I need some clarification on common ground.

I will be using a F16V2-R along with a differential expansion board and four differential receiver boards. If I use 10 universes from the main board to control my mega tree and mega star powered by two power supplies, one for each 8 eight universes and then run a receiver board to say my arches or snow flakes with each receiver board having it own power supply do all of the power supplies need to have a common ground?


11 Replies
Wolfie
Posts: 2225
(@wolfie)
Noble Member
Joined: 11 years ago

Yes. They should all be tied to a common ground. That provides a universal ground reference for all data lines.


Reply
Posts: 126
Topic starter
(@thechief96)
Estimable Member
Joined: 11 years ago

So just a single wire going from one power supply to the next? Even the two that would power the F16V2-R?


Reply
Posts: 1133
(@toozie21)
Noble Member
Joined: 19 years ago

Think of your ground as a reference point. The voltage associated with a particular ground is sitting at that point with respect to that reference. So a power supply that is +12Vdc has 12Vdc above the ground reference. A second power supply with +12Vdc will be doing the same thing, but the ground might be sitting at a different reference. You tie the two grounds together and now the reference points match and the two +12Vdc supplies are with respect to the same potential. Make sense?


Reply
Wolfie
Posts: 2225
(@wolfie)
Noble Member
Joined: 11 years ago

Yes. All the grounds should be connected. Some way. A single wire is sufficient. Even different voltage PSUs should have the grounds tied together. If you have a 5v and a 12v psu, tie the grounds together, just not the V+ obviously.

The goal is to provide a common ground so that the data signals all have the same reference point.

You say there is 5v on a line. 5v referenced from where? Usually ground but it doesn't have to be. The reference point could be 100v above ground. The line is 5v above its reference but its 105v above ground.

By tying all the grounds together, they are all at the same potential as a reference.

An example of an isolated reference/ground is on my 3D printer. It only has 5v and 24v outputs from its control box. I wanted to add strips of LED lights to illuminate the build area. All I had was 12v LEDs. If I plugged them into the 5v, they wouldn't light. If i plugged them into 24 they would fry. So I took two identical lengths and soldered them in series. The V+ of one went to the GND of the 2nd one. Then I applied 24v across both. The common between them is 12v above ground so the first strand sees 12v. The second strand also sees 12v because its ground is 12v above ground. SInce the ground is 12v above ground, 24-12 is 12. Therefore, it also sees 12v.

In the above example an isolated ground is a good thing. In most display circumstances its not. Having a floating ground does not provide a return path for the data signal. It also allows the ground to possibly be at a different potential than some other ground.

Make sense?