in the attached picture do i need to connect the two neutral bus bars together? i am planning on using two different 15Amp circuits and i need to know. Please help!
And also when looking at the male end of the plug [A]
(C)
I know C is ground but which is which on top?
Thanks
No, you don't want to connect the neutral buses together.
I don't think the polarity really matters, but if you're like me (perfectionist), you connect it correctly anyway. If you're looking into the end of a 3-prong plug with the ground down, the left blade is the hot and the right is the neutral. On a 2-prong plug, the wide blade is the neutral.
y cant i connect the buses together?
arent they connected in the house wiring anyway???
Ground is ground and if you use a polarized plug and wire the plug correctly then the wires to the ground bars will meet at the grounding bar in the breaker panel. However if you wire the plug incorrectly and then inter-connect the two ground bars then you will potentially supply out of phase 120 volts, or one connection will be ground and one hot. You don't want to do this.
In general I wonder about your approach: it seems you need more then 15 amps, thus the purpose of connecting the supply to separate circuits. Controlling 15+ amps from a single Xmus board exceeds the intended design capacity. This strikes me as a bad idea.
Good luck,
Bill
What he said.
Yes all of the neutrals as well as the grounds meet at your main panel, but for safety reasons, that's the only place they should meet.
Another caution about your approach is that if the two hots are not from the same leg of your electrical service, there is 240V of potential between them on your board.
so should i just adapt my layout to use only 15 amps and stay with one circuit?
i was only going to be over by one or two amps anyways so im sure i can adjust
I noticed with the way we ran our system this year that just because something is common, it dosn't always work. You have to make sure that if you are using 2 breakers of fuses (if your house uses them) on the same side of the breaker box, then it is ok. If they are on opposite sides however, it is basically hooking up 2 hots together or 2 commons.
Kind of like omzig and Zane said. You can connect the neutrals together IF YOU ARE USING 2 SEPARATE CIRCUITS THAT ARE NOT ON THE SAME LEG (assuming you are in the U.S.). The reason for this is if you have the neutrals wired together and you are sharing the same circuit (like Zane said one breaker across from another breaker) you are returning double the current through the neutral. If you have the neutrals tied together and you are using (now required) a 2 pole breaker again like Zane said one above or below in the panel then the current returning is out of phase so you are returning half the current through the neutral. Also, do not mistake a mini breaker (one that fits in the same slot as a regular 1" breaker that has 2 handles) as 2 separate circuits. They are tied to the same hot.
I'll just use one circuit but thanks for all the help you guys!!!