As said, it really depends on what kind of lights you want to run (incandescent or LED for simplicity) as they draw different amounts of current which is what will determine your power needs.
The LOR controllers (mostly) will allow up to 30 amps at 15 amps per side although it depends on which one you have. I have the CTK kit with high power and can draw 40 amps at 20 amps per side. So it can help to know which controllers you are going to use.

You really have to calculate the amount of power you need by knowing what kind of lights and how many you will be running on each channel of the controller to figure out how much total power you need.
If you are running all the same type of lights, get the total number of bulbs for each controller first. Then find the amp draw of the type of bulb you are going to use. Then you can get the total current draw and see if you need two circuits or if you can use just one.
Also if your LOR controllers have two power cords on each controller then you can use separate circuits to run each "side" of the controller and thus split power usage up even more.

I run LEDS in my display with 16 LOR controllers and I did install a sub panel with 12 - 20 amp GFCI circuits to outlets under my front deck. Come to find out, I am running over 19,000 LED bulbs and drawing so little that I could run all the controllers on just 3 of the circuits! LEDs draw so little that they are great and allow many more per channel.

A Kill-O-Watt meter is a great investment that can help figure this stuff out as well. Very handy and useful. GFCI receptacles are a very good idea for safety as well.


Reply
Protege94
Posts: 556
Topic starter
(@protege94)
Honorable Member
Joined: 10 years ago

I will be using probably 90%-95% LED lights. The only lights that probably wont be LED are my blowmolds. However I plan on ordering a few LED bulbs to see how it looks.


Reply
Posts: 154
 zman
(@zman)
Estimable Member
Joined: 18 years ago

Something to add to Bill's Kill-O-Watt. It would help to use a spreadsheet to track your controller power needs. I could not do a display without the XLS that Rick Williams of Quartz Hill Christmas created long ago. He added the 50 controller version after he got tired if fixing my older 25 controller version he had.

Here is a link to pull one down:

http://www.quartzhillchristmas.com/12.html

I have further modified this with my own info, and a copy of that is linked on my Websites, How-To Page


Reply
Jack Stevens
Posts: 243
(@jack-stevens)
Estimable Member
Joined: 17 years ago
Protege94 wrote:I will be using probably 90%-95% LED lights. The only lights that probably wont be LED are my blowmolds. However I plan on ordering a few LED bulbs to see how it looks.

For a better display, get rid of the single or dual points of light inside the blow-molds. Most blow-molds will let you wrap a piece of pvc with a string of LED lights inserted vertically inside the unit; this makes for a much more even distribution of light. Come out of the bottom of the blow-mold to a T fitting, run some short pvc each way out of that T to another set of T fittings, making the base an "H" shape with the vertical piece going inside the blow-mold attaching to the center bar in the "H" Use molly-bolts to secure the frame to the blow-mold, or maybe hot glue. Drill a hole in the bottom side of the T that holds the vertical pvc, large enough to slide over a piece of #3 rebar put into the ground to keep the blow-mold vertical.

A caveat of doing this; any paint scrape or ding in the blow-mold will be much more visible because it will be lit up better.

I can't claim credit for this idea; Denny Cole (@kidcole on http://ChristmasCarolina.com ) developed this.

-Jack


Reply
Protege94
Posts: 556
Topic starter
(@protege94)
Honorable Member
Joined: 10 years ago

Can someone post their panel or sub-panel so that I can see how they did it?

Additionally. I have a sub-panel in my basement. I dont feel like drilling holes into my foundation to run conduit so would it be ok to put in four 20amp breaks and then run those to four separate 20amp GFCI plugs within the basement? Then use extension cords to run from the GFCI to the LOR controllers outside?