubleshooting_Guide_The_Renard_SS16#Verifying_Diagnostic_LEDs | Renard SS16 Troubleshooting Guide]]
<li>Remove the shunt from JP3.
Line 85: Line 85:
:*Test lights should come ON when the jumper is connected
<li>If either step 23 or step 24 failed, then go to the [[Troubleshooting Guide - The Renard SS16#SSR Circuit Problem | Renard SS16 Troubleshooting Guide]]
<li>If either step 23 or step 24 failed, then go to the [[Troubleshooting_Guide_The_Renard_SS16#Troubleshooting_SSR_Circuitry_Problems | Renard SS16 Troubleshooting Guide]]
<li>Repeat steps 18 thru 25 using the information in the following table:
Line 149: Line 149:
<li>If either step 35 or step 36 failed, then go to the [[Troubleshooting Guide - The Renard SS16#SSR Circuit Problem | Renard SS16 Troubleshooting Guide]]
<li>If either step 35 or step 36 failed, then go to the [[Troubleshooting_Guide_The_Renard_SS16#Troubleshooting_SSR_Circuitry_Problems | Renard SS16 Troubleshooting Guide]]
<li>Repeat steps 31 thru 37 using the information in the following table:
Line 199: Line 199:
<li>Install two RS232/RS485 Interface ICs U4 & U5 (PN# 511-ST485BN).
<br>
<br>
<br>
<br>
<br>
::If you have a PIC programmed with the [[Renard Firmware#Beta Diagnostic Firmware | Renard Diagnostic Firmware]] continue with step 43.
::If you have a PIC programmed with the [[The_Renard_SS16_Controller_Board#Firmware | Renard SS Diagnostic Firmware]] continue with step 43.
'''Note... You must use the Beta Firmware from the link with these instructions.'''
<br>
<br>
<br>
::If you only have PICs programmed with [[Renard Firmware#Regular Firmware | Renard Operational Firmware]] then go to step 60.
::If you only have PICs programmed with [[The_Renard_SS16_Controller_Board#Firmware | Renard SS Operational Firmware]] then go to step 60.
<br>
<br>
<li>Install PIC microcontroller U6 (PN# 579-PIC16F688-I/P) programmed with the [[Renard Firmware#Beta Diagnostic Firmware | Renard Diagnostic Firmware]].
<br>
<br>
<li>Install PIC microcontroller U6 (PN# 579-PIC16F688-I/P) programmed with the [[The_Renard_SS16_Controller_Board#Firmware  | Renard SS Diagnostic Firmware]].
Line 221: Line 217:
<li>Turn ON AC power
<li>The [[Renard Firmware#Beta Diagnostic Firmware | Renard Diagnostic Firmware]] should perform the following channel test:
<br>
<br>
<span style="color:#D2691E">
<blockquote> <center>'''NOTE:''' <br>
'''The following step only applies if you are using the [[The_Renard_SS16_Controller_Board#Firmware | Renard SS Diagnostic Firmware]].'''
<br>
'''If you are using the original [[Renard Firmware#Diagnostic Firmware | Renard Diagnostic Firmware]] just skip this step.'''</center></blockquote>
</span>
<br>
<li>The [[The_Renard_SS16_Controller_Board#Firmware | Renard SS Diagnostic Firmware]] should perform the following channel test:
:*All channels ON for approx. 2 seconds
:*All channels OFF for approx. 2 seconds
Line 234: Line 240:
:*:The above routine is done three times <br>
<li>The [[Renard Firmware#Beta Diagnostic Firmware | Renard Diagnostic Firmware]] should now be blinking the HB LED (channel 2) and ZC LED (channel 5).  All other channels/LEDs should be OFF.
<li>The [[The_Renard_SS16_Controller_Board#Firmware | Renard SS Diagnostic Firmware]] should now be blinking the HB LED (channel 2) and ZC LED (channel 5).
<li>If either step 47 or step 48 failed, then go to the [[Troubleshooting Guide - The Renard SS16#Diagnostic Problem | Renard SS16 Troubleshooting Guide]]
<li>If either step 47 or step 48 failed, then go to the [[Troubleshooting_Guide_The_Renard_SS16#Troubleshooting_Diagnostics_Problems | Renard SS16 Troubleshooting Guide]]
<li>Turn OFF AC power
Line 247: Line 253:
<li>Wait for the diagnostics routine in step 47 to complete
<br>
<blockquote> <center>'''REMINDER:''' <br>
'''Make sure that Vixen is configured correctly before attempting the next step. <br> The settings for the Renard Dimmer Plug-In should be set as shown on <br>[[The Renard SS16 Controller Board#Computer Setup | The Renard SS16 Controller Board wiki page]].  The only difference would be to <br> set the baud rate to 19200 for the original Renard Diagnostic Firmware'''.</center></blockquote>
</span>
<br>
<li>Run a Vixen sequence
<br>
<br>
<center>'''IMPORTANT REMINDER:'''</center>
<span style="color:#9400D3">
<blockquote>Vixen only sends out data when there is a change in event data.  So make sure that the test sequence you are using has frequent changes in the event data.</blockquote>
'''Vixen only sends out data when there is a change in event data.  <br> So make sure that the test sequence you are using has frequent changes in the event data.'''.</center></blockquote>
</span>
<br>
<br>
<li>SD LED will be ON whenever Vixen sends data to the Renard SS16.  The FE and OE LEDs should remain OFF.
:*If incorrect , then go to the [[Troubleshooting Guide - The Renard SS16#Diagnostic Problem | Renard SS16 Troubleshooting Guide]]
:*If incorrect , then go to the [[Troubleshooting_Guide_The_Renard_SS16#Troubleshooting_Diagnostics_Problems | Renard SS16 Troubleshooting Guide]]
Line 264: Line 279:
<li>To verify another functional PIC, repeat steps 43 thru 58 with a new PIC
<li>Install PIC microcontrollers U6 & U7 (PN# 579-PIC16F688-I/P) programmed with the [[Renard Firmware#Regular Firmware | Renard Operational Firmware]].
<li>Install PIC microcontrollers U6 & U7 (PN# 579-PIC16F688-I/P) programmed with the [[The_Renard_SS16_Controller_Board#Firmware | Renard SS Operational Firmware]].
<br>
'''Make sure that Vixen is configured correctly before attempting the next step. <br> The settings for the Renard Dimmer Plug-In should be set as shown on <br>[[The Renard SS16 Controller Board#Computer Setup | The Renard SS16 Controller Board wiki page]].'''</center></blockquote>
</span>
<br>
:*If the outputs do not respond correctly, then go to the [[Troubleshooting Guide - The Renard SS16#Vixen Data Problem | Renard SS16 Troubleshooting Guide]]
:*If the outputs do not respond correctly, then go to the [[Troubleshooting_Guide_The_Renard_SS16 | Renard SS16 Troubleshooting Guide]]
</ol>
</ol>
<br>
<br>
Line 275: Line 297:
<center>'''Your Renard SS16 should now be fully operational!''' </center>
=='''Configuring the jumpers on Renard SS boards'''==
:'''JP1 & JP2 Configuraton'''
:The configuration of JP1 and JP2 depends on the type of communication being used:
<br>
::'''RS-232 Communication (direct connect to PC)'''
:::*'''JP1''' installed
:::*'''JP2''' not installed
:::Reminder:  This only applies to the first Renard SS board connected to the PC.  The output of a Renard SS board to the next board is RS-485.
<br>
::'''RS-485 Communication (output of a Renard board or output from a RS-485 adapter/converter)'''
:::*'''JP1''' not installed
:::*'''JP2''' installed (try removing if data communication issues are encountered)
<br>
:'''JP3 Configuraton'''
::*Installed when running the Diagnostics Firmware
::*Normally not installed when running the Operational Firmware.  But can be left installed if you don’t mind seeing the on-board LEDs responding with the associated channels.
==Related Links==
==Related Links==
:[[The Renard SS16 Controller Board]]
:[[Assembly Instructions - The Renard SS16]]
:[[Assembly Instructions The Renard SS16]]
:[[Troubleshooting_Guide_The_Renard_SS16]]
:[[Troubleshooting Guide – The Renard SS16]]
:[http://doityourselfchristmas.com/forums/showthread.php?6663-The-Renard-SS-16-is-now-available!-(first-post-is-current-2-19-2011)  Board Availability Information]
:[[Renard Main Page]]
:[[The_Renard_SS16_Controller_Board#Firmware | Renard SS Firmware]]
:[[Renard Firmware]]
Line 294: Line 348:
:[http://en.wikipedia.org/wiki/Electronic_symbol Electronic Symbols]
[[Category:Renard SS16]]
Latest revision as of 23:07, 11 March 2012
This page was created to help out the new users who aren't fully confident that they have built their Renard SS16 board correctly. These steps are designed to allow the user to test/verify most components in a manner that should help to eliminate the possibility of damaging any of the components during initial testing.
The following procedures may appear to be tedious and time consuming but they are here for the individuals who are not confident in their soldering skills. By following these steps, the individual will be able to test out individual components and signal paths to verify that everything is working properly.
The following procedures require the individual to be familiar with the operation of a digital multimeter (or voltmeter/ohmmeter if you prefer). If you currently do not know how to measure resistance or how to measure voltage, please take some time now an learn these basic skills before attempting these procedures. This website provides some basic information on using multimeters.
Multimeter Usage Tip
All DC voltages in this document are referenced to GND. So for all measurements, the multimeter negative (-), usually black, lead needs to be connected to a GND point on the PCB. The best location would be the GND Test Point located below U1. The positive lead (+), usually red, gets connected to the location called out in the procedure.
Due to the nature of the information contained on this page, it is imperative that all individuals read and understand the disclaimers contained here.
Renard SS16 Basic Setup Steps
  1. Ensure all power is OFF
  2. Remove all cables
  3. If installed, remove all 21 removable IC chips (U2, U4 thru U7, and M1 thru M16).
  4. Perform a complete and thorough inspection of the underside of the PCB.
    • Check all the solder pads for clean solder joints, no bridging between adjacent pads and that all pads did get soldered.
    • Make sure the board surface is clean and free from any debris and flux residue.
  5. If not installed already, install an appropriate rated fuse in the left side fuse holder. Use the smallest value fuse that you have available for this portion of testing.
    • Using a smaller fuse here is for safety during initial power testing. If there are any problems with bad triacs, bridged solder pads or a bad transformer during first power application, a small fuse will blow before any permanent damage to the PCB can occur.
  6. Connect an AC power cable to the left side [N 120V] terminal block. The 120V neutral line (wide blade on a polarized plug) goes to the N terminal and the 120V hot line goes to the 120V terminal.
  7. Turn ON AC power
  8. Measure DC voltage at the +5 test point (below U1).
  9. Power LED should be lit.
  10. Place a shunt (jumper) on JP3.
  11. Momentarily connect a jumper (small piece of wire) between U6 IC socket pin 13 and pin 14
    • HB LED should light
  12. Momentarily connect a jumper between U6 IC socket pin 10 and pin 14
    • ZC LED should light
  13. Momentarily connect a jumper between U6 IC socket pin 9 and pin 14
    • SD LED should light
  14. Momentarily connect a jumper between U6 IC socket pin 8 and pin 14
    • FE LED should light
  15. Momentarily connect a jumper between U6 IC socket pin 7 and pin 14
    • OE LED should light
  16. If any of the LEDs in steps 11 thru 15 did not light, then go to the Renard SS16 Troubleshooting Guide
  17. Remove the shunt from JP3.
  18. Turn OFF AC power
  19. Install optoisolator M1 (PN# 859-MOC3023)
  20. Attach some test lights to the [N Ch1] terminal block
  21. If you installed a small value fuse in step 5, replace it with an appropriate value fuse in the left side fuse holder.
    • The fuse needs to be rated to handle the load of the lights that will be connected to channels 1 thru 8 but not greater than 15 amps.
  22. Turn ON AC power
  23. Test lights should be OFF
  24. Momentarily connect a jumper (small piece of wire) between U6 IC socket pin 3 and pin 14
    • Test lights should come ON when the jumper is connected
  25. If either step 23 or step 24 failed, then go to the Renard SS16 Troubleshooting Guide
  26. Repeat steps 18 thru 25 using the information in the following table:
    Optoisolator Test Lights at
    Terminal Block
    Connect jumper between
    M2 [N Ch2]
    M3 [N Ch3]
    U6 IC socket pin 12 and pin 14
    M4 [N Ch4]
    U6 IC socket pin 11 and pin 14
    M5 [N Ch5]
    M6 [N Ch6]
    M7 [N Ch7]
    M8 [N Ch8]
  27. Turn OFF AC power
  28. Connect an AC power cable to the right side 120V terminal block. The 120V neutral line (wide blade on a polarized plug) goes to the N terminal and the 120V hot line goes to the 120V terminal. This connection can be either a separate power cord or it can just be a jumper from the left side 120V terminal block.
  29. If not installed already, install an appropriate value fuse in the right side fuse holder.
    • The fuse needs to be rated to handle the load of the lights that will be connected to channels 9 thru 16 but not greater than 15 amps.
  30. Make sure the AC power cable going to the left side 120V terminal block is still securely attached.
  31. Turn OFF AC power
  32. Install optoisolator M9 (PN# 859-MOC3023)
  33. Attach some test lights to the [N Ch9] terminal block
  34. Turn ON AC power
  35. Test lights should be OFF
  36. Momentarily connect a jumper (small piece of wire) between U7 IC socket pin 3 and pin 14
  37. If either step 35 or step 36 failed, then go to the Renard SS16 Troubleshooting Guide
  38. Repeat steps 31 thru 37 using the information in the following table:
    Terminal Block
    M10 [N Ch10]
    U7 IC socket pin 13 and pin 14
    M11 [N Ch11]
    U7 IC socket pin 12 and pin 14
    M12 [N Ch12]
    U7 IC socket pin 11 and pin 14
    M13 [N Ch13]
    U7 IC socket pin 10 and pin 14
    M14 [N Ch14]
    U7 IC socket pin 9 and pin 14
    M15 [N Ch15]
    U7 IC socket pin 8 and pin 14
    M16 [N Ch16]
    U7 IC socket pin 7 and pin 14
  39. Turn OFF AC power
  40. Place a shunt on JP2
  41. Install optocoupler U2 (PN# 782-H11AA1).
  42. Install two RS232/RS485 Interface ICs U4 & U5 (PN# 511-ST485BN).
    If you have a PIC programmed with the Renard SS Diagnostic Firmware continue with step 43.
    If you only have PICs programmed with Renard SS Operational Firmware then go to step 60.
  43. Install PIC microcontroller U6 (PN# 579-PIC16F688-I/P) programmed with the Renard SS Diagnostic Firmware.
  44. Place a shunt (jumper) on JP3.
  45. If desired, attached lights to terminal blocks [N Ch1] thru [N Ch8]. The diagnostics can be done with only the on-board LEDs.
  46. Turn ON AC power
    NOTE:
    The following step only applies if you are using the Renard SS Diagnostic Firmware.
    If you are using the original Renard Diagnostic Firmware just skip this step.
  47. The Renard SS Diagnostic Firmware should perform the following channel test:
    • All channels ON for approx. 2 seconds
    • All channels OFF for approx. 2 seconds
    • Channel 1 turns ON for approx. 1 second then turns OFF
    • Channel 2 (HB LED) turns ON for approx. 1 second then turns OFF
    • Channel 3 turns ON for approx. 1 second then turns OFF
    • Channel 4 turns ON for approx. 1 second then turns OFF
    • Channel 5 (ZC LED) turns ON for approx. 1 second then turns OFF
    • Channel 6 (SD LED) turns ON for approx. 1 second then turns OFF
    • Channel 7 (FE LED) turns ON for approx. 1 second then turns OFF
    • Channel 8 (OE LED) turns ON for approx. 1 second then turns OFF
  48. The Renard SS Diagnostic Firmware should now be blinking the HB LED (channel 2) and ZC LED (channel 5).
  49. If either step 47 or step 48 failed, then go to the Renard SS16 Troubleshooting Guide
  50. Turn OFF AC power
  51. Connect a data cable to the computer running Vixen to either J2 or JDP1 on the Renard SS16.
  52. If receiving RS232 data from the computer place a shunt on JP1
  53. Turn ON AC power
  54. Wait for the diagnostics routine in step 47 to complete
    REMINDER:
    The Renard SS16 Controller Board wiki page. The only difference would be to
  55. Run a Vixen sequence
    NOTE:
  56. SD LED will be ON whenever Vixen sends data to the Renard SS16. The FE and OE LEDs should remain OFF.
  57. Turn OFF AC power
  58. Remove U6
  59. To verify another functional PIC, repeat steps 43 thru 58 with a new PIC
  60. Install PIC microcontrollers U6 & U7 (PN# 579-PIC16F688-I/P) programmed with the Renard SS Operational Firmware.
  61. Turn ON AC power
    REMINDER:
  62. Run a Vixen sequence
  • JP1 installed
  • JP2 not installed
  • JP1 not installed
  • JP2 installed (try removing if data communication issues are encountered)
JP3 Configuraton
  • Installed when running the Diagnostics Firmware
  • Normally not installed when running the Operational Firmware. But can be left installed if you don’t mind seeing the on-board LEDs responding with the associated channels.
Renard Main Page
Renard SS Firmware
Renard Firmware
Part Substitutions
VIXEN
Glossary of DIYC Terms
Electronic Symbols
